#3306 - 12/05/06 09:05 AM 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Our department has come up with three solutions for the new deck bonding requirements in the 2005 NEC.

1. The rebar used to form the pool shell can be extended 3' into the deck area. 2. The standard 6x6 welded wire mesh can be bonded to the pool rebar or other point on the equipotential grid. 3. The alternate means stated in (part 3) of the section can be constructed.

Now, a few of the other surrounding jurisdictions are objecting to us permitting the wire mesh to be used. They claim the bonding grid cannot be less than typical ½" rebar or #8 copper. They feel the wire mesh is not suitable.

I referenced the similar bonding requirements in Article 547 that clearly identify wire mesh, however they feel the section and allowance in this article cannot apply to pools or the deck.

What are thoughts on the issue? The wire mesh will certainly provide the equipotential gradients along the deck and satisfy what I believe is the intent of the section, though wire mesh is not specifically referenced in that section.

(On a side note, I have been hearing a rumor from a very good source that another TIA is soon being released removing this entire new wording all together - or at least the part about the paved decks)
_________________________
Bryan P. Holland, MCP

Top
#3307 - 12/05/06 12:00 PM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
The wire mesh is not one of the methods permitted in the 2005 code. However, the 2008 has been rewritten, and I just received word back from the code panel meeting in California that the panel will accept the wire mesh as a bonding grid. I don't know if that wording will be included in 2008 NEC, (it's not included in the 2008 draft), but they seem to say they will accept it.

I just don't know how we can accept something if it is not written in the code, or how we can accept something from the 2008 cycle when we are just adopting the 05?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3308 - 12/05/06 06:22 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I agree that is how it reads. (6x6 steel wire is not acceptible) but I am not sure why not.BTW pools are usually built with #3 rebar AKA 3/8" 12" O/C.

Top
#3309 - 12/05/06 07:25 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
This is kind of strange because last week I had to instruct an entire jurisdiction on this and how to do this. The plans examiners wanted answers as they will get asked questions all day about this subject. I told them something very similar, if not exactly what Bryan has just said. Read the wording in the code again:

(C) Equipotential Bonding Grid. The parts specified in 680.26(B) shall be connected to an equipotential bonding grid with a solid copper conductor, insulated, covered, or bare, not smaller than 8 AWG or rigid metal conduit of brass or other identified corrosion-resistant metal conduit. Connection shall be made by exothermic welding or by listed pressure connectors or clamps that are labeled as being suitable for the purpose and are of stainless steel, brass, copper, or copper alloy. The equipotential common bonding grid shall extend under paved walking surfaces for 1 m (3 ft) horizontally beyond the inside walls of the pool and shall be permitted to be any of the following:

(1) Structural Reinforcing Steel. The structural reinforcing steel of a concrete pool
where the reinforcing rods are bonded together by the usual steel tie wires or the equivalent


The code is "admitting" that the grid is held together by the little steel twisty ties. THAT is what is making the contact between the structural bars and forming the grid.

I instructed the plans examiners to make sure that ALL of the STRUCTURAL REINFORCING STEEL needs to be left extended such that 3' of the STRUCTURAL REINFORCING STEEL can be bent outward into the deck. Then mesh would be added (EQUIVALENT to the steel twisty ties, in my opinion) to form a 3' grid around the pool.

The #8 would have to be clamped to the STRUCTURAL steel to ensure a good connection, in my opinion.


So there's the grid.


Comments please.
_________________________

Top
#3310 - 12/06/06 09:07 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Again the code calls for structural bars forming the grid....same as the construction of the pool.

I'm not saying that the wire mesh won't work...I just don't see how we can permit something that the code doesn't.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3311 - 12/06/06 11:30 AM Re: 680.26 Bonding Methods
Anonymous
Unregistered


If every #3 that comes up to the tie beam is bent and extended under the pool deck for 3 feet all they need to add is two #3s to ring the deck at 2' and 3' out. There is already one at the top of the tie beam. That will be a 12x12 matrix. They might have to put some short pieces in the corners to pick up the radius.
It would probably be cheaper and definately easier for pool "steelers" than using mesh.
I don't think you need any special bonding for the deck of this is simply extended pool steel, which is already bonded.

Personally I bonded my pool steel with a #8 cu ring tied to every 20' stick on the bond beam and brought out 6 #8s for my pool cage bonding but I am a fanatic about grounding/bonding. I think my pool cage is really a faraday cage that save us from a lightning strike if it is bonded well.

I believe the writers of 680.26 believe the Ufer concept that the concrete is actually what makes the electrical connection between tied rebars.

Top
#3312 - 12/06/06 01:22 PM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Article 680.26 (C) Equipotential Bonding Grid.
The equipotential common bonding grid shall extend under paved walking surfaces for 1 m (3 ft)horizontally beyond the inside walls of the pool and shall be permitted to be any of the following:
(1) Structural Reinforcing Steel. The structural reiforcing steel of a concrete pool where the reinforcing rods are bonded together by the usual steel tie wires or the equivalent.

This would be an extension of the pool forming steel out 3 feet from the inside wall of the pool in a grid formation just as exibit 680.14 of the handbook shows. Nothing less nothing more.

"a network of uniformly spaced horizontal and perpendicular lines" definition from websters of a grid.

If it was a metal liner pool we would go to (2).

We would also give them the option of the alternate means exactly as described.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3313 - 12/06/06 02:34 PM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
I was notified by Koert Van Wormer (City of Melbourne) that they are accepting the 6X6X10 WWF. He also mentioned the rest of Brevard County is as well.
_________________________
Bryan P. Holland, MCP

Top
#3314 - 12/06/06 02:37 PM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
I think with all these ideas we are designing something that is not the intent of the code.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3315 - 12/06/06 09:20 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
(1) Structural Reinforcing Steel. The structural reinforcing steel of a concrete pool where the reinforcing rods are bonded together by the usual steel tie wires or the equivalent.


Question: If the pool is engineered (which it is) and the engineer specifies the structural steel to stick past the pool into the deck (3'), and be connected by the mesh -- then doesn't that satisfy (1) above?


Why or why not.
_________________________

Top
#3316 - 12/07/06 07:07 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
An engineer can't design something different than the NEC code section. Still must comply with code.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3317 - 12/07/06 08:44 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
I'm saying he can design it as part of the pool structural steel system.
_________________________

Top
#3318 - 12/07/06 08:48 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Correct, and that is the intent, to design the equipotential grid when using structural steel the same as the pool wall.

