This is kind of strange because last week I had to instruct an entire jurisdiction on this and how to do this. The plans examiners wanted answers as they will get asked questions all day about this subject. I told them something very similar, if not exactly what Bryan has just said. Read the wording in the code again:
(C) Equipotential Bonding Grid. The parts specified in 680.26(B) shall be connected to an equipotential bonding grid with a solid copper conductor, insulated, covered, or bare, not smaller than 8 AWG or rigid metal conduit of brass or other identified corrosion-resistant metal conduit. Connection shall be made by exothermic welding or by listed pressure connectors or clamps that are labeled as being suitable for the purpose and are of stainless steel, brass, copper, or copper alloy. The equipotential common bonding grid shall extend under paved walking surfaces for 1 m (3 ft) horizontally beyond the inside walls of the pool and shall be permitted to be any of the following:
(1) Structural Reinforcing Steel. The structural reinforcing steel of a concrete pool
where the reinforcing rods are bonded together by the usual steel tie wires or the equivalent
The code is "admitting" that the grid is held together by the little steel twisty ties. THAT is what is making the contact between the structural bars and forming the grid.
I instructed the plans examiners to make sure that ALL of the STRUCTURAL REINFORCING STEEL needs to be left extended such that 3' of the STRUCTURAL REINFORCING STEEL can be bent outward into the deck. Then mesh would be added (EQUIVALENT to the steel twisty ties, in my opinion) to form a 3' grid around the pool.
The #8 would have to be clamped to the STRUCTURAL steel to ensure a good connection, in my opinion.
So there's the grid.
Comments please.