#1409 - 12/07/04 12:44 PM nm through metal studs
John Desjardins Offline
Mechanic Member

Registered: 08/07/03
Posts: 306
Loc: Body=NC, Head & Heart=Florida
romex going floor to floor through a metal bottom plate. The wire is being protected by a 6" piece of PVC. I don't feel that this meets the code as its not a "listed" Grommet or Bushing. What do you all think?

Top
#1410 - 12/07/04 02:24 PM Re: nm through metal studs
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
I think that 334.15(b) permits the installation for NM cable passing through the floor, since 300.4(b)(1) only requires bushings and grommets to be listed for use when MN cable passes through metal studs.

334.15(b)
Quote:
Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC rigid nonmetallic conduit , listed surface metal or nonmetallic raceway , or other metal pipe extending at least 150 mm (6 in.) above the floor.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#1411 - 12/07/04 02:26 PM Re: nm through metal studs
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
I believe that there is something in the Code that requires that -- not PVC mind you but an emt sleeve or other suitable material for insure for proper firestopping.

I will look into this and post back.
_________________________

Top
#1412 - 12/07/04 02:27 PM Re: nm through metal studs
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Mike just got it. We posted back at the same time. I wasn't aware from memory that non-metallic was in there but it is.
_________________________

Top
#1413 - 12/07/04 04:50 PM Re: nm through metal studs
John Desjardins Offline
Mechanic Member

Registered: 08/07/03
Posts: 306
Loc: Body=NC, Head & Heart=Florida
more clarification. Single family residence. The NM is going from the ceiling cavity below into the wall cavity above by passing through a metal framing member. I believe that 334.15(b)is not really applicable here as 334.15 main heading is for exposed work. This is concealed work and thus does not need the conduit BUT requires a listed bushing for passing through the metal stud even though there is a piece of conduit. Maybe I'm being nit picky but.....

Top
#1414 - 12/08/04 07:52 AM Re: nm through metal studs
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Ok now that is a different subject, and I think both Nick and I got the wrong picture as to what you were pointing out. Thanks for the clarification, and yes I agree with you, 300.4 will apply and a listed bushing or grommet is required.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#1415 - 12/08/04 10:35 AM Re: nm through metal studs
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
In my opinion, 300.4(B)(1) does not apply as the NM is not passing through the metal framing memeber, the piece of conduit is. The NM is passing through the NM.

The intent of the section is to protect the NM cable from abrasion or cuts from sharp metal edges. The reason the listing requirement was added to the 2002 NEC was that unevaluated methods were being employed in the field such as duct tape. RNC has been evaluated as a protective "sleeve" for NM and should be permitted in leu of a listed grommet or bushing.

I see no hazard that arises from the method you describe and think it should be approved.
_________________________
Bryan P. Holland, MCP

Top
#1416 - 12/08/04 02:16 PM Re: nm through metal studs
Anonymous
Unregistered


At a certain point you need to ask, where is the hazard if the hole in the wood deck is centered and some distance away from the edge of the punched hole in the stud, even without the grommet/PVC. I can see the problem with installing a grommet. The metal is flat against the plywood. What holds the grommet in place? They snap into the metal, protruding on both sides. You would need an unlisted way to install the grommet. I would give the installer a break for trying to be safe with his PVC and go look for something that will burn houses and kill babies.

Top
#1417 - 12/08/04 03:56 PM Re: nm through metal studs
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Good question. I am going to think on this while I soak in the hot tub. Post back later.

It boils down to:

The code is the code is the code. So is he being too picky???
_________________________

Top
#1418 - 12/09/04 09:12 AM Re: nm through metal studs
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
You are correct Nick, the code is the code, and is that too picky? It may in fact be ok, it may work just fine without any problems, but.... it's just not one of the methods permitted by that code section in 300.4.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top



Active Topics
May Meeting Minutes
by Bryan Holland
Yesterday at 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
Registered: 01/25/12
Posts: 0
Forum Stats
518 Members
29 Forums
1892 Topics
8569 Posts

Max Online: 53 @ 03/30/12 04:16 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image