Going ack to my question, how can we accept 6x6 wire mesh when the code doesn't?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3319 - 12/07/06 11:31 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Engineer can design that part of the "wall" any way he wants to. He/she is the engineer and if they use mesh for the deck part that is their design.

BUT, I think I am wrong again. I have just been speaking to several structural engineers who say that continuing the structural steel out 3' on the deck is no good. They claim if the deck cracks, which it will, the crack will continue down into the pool. So this may not be a good method at all unless there is some type of expansion joint between the pool and the deck.

It seems after all of this being said, the only real way to accomplish this would be with the alternate means. So,

DOES ANYONE KNOW OF A PRODUCT THAT IS FOR SALE TO ACCOMPLISH THE BONDING? IS THERE SOME TYPE OF A ROLL-OUT MAT? WHO SELLS IT? PLEASE POST THE LINK!!!!!

Thanks.
_________________________

Top
#3320 - 12/07/06 11:36 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
_________________________

Top
#3321 - 12/07/06 11:57 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Fantastic......so than why do we need to permit something that is not in the code when a product exists that does meet the code.

Great job Nick!!!!
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3322 - 12/07/06 01:43 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
YES, I agree with you.

Go ahead, rub it in...


laugh
_________________________

Top
#3323 - 12/07/06 02:01 PM Re: 680.26 Bonding Methods
Alan L. Waters Offline
Mechanic Member
*****

Registered: 12/11/02
Posts: 102
Loc: Jacksonville Florida
What if it is a fiberglass pool shell. With a fiberglass ladder (no metal to bond) and a double insulated pool motor. Do we have to build a grid beneath the pavers surrounding it? And attach it to what?
_________________________
Alan L. Waters
Electrical Contractor
IAEI Division Secretary
(North Florida Division)
JMEA Director

Top
#3324 - 12/07/06 02:13 PM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Good point....I vote no.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3325 - 12/07/06 02:37 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Great point....I vote yes.


Alan's point/question is that if there is no structural steel, then what...?

But lets go back to 680.26(B)(1) which says at the end,

"Where the reinforcing steel is encapsulated with a nonconductive compound, provisions shall be made for an ALTERNATE MEANS to eliminate voltage gradients that would otherwise be provided by unencapsulated, bonded reinforcing steel."


Sounds like the intent of the code is to eliiminate voltage gradients around the pool no matter what.

Would you not agree?

.
_________________________

Top
#3326 - 12/07/06 02:41 PM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
I sure hope the TIA Bryan was talking about is coming out very soon. I don't think anyone really gave this thing any thought. It's kinda late to be debating this what with tomorrow being the deadline.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3327 - 12/07/06 03:08 PM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Nick....again as Alan said what do you connect that grid to since there is no metallic parts, and when used with a double insulated motor, it is not required to be incorporated into the bonding grid per 680.26(b)(4)?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3328 - 12/07/06 04:41 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
There is usually always a light niche and a swimming pool light junction box. And down here we have screen cages as well.
_________________________

Top
#3329 - 12/07/06 09:04 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I am with Nick. I don't really see that many double insulated pumps plus heaters, lights and metal within 5' will still need bonding.

Top
#3330 - 12/08/06 06:56 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
You didn't get the question.....Alan asked, what if there is nothing metal to bond and you have a double insulated pump that doesn't require bonding? Now what do we do? Are we required to provide that equipotential grid when there is nothing there to bond to?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3331 - 12/08/06 07:38 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
We are getting crazy. Our county is going to enforce the structural steel of the pool extending out 3 foot in a grid pattern as the code says, or give them the option of the alternate methods.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3332 - 12/08/06 08:29 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Alan based on the specific question you asked (nothing to bond), my answer is that no grid is required.

You do understand that if anything were to change, wet niche fixture, pool enclosure, metal parts, etc..etc..than the equipotential grid would be required.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3333 - 12/08/06 09:13 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
I agree with that Mike.


The real scary thing here is that pool contractors should have been lined up out the door yesterday submitting applications...........but they were no where in sight. I wonder if they know about this change at all.
_________________________

Top
#3334 - 12/08/06 09:19 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Guess not.

I understand that many jurisdictions are going to accept the 6x6 wire mesh for the equipotential grid.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3335 - 12/08/06 11:56 AM Re: 680.26 Bonding Methods
Anonymous
Unregistered


The real question is what happens when the owner does swap out that pump or decides he wants a heater and the grid is not already in place.
Are they really going to rip out the pool deck to replace a pump or add a heater? I am betting, no, since they will not get a permit.

If we think it is really important, we should require it with a #8 stub available. If we think it is not important why are we doing it in the first place?

I do agree pool contractors are largely ignorant of this new rule. I have tried to explain it to a few of them and they simply do not believe me. I guess they are going to find out about it pretty soon.

Top
#3336 - 12/08/06 12:00 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


BTW I guess that begs the question, if someone does add a light or heater, are we going back to look at the original pool permit date to see if the grid was required at that time or simply say the heater/light is a change that requies a grid to be added no matter when the pool was built?

Top
#3337 - 12/08/06 12:18 PM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
I guess we only inspect based on what they pull a permit for, according to that scope of work. If they add things after the passed inspection and do not pull permits and get approved inspections the fault is not ours.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3338 - 12/08/06 01:55 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Really good questions.
_________________________

Top
#3339 - 12/09/06 11:09 PM Re: 680.26 Bonding Methods
Rob Reading Offline
Apprentice Member

Registered: 12/09/06
Posts: 15
Loc: Oviedo, Florida
Back to the original question, 680.26(C)of the code is specific on materials approved for use to form the equipotential bonding grid 3' outward from the inside walls of all pools . In my opinion, the use of anything not mentioned in this prescriptive code section is not sufficient or within the intent of the code.
_________________________
Rob Reading CBO,MCP
Plans Examiner
City of Oviedo
P. 407-971-5767
rreading@cityofoviedo.net

Top
#3340 - 12/10/06 12:03 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
I am with Rob! Welcome to the NEC forum Rob! :p :p :p

I can make an argument wink for the 6x6 mesh (per code) and "probably" it will be sufficient to eliminate gradients for a poured deck. But it will not hold up with a paver deck.

In all reality (and this is what Mike was saying from the beginning) the code is clear, and yes, this will change the way pools are constructed. I think Greg would also agree. And electricman agrees.

