We check for it on plan reviews whether we are working as private provider, doing a peer review for a design professional (who will submit to the AHJ the regular way), or while supplementing the local AHJ with our plan review staff temporarily. Here is one of my typical templates. I have a bunch of them all worded a bit differently. If anyone wants, feel free to use all or in part:
1. [GENERAL] 2004 FLORIDA BUILDING CODE CHAPTER 13 13-413.1.ABC.2.1 INDICATE ON THE CONSTRUCTION DOCUMENTS THAT WITHIN 30 DAYS OF SYSTEM ACCEPTANCE, RECORD DRAWINGS SHALL BE PROVIDED TO THE OWNER. PLEASE REFER TO THE DETAILS IN THE CODE INDICATED ABOVE FOR SPECIFIC WORDING REQUIREMENTS.
2. [GENERAL] 2004 FLORIDA BUILDING CODE CHAPTER 13 13-413.1.ABC.2.2 INDICATE ON THE CONSTRUCTION DOCUMENTS THAT AN OPERATING MANUAL WILL BE PROVIDED TO THE BUILDING OWNER. PLEASE REFER TO THE DETAILS IN THE CODE INDICATED ABOVE FOR SPECIFIC WORDING.
3. [GENERAL] 2004 FLORIDA BUILDING CODE CHAPTER 13 13-413.1.ABC.1.1 INDICATE SOMEWHERE ON PLANS THE MAIMUM VOLTAGE DROP FOR FEEDER CONDUCTORS IN ACCORDANCE WITH THIS SECTION. PLEASE REFER TO THE DETAILS IN THE CODE INDICATED ABOVE FOR SPECIFIC WORDING. ALSO PROVIDE A TABLE SHOWING THE LENGTH OF HOME RUNS AND VERIFYING THE % (PER CENT) VOLTAGE DROP FOR THE FEEDERS.
4. [GENERAL] 2004 FLORIDA BUILDING CODE CHAPTER 13 13-413.1.ABC.1.2 . INDICATE SOMEWHERE ON PLANS THE MAIMUM VOLTAGE DROP FOR BRANCH CIRCUITS IN ACCORDANCE WITH THIS SECTION. PLEASE REFER TO THE DETAILS IN THE CODE INDICATED ABOVE FOR SPECIFIC WORDING REQUIREMENTS.
5. [GENERAL] 2004 FLORIDA BUILDING CODE CHAPTER 13 13-415.1.ABC.1.2 . THE LIGHTING LAYOUT DOES NOT HAVE ANY MEANS OF SPACE CONTROL. PLEASE REFER TO THE DETAILS IN THE CODE INDICATED ABOVE FOR SPECIFIC REQUIREMENTS.