#2356 - 02/27/06 10:45 AM 310.15(B)(6) Main Power Feeder
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
I know this section has been beat to death, but I have a very minor question on interpretation of "Main Power Feeder."

Many homes here are installed with services on one side of the home and the lighting and applaince panelboard on the other. (split-service/extended service)

On many occasions, the contractor installes a meter/main assembly. Many times, this main section also incorporates a panelboard section usually with 6 or so spaces. From this point, the feeder is connected to feed through lugs.

On many occasions, the outside panelboard is used to serve A/C loads, and perhaps pool equipment.

Can the feeder to the inside panelboard still be considered the "main power feeder"?
_________________________
Bryan P. Holland, MCP

Top
#2357 - 02/27/06 11:44 AM Re: 310.15(B)(6) Main Power Feeder
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
I am going to say it is a feeder, but not the "main" feeder.


What say Mike?
_________________________

Top
#2358 - 02/27/06 11:49 AM Re: 310.15(B)(6) Main Power Feeder
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
I change my answer. After rereading the section I think it would be OK, see "...For application of this section..."
_________________________

Top
#2359 - 02/27/06 08:37 PM Re: 310.15(B)(6) Main Power Feeder
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Mike say Yes its a main power feeder
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#2360 - 02/28/06 08:25 AM Re: 310.15(B)(6) Main Power Feeder
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
I also agree with Mike and Nick, as it explains it quite well in 310.15 (b)(6)
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#2361 - 03/01/06 02:32 PM Re: 310.15(B)(6) Main Power Feeder
Anonymous
Unregistered


I agree it is OK if they size feeder to the general lighting sub panel at the size of the main breaker using 310.15(B)(6) since that is all that is required from there to the meter. When this gets questionable is when they have a larger main and split off a sub with another breaker and still want to use 310.15(B)(6) based on the size of the smaller breaker.

Top
#2362 - 03/18/06 08:30 AM Re: 310.15(B)(6) Main Power Feeder
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Yes you are correct...the problem is when they use this table to size the feeder to the detached garage panel or to the pool sub-panel.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top



Active Topics
May Meeting Minutes
by Bryan Holland
Yesterday at 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
Registered: 02/02/07
Posts: 0
Forum Stats
518 Members
29 Forums
1892 Topics
8569 Posts

Max Online: 53 @ 03/30/12 04:16 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image