IAEI? They will probably just say to "do like the code says." How many IAEI folks are on that CMP, does anybody know?


I close with my 2 cents (as usual): The smart pool contractors will see this as a legitimate opportunity to adjust their price structure. The not-so-smart pool contractors will kick, scream and whine.


eek mad eek


PS - Let me just clarify that my original intent in the first few posts was never to use "just the mesh."
_________________________

Top
#3341 - 12/10/06 02:23 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


CMP 17 which also does appliances, space heating and deicing equipment has one regular and one alternate IAEI member Milatovich and Maldonado according to the 2005 book.

Top
#3342 - 12/11/06 04:51 PM Re: 680.26 Bonding Methods
Anthony Sapuppo Offline
New Member

Registered: 12/11/06
Posts: 1
Loc: Bradenton
This is an odd issue. I am hearing from local AHJ's that they want the pool steel to form the grid. I find it strange that the NEC would then in fact changing a building standard? I feel the electrical contractor should be responsible for a Code worthy sollution not the "pool steel" sub.
Installing any steel improperly under a deck would lead to corrosion, concrete sparing and who inspects it?? The building inspector? or are us electrical inspector now inspecting a building item?
Am I missing something?!?
Thanks! Tony...

Top
#3343 - 12/11/06 05:33 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Welcome to the NEC forum Tony! :p :p :p


Well, there are different ways that we can get compliance on this issue, according to 680.

One way is by using the pool structural steel. The building inspector or the 1&2 family dwelling inspector always inspects the steel.
But the electrical inspector would inspect all the bonding connections.

If the equipotential grid is made via the alternate means (#8 bare copper) then the electrical inspector would do that inspection.

It will be interesting to say the least! One thing should always be certain - that every pool permit have the pool contractor and an electrical contractor declared somewhere on that permit.


smile
_________________________

Top
#3344 - 12/11/06 05:51 PM Re: 680.26 Bonding Methods
Tony Sapuppo Offline
New Member

Registered: 08/05/02
Posts: 1
Loc: Longboat Key Florida
Thanks Nick! Just found my existing log in from way back. I am raising the questions because I inspect a lot of pool steels as both Electical Official and as a One and Two Family. I like the alternate method! Thanks for the clarity and glad to be back on the Forum!
Tony Sapuppo
BN 2276
PX 1942

Top
#3345 - 12/12/06 07:04 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Don't forget the code panel is including wire mesh in the 2008 code, and because of that some jurisdictions are going to permit it for the 2005.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3346 - 12/12/06 08:41 AM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
Let me through something more into the mix. 1st I agree no wire mesh.
Now heres the pitch. What do we do if we are installing a pool and it is located closer then 3' from an existing porch slab? Is it permissible to not require 3' in that section?

Top
#3347 - 12/12/06 09:36 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
If wire mesh is sufficient for the equipotential plane at agricultural buildings, then why would it not be sufficient for pools?

I've asked the very same question regarding pools located with 3' of an existing deck, and the answers were as divided as the question of wire mesh.
_________________________
Bryan P. Holland, MCP

Top
#3348 - 12/12/06 10:13 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
It's not a question as to if the wire mesh will work, or not. The question is;
1. Is it permitted by the code?
2. Should we permit something from the 2008 code to be used before it's adopted in Florida for 2005?
3. Is that legal?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3349 - 12/12/06 10:14 AM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
I would agree Bryan I would think it would be sufficiant also as it is in ag. bldings. I guess until 2008 it wont be.
So do you think that the equipotential from pool deck to exsiting deck would be diffenrent right? How do we take care of our 3'make them install the pool so this could be meet as like in the recp of 10' min and 20' max from the pool, less the lot size exception?

Top
#3350 - 12/12/06 12:50 PM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
To answer Mike,

1. I don't think the wire mesh is permitted as the code is worded now.

2. If the omission was due to an oversight than why should it not be permitted under the 2005 if specified in the 2008?

3. I don't know. Perhaps 90.4 can be used. "By special permission, the authority having jurisdiction may waive specific requirements in this Codeor permit alternative methods where it is assured that equivalent objectives can be achieved by establishing and maintaining effective safety."

I believe that could also be used to answer the question posed by "rasmith".
_________________________
Bryan P. Holland, MCP

Top
#3351 - 12/12/06 01:09 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I don't see the wire mesh as a huge problem if the structural inspector verifies it is up on chairs so it will actually end up in the concrete and the electrical inspector sees it is properly bonded. I do see the omission in 2005 as simply an oversight since it is going in the 2008. New code does seem to work that way.
It may not be the way the law is written but the fact remains the AHJ still has the final word on what they will approve.

Top
#3352 - 12/13/06 07:34 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
If you put wire mesh in the dirt under the pavers it will deteriorate....quickly.

That won't work. eek
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3353 - 12/13/06 10:23 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Brevard County, City of Melbourne, and City of Orlando have notified our department that the welded wire mesh will be approved.
_________________________
Bryan P. Holland, MCP

Top
#3354 - 12/13/06 11:48 AM Re: 680.26 Bonding Methods
Anonymous
Unregistered


Mike, I don't think anyone is talking about steel mesh in the dirt. This is about the mesh, embedded in concrete. In all but the most hostile environments, like a bridge over salt water, this steel in concrete will last virtually forever.
I agree steel in dirt will be red dust in a year or two.

Top
#3355 - 12/13/06 01:24 PM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Brick Pavers? Where do you put the mesh? In the dirt under the pavers.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3356 - 12/13/06 11:49 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
In the dirt. Not the wire mesh for contruction, but the copper mesh for the E plain.

Top
#3357 - 12/14/06 06:56 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
That is 100% correct!
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3358 - 12/14/06 06:49 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
If it helps any, I have been talking to a few people (informally) in the Building Officials Association of Florida and they agree mesh for pavers isn't going to be good.


Cool, 4 pages so far...this could be a new record.
_________________________

Top
#3359 - 12/14/06 10:43 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
Copper mesh for paver right?

Top
#3360 - 12/14/06 11:15 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
What Mike T. said.
_________________________

Top
#3361 - 12/15/06 06:13 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
I received word from Building Officials Association of Florida this morning that an informal interpretation will be released within the next 3 weeks.
_________________________
Bryan P. Holland, MCP

Top
#3362 - 12/16/06 01:54 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


This came as a surprise to them too? Sounds like a ruling about a month too late.
There are guys over on ECN who have been doing this for well over a year on jurisdictions that are already on 2005. Products (12 over 8ga welded copper) are on the market for this but they are pricy.

