#2413 - 03/14/06 11:30 AM 250.53(B) Question
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
250.53(B) basically states that the electrodes of one system are to be spaced not less than 6' from electrodes of another system. It then goes on to say that when electrodes are bonded together, they become one system. Does this mean that once I bond the electrodes of two different systems together, the 6' rule would no longer apply since I now have one system?

For example, I install a ground rod for the service and a ground rod for lightning protection. Since I plan to bond these two together, must they remain 6' apart or are they now one system?
_________________________
Bryan P. Holland, MCP

Top
#2414 - 03/14/06 12:30 PM Re: 250.53(B) Question
Anonymous
Unregistered


I agree you have made one system. You are still not getting the biggest bang for your grounding rod buck if they are less than 6' apart. ("well of influence" and such)

Top
#2415 - 03/14/06 03:02 PM Re: 250.53(B) Question
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
All electrodes bonded together form one single electrode system, and the 6ft rule also applies.

To get the biggest bang for your ground rod buck they need to be spaced 16ft apart . If installed less than 16ft, the grounding resistance is changed very very little.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#2416 - 03/14/06 03:30 PM Re: 250.53(B) Question
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Just to clarify, this 6' rule only applies to the electrodes in A5 and A6. A ground rod of one system, for example, does have to be 6' or more from a ground rod of another system. This article is talking about two distinctly different grounding systems. Possibly when there are multiple services on a building? Or 2 separate buildings very close to each other?

The article that requires the 6' separation for rods on the same system is 250.56.

Agree or disagree?
_________________________

Top
#2417 - 03/14/06 03:34 PM Re: 250.53(B) Question
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Yes you are 100% correct, I should have explained that better.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#2418 - 03/14/06 05:26 PM Re: 250.53(B) Question
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Mike if you get a moment can you explain where the 16 feet apart comes from?
_________________________

Top
#2419 - 03/15/06 06:13 AM Re: 250.53(B) Question
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
I submittted this proposal for the 2008 NEC. From what I unbderstand it has been accepted by the CMP:

Quote:
1. Section 250.53(A)

2. New Text

3. Add to the end of the end of the section: Where more than one rod or pipe electrode are used for the same system, the distance between electrodes shall not be less than the length of the longest rod or pipe and not exceed four times the length of the longest rod or pipe.

4. Substantiation: 1. I feel section 250.56 should be deleted completely. (proposal already provided for this) 2. The spacing requirements in this section only applies to rod, plate, and pipe electrodes installed to meet this section. There is no requirement for electrode spacing under any other purpose for the same system. 3. 250.53(B) spacing requirements only apply to electrodes of different systems. 4. One of the primary purposes of electrical system grounding is to limit the voltage imposed by lightning as indicated in 250.4(A)(1). Per the NFPA 780 section A.4.13.2.4, "No benefit is gained from the second ground rod if placed closer than the length of the longer rod. No additional benefit is gained if the second rod is placed over four times the length of the longer rod."
_________________________
Bryan P. Holland, MCP

Top
#2420 - 03/15/06 05:55 PM Re: 250.53(B) Question
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
The ground shell area around a 8ft rod is 8ft. The farther the shells are from the electrode the lower the resistance. This is called the effective resistance area. If you install a 2nd rod in the same 8ft ground shell area as the first it does nothing..so if you have 2 8ft rods they should be spread 16 ft.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#2421 - 03/15/06 07:06 PM Re: 250.53(B) Question
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Thanks Mike, for that explanation.

Neat stuff, Bryan.

Sort of cleans up both sections and puts it all in one place. My only comment would be -- how can the inspector tell what size ground rod is installed on a given installation when he gets there to do the inspection? Be neat if there was a way to put specific distances in the proposal. For what it's worth, just my 2 cents.
_________________________

Top
#2422 - 03/15/06 08:14 PM Re: 250.53(B) Question
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
The problem......the code only requires 6ft. Once the second rod is added we don't have to meet 25 ohms.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#2423 - 03/16/06 05:19 PM Re: 250.53(B) Question
Anonymous
Unregistered


Mike, the way it was explained to me is that well of influence decreases as you move away from the rod as a function of the square of the distance. At 6 feet the effectiveness has decreased enough from the first rod that there is an effect from the second. I do agree farther is better but rods are simply a poor choice in the first place.

Top
#2424 - 03/18/06 06:51 AM Re: 250.53(B) Question
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Very True....just that driving a 2nd rod 6ft from the first is useless for lowering grounding resistance..but meets code.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
Page 1 of 2 1 2 >



Active Topics
May Meeting Minutes
by Bryan Holland
Yesterday at 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
Registered: 02/02/07
Posts: 0
Forum Stats
518 Members
29 Forums
1892 Topics
8569 Posts

Max Online: 53 @ 03/30/12 04:16 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image