I never said any of that. I do care if metal parts become energized by a circuit. However I feel it shoulf be the circuit that energizes the part that clears the fualt, not the pool grid.
I do believe all parts should be bonded together at the pool to eliminate step and touch potentials.
But as soon as grid is connected to the premise grounding system, it becomes apart of normal operatiing current.
I keep telling you that these are different issues, and you keep making them all the same.
Voltage gradients at the pool are to be minimized by the pool equipotential grid. Ground faults should be cleared by EGC's of the supplying circuit. And grounding should be made at the service and only the service and it would be advisable to limit how much normal current will flow through the pool system.
Again, three different issues.