Top
#3363 - 12/17/06 09:53 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Does anyone know if brass wire mesh is available?
_________________________

Top
#3364 - 12/18/06 06:22 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
How about 2 years late! No reason why the state can't put the NEC into effect (since it goes through the NFPA process ) as soon as it comes out, than if changes need to be made it can be after the fact.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3365 - 12/19/06 08:44 AM Re: 680.26 Bonding Methods
inspector32513 Offline
Lynn Adams

Registered: 10/06/05
Posts: 46
Loc: Pensacola, FL
Most of our residential pools are vinyl. PVC walls, vinyl liner. The only metal is the coping.
For several years Escambia County has required a Ring Ground around the pool. Hitting a lay-in lug or lug on the gr wire at every section of coping. (this follows a previous practice of allowing short jumper wires and two lugs at the joint in every section. I think the ring with a single lug on each section of coping and also each "cup" or niche, or other metal around the pool is almost as cheap, and easy, and 100% better)

The only comment I have heard locally is the suggestion that the "steel reinforcing of the deck" be bonded out 3'. And since most pool decks do not have "steel" the options are either the welded #8 copper grid - OR let the contractor put down some steel. If he wants to put down #3 rebar on a 12" grid, FINE. If he puts down 6" x 6" welded steel mesh- well that IS the "steel reinforcement of the deck" just take the ring ground and tag each individual section with a split bolt or other connection.
_________________________
Lynn Adams
Chief Electrical Inspector, Escambia County
IAEI_Panhandle Division

Top
#3366 - 12/19/06 08:55 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Welcome to the NEC forum inspector32513!!!

laugh laugh laugh


What are you guys going to do for a pool with pavers?
_________________________

Top
#3367 - 12/20/06 09:45 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
After much deliberation and thinking up ways around this code, the only thing that I can think up now is to comply with the code as written. So this is my final "analysis" on this subject:

2005 NEC 680.26(5)(C):

The 2005 National Electrical Code and the Florida Building Code 2006 revisions have been adopted by the State of Florida and are in effect beginning Friday, December 8, 2006. All permits for pools after this date are subject to the new 2005 NEC requirement for a 3-foot wide, equipotential bonding grid under the pool deck.

Paved surfaces shall include but not be limited to: concrete, tile, brick pavers, brick, marble, terrazzo, flat stone, or any other hard masonry like surface whether poured in place, grouted in place or bedded in sand. Paved surfaces covered with sealer, paint, protective coatings, carpet, etc., remain a paved surface and require the equipotential bonding plane. Non-paved surfaces are grass, loose stone and gravel, wood or composite decking, and do not require the equipotential bonding plane.

There are two material options for construction. The use of structural steel rods, or #8 AWG bare solid copper conductor. There is no minimum size specified for the steel rods. The code specifies "reinforcing rods" thereby excluding wire mesh as the means for the bonding grid material. Wire mesh may be used as a means of concrete deck reinforcement, however the boning grid around the pool is required to be made of steel rods. Reinforcing steel use is limited to being installed in poured concrete. Solid copper wire is required where the grid is buried in the sand/soil under a brick or paver deck type of surface. The #8 AWG copper wire grid shall be arranged in a 12 inch by 12 inch network of conductors in a uniformly spaced perpendicular grid pattern.

Grids fabricated out of steel rods shall be tied together at every cross point by the usual steel wire ties. Grids fabricated out of copper conductors shall be terminated at each crossing by exothermic welding, listed pressure connectors, listed clamps, or other listed means.

The vertical steel rods from the pool shall not be field bent or made continuous with the deck steel, except as shown on the construction documents or permitted by the registered design professional (see FBC 1907.3.2).


Happy Enforcement! smile
_________________________

Top
#3368 - 12/20/06 10:13 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
I agree 100% Well said!!!
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3369 - 12/20/06 11:00 AM Re: 680.26 Bonding Methods
Anonymous
Unregistered


Nick, pool "steelers" do not tie every junction. That would be a new requirement if you say that.
They only get tied when they are not laying together. The tie wire really does not contribute that much to the electrical conductivity anyway since they are usually pretty loose, rusty metal to rusty metal.

Top
#3370 - 12/21/06 06:07 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Finally, and exactly as the code is written, Well done Nick.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3371 - 12/21/06 06:21 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
The consensus at the IAEI Gulf Coast Division meeting yesterday is that wire mesh is NOT approved for use. The jurisdictions of Charlotte County, City of Punta Gorda, City of Venice, City of Cape Coral, and City of North Port were present.

These jurisdictions will basically follow the description detailed by NICK in his post above - save for any new word from Building Officials Association of Florida or the NFPA.
_________________________
Bryan P. Holland, MCP

Top
#3372 - 12/21/06 12:57 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


It is funny that a state with a "uniform" building code can have so many variations in these rules. I bet the mesh is OK in Lee ... but they seldom come to the IAEI meetings.

As an aside, did Pete bring up my idea about conference calling or web casting these meetings?
It is getting harder to justify driving 2 hours or more for a meeting that has about an hour of real content.

Top
#3373 - 12/27/06 11:55 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Maybe we can get some direction from the folks in Texas, after all - they have been on the '05 now for a while, from what I am told. See my question:

IAEI Global Forum - Pool Deck Bonding
_________________________

Top
#3374 - 12/27/06 02:57 PM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Here is how the 2008 NEC section will be reworded. I know it doesn't apply to the 2005 NEC, but can be used as guidance for 2005 interpretation. Notice the last statement made by the panel regarding WELDED WIRE MESH:

