#2234 - 02/14/06 02:42 PM PVC types?
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Can someone give me a brief description that differentiates between the various forms of PVC (RNC)?

Type A, Type EB, HDPE-EPEC A, and HDPE-EPEC B?

Thanks
_________________________
Bryan P. Holland, MCP

Top
#2235 - 02/14/06 05:22 PM Re: PVC types?
Ruben Rocha Offline
Senior Member
*****

Registered: 05/24/00
Posts: 767
EB is used as a concrete encased raceway. Here is a link to carlon eb
I am not sure on HDPE pipe but I believe it is designed for non electrical use such as gas and liquids. HDPE

Top
#2236 - 02/15/06 01:24 AM Re: PVC types?
Anonymous
Unregistered


Ruben, check out NEC2005 art 353.

Bryan, I think the EPEC A and EPEC B refer to sched 40 vs sched 80. I see it listed as EPEC 40 and 80 in the catalog. There are a couple ASTM specs. This stuff is sold in rolls instead of sticks like regular RNC. I think you can even use it in the machines that cut a slit and direct bury pipe in one pass like the sprinlker guys use in cold places where it has to be deeper than just under the sod.
Try a google on "HDPE Conduit" and look at the first few hits.

Top
#2237 - 02/15/06 06:10 AM Re: PVC types?
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
I found this statement by UL but it doesn't explain too much. Thanks again.

Quote:
This category covers plastic types of rigid nonmetallic conduit, including straight conduit, elbows and other bends in sizes 1/2 to 6 (metric designators 16 to 155) inclusive, intended for installation underground as raceway for wire and cable in accordance with Articles 352 and 353 of ANSI/NFPA 70, "National Electrical Code" (NEC). This conduit may be: (1) polyvinyl chloride (PVC) Type A, Type EB or Schedule 40, or (2) high density polyethylene (HDPE) Schedule 40, Schedule 80, EPEC A, EPEC B.

The conduit is intended for underground use under the following conditions, as indicated in the Listing Mark: (1) when laid with its entire length in concrete in any location (Type A), (2) when laid with its entire length in concrete in outdoor trenches (Type EB) and (3) direct burial with or without being encased in concrete (HDPE Schedule 40, Schedule 80, EPEC A, EPEC B or PVC Schedule 40). The conduit is intended for use in ambient temperatures of 50°C or less.

Unless marked otherwise, Type A and HDPE Schedule 40, Schedule 80, EPEC A, EPEC B conduit is intended for use with wire rated 75°C or less. Type EB and Type A conduit, where encased in concrete in trenches outside of buildings, may be used with wire rated 90°C or less. HDPE Schedule 40, Schedule 80, EPEC A, EPEC B or PVC Schedule 40 conduit, when directly buried or encased in concrete in trenches outside of buildings, may be used with wire rated 90°C or less.

_________________________
Bryan P. Holland, MCP

Top



Active Topics
May Meeting Minutes
by Bryan Holland
Yesterday at 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
Registered: 02/02/07
Posts: 0
Forum Stats
518 Members
29 Forums
1892 Topics
8569 Posts

Max Online: 53 @ 03/30/12 04:16 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image