Quote:
Panel Meeting Action: Accept in Principle
Revise as follows:
680.26 Equipotential Bonding.
(A) Performance. The equipotential bonding required by this section shall be installed to reduce voltage gradients in
the pool area.
(B) Bonded Parts. The parts specified in 680.26(B)(1) through (B)(7) shall be bonded together using solid copper conductors, insulated covered , or bare, not smaller than 8 AWG or with rigid metal conduit of brass or other identified corrosion-resistant metal. Connections to bonded parts shall be made in accordance with 250. 8. An 8 AWG or larger solid copper bonding conductor provided to reduce voltage gradients in the pool area shall not be required to be extended or attached to any remote panelboard , to service equipment, or electrodes.
(1) Conductive Pool Shells. Bonding to conductive pool shells shall be provided as specified in 680. 26(B)(1)(a) or 680.26(B)(1)(b). Poured concrete, pneumatically applied or sprayed concrete, and concrete block with painted or plastered coatings shall all be considered conductive materials due to water permeability and porosity. Vinyl liners
and fiberglass composite shells ar shall be considered to be non-conductive materials.
a. Structural Reinforcing Steel. Unencapsulated structural reinforcing steel shall be bonded together by steel tie wires or the equivalent. Where structural reinforcing steel. encapsulated in a nonconductive compound, a copper conductor arid shall be installed in accordance with;- 680.26(B)(1)(b).
b. Copper Conductor Grid. A copper conductor grid shall be provided and shall comply with the following conditions:
(1) Be constructed of minimum 8 AWG bare solid copper conductors bonded to each other at all points of
crossing.
(2) Conform to the contour of the pool and the pool deck.
(3) Be arranged in a 300 mm (12 in. ) by 300 mm (12 in.) network of conductors in a uniformly spaced
perpendicular grid pattern with a tolerance of 100 mm (4 in.)
(4) Be secured within or under the pool no more than 150 mm (6 in.) from the outer contour of the pool shell.
(2) Perimeter Surfaces. The perimeter surface 2b extends for 1 m (3 ft) horizontally beyond the inside walls of the pool:- and shall includes unpaved surfaces as well as poured concrete and other types of paving. Bonding to perimeter surfaces shall provided as specified in 680. 26(B)(2)(a) or 680.26(B)(2)(b), and shall be attached to the pool reinforcing steel or copper conductor grid at a minimum of four (4) points uniformly spaced around the perimeter of the pool. For non-conductive pool shells , bonding at four points shall not be required.
(a) Structural Reinforcing Steel. Structural reinforcing steel shall be bonded In accordance with 680.26 (B)(1)(a).
(b) Alternate Means. Where structural reinforcing steel is not available or is encapsulated in a nonconductive compound, copper conductor shall be utilized where the following conditions are met:
(1) At least one minimum 8 AWG bare solid copper conductors shall be provided.
(2) The conductor(sl shall follow the contour of the perimeter surface.
(3) Onlv listed splices shall be permitted.
(4) The required conductor shall be 450 to 600 mm (18 to 24 in.) from the inside walls of
the pool.
(5) The required conductor shall be secured within or under the perimeter surface 100 to 150 mm (4 to 6 in.) below
the subgrade.
(3) Metallc Components. All metallc parts of the pool structure , including reinforcing metal not addressed in 680.26(1)(a), shall be bonded. Where reinforcing steel is encapsulated with a nonconductive compound the reinforcinq steel shall not be required to be bonded.
(4) Underwater Lighting. All metal forming shells and mounting brackets of no-niche luminaires shall be bonded.
Exception: Listed low-voltage lighting systems with nonmetallic forming shells shall not requirejr bonding.
(5) Metal Fittings. All metal fittings within or attached to the pool structure shall be bonded. Isolated parts that are not over 100 mm (4 in.) in any dimension and do not penetrate into the pool structure more than 25 mm (1 in. ) shall not require bonding.
(6) Electrical Equipment. Metal parts of electrical equipment associated with the pool water circulating system including pump motors and metal parts of equipment associated with pool covers , including electric motors, shall be bonded.
Exception: Metal parts of listed equipment incorporating an approved system of double insulation shall not be bonded.
(a) Double-Insulated Water Pump Motors. Where a double-insulated water-pump motor is installed under the provisions of this rule , a solid 8 AWG copper conductor tt of sufficient length to make a bonding connection to a replacement motor shall be extended from the bonding grid to an accessible point in the mo vicinity of the pool pump motor. Where there is no connection between the swimming pool bonding grid and the equipment grounding system for the premises , this bonding conductor shall be connected to the equipment grounding conductor of the motor circuit.
(b) Pool Water Heaters. For pool water heaters rated at more than 50 amperes and having specific instructions regarding bonding and grounding, only those parts designated to be bonded shall be bonded and only those parts designated to be grounded shall be grounded.
(7) Metal Wiring Methods and Equipment. Metal-sheathed cables and raceways , metal piping, and all fixed metal parts shall be bonded.
Exception No. 1: Those separated from the pool by a permanent barrier shall not be reauired to be bonded.
Exception NO. 2: Those greater than (5 ft) horizontally of the inside walls of the pool shall not be reauired to be bonded.
Exception No. 3: Those greater than (12 ft) measured vertically above the maximum water level of the pool, or as measured vertically above any observation stands, towers, or platforms, or any diving structures shall not be required to be bonded.
Panel Statement: The revised text more clearly presents the requirements and meets the intent of the submitter.
The panel has removed the word " (rebar)" from 680.26(B)(1)a to clarify that welded wire mesh can be included in the term "structural reinforcing steel" where acceptable to the authority having jurisdiction.
_________________________
Bryan P. Holland, MCP

Top
#3375 - 12/27/06 11:15 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I still didn't see a definition of "structural reinforcing steel". Does that include 6 over wire?

Top
#3376 - 12/28/06 06:26 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
As far as I am thinking that didn't clarify anything, since it is still up to the AHJ to determine what structural reinforcing steel is.

Why can't they just state that welded wire mesh is permitted for the equipotential bonding grid. I think that they let us down again!
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3377 - 12/28/06 06:36 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
This CMP should address the questions and issues NOW !
_________________________

Top
#3378 - 12/28/06 07:21 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
I agree
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3379 - 12/28/06 08:59 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Me Too!
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3380 - 12/28/06 02:28 PM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Me Three...
_________________________
Bryan P. Holland, MCP

Top
#3381 - 12/29/06 11:48 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Here is an article from a U.L. expert, the point of which is that the 2008 wording leaves more questions than answers...

Be Specific by Mark C. Ode
_________________________

Top
#3382 - 12/29/06 12:32 PM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Yep I already saw that article and I agree the code panel left us high and dry.

Second the definition of structural reinforcing steel does not apply to wire mesh. Since they did not use the "welded wire mesh" wording in the actual code section I don't think that it should be permitted!

I think the code panel needs to get their act together and say what they mean!
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3383 - 01/04/07 04:03 PM Re: 680.26 Bonding Methods
Rob Reading Offline
Apprentice Member

Registered: 12/09/06
Posts: 15
Loc: Oviedo, Florida
Here is a link to the informal interpretation that I requested from Building Officials Association of Florida on this subject
pool bonding
_________________________
Rob Reading CBO,MCP
Plans Examiner
City of Oviedo
P. 407-971-5767
rreading@cityofoviedo.net

Top
#3384 - 01/04/07 06:23 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
How do you request a formal interpretation?

PS - Since "this product is specifically referenced in Article 547 for agricultural
buildings and has been used for many years" why didn't they use that language in 680?

Answer: Because they meant to use "rods" and not "mesh"
_________________________

Top
#3385 - 01/05/07 07:27 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
The Building Officials Association of Florida interpretation is 100% incorrect !

In addition...I don't care about Building Officials Association of Florida opinions...and in my opinion they should not offer interpretations to NFPA fire codes as they have their own process. I am only interested in the NFPA interpretation.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3386 - 01/05/07 07:31 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
I say let's get a formal interpretation.
_________________________

Top
#3387 - 01/05/07 07:34 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
I got one.....how about if we just read the code and apply what it says....cause nobody disputes what it say's, but as Nick said...they just don't like it.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3388 - 01/05/07 07:39 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Mike,
Are you really surprised at this? There is no excuse -- because the NEC is already interpreted by NEC the handbook. So in this case, Building Officials Association of Florida throws away the NEC handbook to achieve their desired result. They know more than the NEC experts that wrote the handbook and NFPA.

I won't take it out on Building Officials Association of Florida though. The code making panel knew exactly what they meant by the language that is in the 2005. Exactly. They may be fumbling around now and trying to save face with the 2008 language, but it is evident what was to be done with regard to this code, in the 2005.
_________________________

Top
#3389 - 01/05/07 07:47 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
I agree 100% and to add a point the changes in the 2008 aren't much different and as of yet, and the last wording so far still makes no reference to wire mesh!

I was talking to someone at NFPA who I will not identify...but per his opinion wire mesh is not approved and said "not until the fat lady sings". In other words until the 2008 comes out and we see it in print!
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3390 - 01/05/07 07:53 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
In addition we just adopted the 2005! Why are we going to the 2008 for something and it isn't even in print yet.

Lets just adopt the 2008 and the heck with the 2005 since nobody likes it anyway.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3391 - 01/05/07 08:04 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Mike,
The fat lady is singing,
BUT I CAN'T HEAR HER !!!

_________________________

Top
#3392 - 01/05/07 08:20 AM Re: 680.26 Bonding Methods
Rob Reading Offline
Apprentice Member

Registered: 12/09/06
Posts: 15
Loc: Oviedo, Florida
I agree with all of you. For a binding interpretation there must be someone who does not agree with the Building Officials interpretation and they must submit for the binding interpretation as outlined in FAC 9B-3.055 and submit it electronically through this link binding interpretations
Quote:
FAC 9B-3.055
Binding Interpretations of the Florida Building Code, Forms Adopted.
(1) Petitions for binding interpretations of the Florida Building Code shall be made through the Building Code Information
System on the Internet in accordance with the provisions of Section 553.775, F.S.
(2) A fee of $250 shall be paid by petitioner by credit card or electronic check upon such submission to cover processing costs.
(3) The following form is adopted for use in conjunction with issuance of a binding interpretation: Florida Building
Commission, Petition for Binding Interpretation, Form No. 9B-3.055(1), November, 2005 (electronic version).
(4) The petitioner shall print two (2) completed petitions for submittal to the enforcement agency that rendered the decision
that is the subject of the petition. The enforcement agency shall stamp each of the petitions submitted with the time and date of
receipt, retain one copy and return one to the petitioner, who shall retain the stamped petition for submittal in the event that receipt
of the petition or the time thereof become material to the dispute.
(5) Within 5 working days after receipt, the local building official shall respond to the petition through the Building Code
Information System, or in writing, including statements 1) admitting or denying the statements contained in the petition, 2) of the
interpretation of the provisions of the Florida Building Code deemed correct by the local building official or jurisdiction, and 3)
containing the basis for the interpretation, and shall return the petition with his or her response to the petitioner. The petitioner may
file the petition with the Commission at any time after it is returned to him or her, or after 10 days if the local building official has
not responded. The Commission shall immediately publish the petition online on the Building Code Information System, accept
online comments from interested parties for a period of seven calendar days, and provide copies of the petition to a panel. The panel
shall conduct proceedings as necessary to resolve the issue, considering the petitioner’s arguments, the building official’s response
and comments made on the petition, and shall issue an interpretation within 21 days of the petition’s submittal, based either on code
language or the intent of the code. The 21 days may be waived only upon consent of all parties. The interpretation shall be provided
to the Commission, which shall post it online on the Building Code Information System and in the Florida Administrative Weekly.
The interpretation shall be binding to all parties and all jurisdictions subject to the code unless it is superseded by a declaratory
statement issued by the Florida Building Commission or by a final order entered after an appeal proceeding conducted. Appeals to
interpretations shall be filed within 30 days of issuance of an interpretation and shall be conducted in accordance with Chapter 120,
F.S., and the uniform rules of procedure.
(6) The interpretation rendered by the panel of building code administrators shall become final upon the earlier of the
resolution of any appeal of that interpretation before the Florida Building Commission or the expiration of the time period in which
to initiate such appeal.
Specific Authority 553.775 FS. Law Implemented 553.775(3)(c) FS. History–New 2-28-06.
_________________________
Rob Reading CBO,MCP
Plans Examiner
City of Oviedo
P. 407-971-5767
rreading@cityofoviedo.net

Top
#3393 - 01/05/07 08:49 AM Re: 680.26 Bonding Methods
Rob Reading Offline
Apprentice Member

Registered: 12/09/06
Posts: 15
Loc: Oviedo, Florida
Also article 547 is for protecting livestock and not people!
_________________________
Rob Reading CBO,MCP
Plans Examiner
City of Oviedo
P. 407-971-5767
rreading@cityofoviedo.net

Top
#3394 - 01/05/07 08:54 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Binding interpretations are great for other trades.....but again I only care about NFPA interpretations since the NEC process is separate from Florida.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3395 - 01/05/07 10:41 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Yeah, I know Mikeeee....

but if we are going to make a game out of code interpretations, then let them put their opinion out there as a formal and binding interpretation.
Count me in for 50 bucks.


$$cha-ching$$

laugh
_________________________

Top
#3396 - 01/05/07 11:03 AM Re: 680.26 Bonding Methods
Anonymous
Unregistered


If there were not a lot of different code interpretations you could build the same thing in Collier County as you did in Cape Coral or unincorporated Lee County. It is just not true.
I have been in IAEI meetings up at the "all you can choke down buffet" and saw one building department with more than one opinion on something.
When I talk to the builder side, these questions are always prefaced by "where are you building it"?

Top
#3397 - 01/05/07 11:45 AM Re: 680.26 Bonding Methods
Rob Reading Offline
Apprentice Member

Registered: 12/09/06
Posts: 15
Loc: Oviedo, Florida
Has anyone submitted a request for a formal interpretation from NFPA on this subject?
_________________________
Rob Reading CBO,MCP
Plans Examiner
City of Oviedo
P. 407-971-5767
rreading@cityofoviedo.net

Top
#3398 - 01/05/07 11:58 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Not that I know of....but you understand that it is a 6 month process for a formal NFPA interpretation.

Since we are just starting to use the 2005....I wonder what has been going on in other states that have been on the 2005 for the past 2 years?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3399 - 01/05/07 06:34 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
I possed this question on December 12, 2006 09:41 AM
What do we do if we are installing a pool and it is located closer then 3' from an existing porch slab? Is it permissible to not require 3' in that section?

Top
#3400 - 01/05/07 08:38 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
The deck would have to be bonded for any amount of walking surface less than 3 feet.

The equipotential common bonding grid shall extend under paved walking surfaces for 1 m (3 ft) horizontally

Obviously if you only have 2' then the intent is to have the bonding grid there for those 2'.
_________________________

Top
#3401 - 01/06/07 06:24 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
Thanks. To tell you the truth I wasnt sure. With the wording in the code I wasnt sure if we were going to make them chip into an exsisting slab to bond it so the 3' can be reached.

Top
#3402 - 01/06/07 11:49 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I am not sure you wouldn't have to chip out any concrete within 3 feet. I don't see any relief for existing decking.

Top
#3403 - 01/07/07 01:25 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
Thats what I was thinking

Top
#3404 - 01/08/07 06:54 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Nick is 100% correct and I have an informal opinion from NFPA on that!

Second I understand the informal interpretation from Building Officials Association of Florida permitting the wire mesh is to be reversed since mesh is not one of the permitted items to be used as the equipotential bonding grid.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3405 - 01/09/07 09:13 AM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
As far as the exisiting decking. Im under the opinion that if it is a walking surface and this walking surface is in the 3' requirement then the walking area has to be part of the E grid.Im not sure there is an exception for exsisting decks.

Top
#3406 - 01/09/07 09:17 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
There is no exception!
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3407 - 01/09/07 10:05 AM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
I agree. If you have an walking surface and it falls in the perimeter of 3' it has to be chipped and made code worthy. Thanks Mike. We are having a big deal about this here and Im trying to convince the BO to not allow wire mesh also about the exsisting slab sinario.

Top
#3408 - 01/12/07 07:15 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Just for information:
I have requested a Formal Interpretation from NFPA. Based on the 2005 NEC is welded wire mesh permitted to be used as the equipotential bonding grid per 680.26(c).

We shall see what comes back?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3409 - 01/12/07 08:42 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Good Job Mike!
_________________________
Bryan P. Holland, MCP

Top
#3410 - 01/12/07 10:52 AM Re: 680.26 Bonding Methods
Rob Reading Offline
Apprentice Member

Registered: 12/09/06
Posts: 15
Loc: Oviedo, Florida
Thanks, Mike
_________________________
Rob Reading CBO,MCP
Plans Examiner
City of Oviedo
P. 407-971-5767
rreading@cityofoviedo.net

Top
#3411 - 01/12/07 10:57 AM Re: 680.26 Bonding Methods
Vince Offline
Mechanic Member

Registered: 01/05/06
Posts: 126
Loc: South Florida
What if the deck is made of wood. Is the 3' grid still required?

Top
#3412 - 01/12/07 10:59 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
No.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3413 - 01/12/07 01:25 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I agree that if this is an elevated deck 680.26(C) does not apply.
The real question is what is the definition of "paving" Is it just concrete, brick and stone?
Does that include asphalt? What if they come up with a plastic composite paver? Would we be concerned with the dirt between the pavers?

680.26(C) certainly brings up more questions than NFPA answers.

Top
#3414 - 01/12/07 02:20 PM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Yes, Yes, NO.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3415 - 01/12/07 08:30 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


So they would need a grid under a plastic composite paver?

Top
#3416 - 01/15/07 08:18 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
So get this. In our meeting at work we were talking about this very same subject. It was brought up by the pool contractors what should the grid be made of? We threw around some answers. I spoke of what was discussed on this site and what I believed in and its intent. So I researched and found the American Concrete Institute. I asked....


Inquiry: Is welded wire mesh by definition concidered structural steel?
To: Robert Smith
Subject: 70015-NM-318-Is welded wire mesh by definition concidered structural steel? - 6


Dear Robert:

ACI publishes codes, specifications, and reports for the concrete user. This message is in response to your technical question/inquiry.

Yes it is - as defined in ACI 318, Section 3.5

So is this a repitable(sp) Institute and / or responce and has anybody ever heard of ACI, Section 3.5. Because I think my boss is going to approve welded wire mesh in slab for the grid and copper in the ground for the grid.

Just when you thought this was dead right?

Top
#3417 - 01/15/07 09:23 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
I agree but that was never really the question. The 2005 NEC says "steel rods". Ask the ACI person if welded wire mesh is a steel rod, and I bet he will tell you no.

Not trying to be a smart alec, but just pointing out the dilemna that the CMP left us all with. There will be a formal NFPA interpretation on this, but not for about 6 months.
_________________________

Top
#3418 - 01/15/07 09:42 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
Nice catch Nick Either way the BO is going to allow the mesh I believe.

Top
#3419 - 01/16/07 08:20 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Ok so let’s say that wire mesh is ok.....

1. How much lap is required to provide a proper bond between sections of #10 steel wire mesh?
2. How do we make the connections between sections?
3. If tie-wires are ok...how many do we need to make a proper bond connection?
4. Do we need to weld the sections?
5. If we use a listed clamp, will the fact that there are dissimilar metals involved be a problem?

If these items are not taken into consideration, will the equipotential bonding grid in the deck actually have voltage gradients from one part of the deck to another?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3420 - 01/16/07 10:28 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
This and many other aspects of the 680.26 issue were discussed in great detail this past weekend at the IAEI Florida Chapter Board of Directors Meeting in Orlando. I was in attendance at this meeting and heard the opinions of many of the members present.
The bottom line as we all well know is that the 2005 language is not very good and has plenty of holes. The consensus was that the scope of the NEC does not cover nor specify how structural reinforcing is to be installed at a pool deck. The NEC only calls for bonding of structural steel if installed and present. In the event no structural steel is present in the deck, only then is the alternate means needed.

It really isn't then intent, nor a prescriptive requirement of the code to install structural steel exclusively for the purposes of creating a bonding grid. This again is not the scope of the NEC. If the design professional wishes to add structural steel to the deck, and specifies wire mesh, it is left up to the individual AHJ to determine if that wire mesh is suitable for the use as the bonding grid material.

At the end of the discussion, it was agreed that bonding of the perimeter surfaces could be performed in a method as described in the 2008 if acceptable to the AHJ per 90.4 even though it is not specifically adopted at the time of the deck installation.
_________________________
Bryan P. Holland, MCP

Top
#3421 - 01/16/07 11:50 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Still...the questions remain unanswered.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3422 - 01/16/07 12:38 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
NEWSFLASH!

A FRIEND SHOWED ME THIS TODAY!

IT IS OUT!! THE "BONDING MAT" IS HERE:

EQUIBOND GRID SYSTEM

NOW THERE IS NO MORE EXCUSES!
_________________________

Top
#3423 - 01/16/07 11:46 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Quote:
The consensus was that the scope of the NEC does not cover nor specify how structural reinforcing is to be installed at a pool deck.[/QB]
But the code specifies "rods" for 680.26(C)1

Quote:
It really isn't then intent, nor a prescriptive requirement of the code to install structural steel exclusively for the purposes of creating a bonding grid. This again is not the scope of the NEC. If the design professional wishes to add structural steel to the deck, and specifies wire mesh, it is left up to the individual AHJ to determine if that wire mesh is suitable for the use as the bonding grid material.[/QB]

But the code specifies "rods" for 680.26(C)1

[QUOTE]At the end of the discussion, it was agreed that bonding of the perimeter surfaces could be performed in a method as described in the 2008 if acceptable to the AHJ per 90.4 even though it is not specifically adopted at the time of the deck installation. [/QB]
But the code specifies "rods" for 680.26(C)1 and the 2008 has nothing to do with it and is not legally in force


90.4 is exactly what we don't need now.


553.72 Intent.--

(1) The purpose and intent of this act is to provide a mechanism for the uniform adoption, updating, amendment, interpretation, and enforcement of a single, unified state building code, to be called the Florida Building Code, which consists of a single set of documents that apply to the design, construction, erection, alteration, modification, repair, or demolition of public or private buildings, structures, or facilities in this state and to the enforcement of such requirements and which will allow effective and reasonable protection for public safety, health, and general welfare for all the people of Florida at the most reasonable cost to the consumer. The Florida Building Code shall be organized to provide consistency and simplicity of use. The Florida Building Code shall be applied, administered, and enforced uniformly and consistently from jurisdiction to jurisdiction.


Decide ye must... whom ye shall serve, ye who be at the crossroads...
-Yoda
_________________________

Top
#3424 - 01/17/07 06:33 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Sometimes code changes create unintended consequences that were unforeseen before the final published draft. There is no argument that the 2005 edition of the NEC has wording that excludes the use of wire mesh as an acceptable material. The argument is whether or not the wire mesh would be suitable for use in particular instances were it would be protected from corrosion and would be as effective as copper or steel rebar. I don't think anyone feels wire mesh is suitable under pavers.

The product you posted a link to by CMI provides a convenient and practical method for making a paved deck surface compliant with the current version of the NEC. I am just not certain it would be necessary to require this product if wire mesh is specified by the pool/deck engineer as structural reinforcing steel in a poured deck.

In the event the 2008 NEC includes new wording that eliminates the "grid" arrangement at the perimeter surfaces and replaces the requirement with a simplified single ring method, would that not identify the actual intent of the section in the 2005 NEC?
_________________________
Bryan P. Holland, MCP

Top
#3425 - 01/17/07 06:40 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
1. If "wire mesh would be suitable for use in particular instances" as you stated.....than how about someone providing an answer to the installation questions I asked, and with what proof?

2. Let me ask the same question again. Is it legal to use parts of a code that is not adopted as the state code at this time?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3426 - 01/17/07 09:07 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
No it is not Mike. Where has the Bryan Holland that we know gone to? He knows that we can't go by "what ifs" in the next code cycle. From what I heard, the 2008 is going to stay THE SAME except for the bonding of the pool water. But putting that aside...

Given a code change of significant proportion (but not nearly impossible) everyone is dealing with the politics rather than a way to just comply. Stay out of the politics!

Mesh is unacceptable and opens a Pandora's box. First off, pool contractors often don't chair up the mesh properly. They also seldom "pull" up the mesh during a pour. If the mesh lays on the bottom of the concrete, it will deteriorate and then so will the bonding grid. If this happens there could be different gradients at different locations in the deck!

Steel rods have a prescribed overlap. The lap makes the rod "continuous". What is the prescribed overlap for mesh, in order to achieve acceptable and uniform equipotential bonding? Where is the test data on this?

How does the mesh connect together? Twisty ties? Do you really think the pool companies will sinch up those twisty ties tight with the mesh? Will the inspector who red tags this issue get called into the B.O.'s office (assume B.O. typical with no electrical background) only to be told that "he/she is being to "hard" on the pool contractor?"

What is the effect of chlorine on the mesh, if any? Where is the test data to back that up?

What end product does this provide to the consumer, by using this "alternate" method (that ISN'T the alternate method described in the NEC)? When a code specifically gives you an alternate method, how can someone come up with their own alternate method at that point? God forbid if there is some accident where the person gets shocked or worse, and one of these alternate-to-the-alternate "mesh" bonding grids are under the deck.

If we should err, should it not be on the side of safety?

At times some describe me as pig-headed. Even if that is true, don't I deserve better protection than a pig, cow, or horse?

A group of people sent me an informal interpretation on this very issue. I read it over and over again, and I can't find anything I can disagree with. There are no politics in this informal interpretation, just hard, cold, facts:


Swimming Pool Equipotential Bonding


cool
_________________________

Top
#3427 - 01/17/07 09:20 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
I agree 100%!
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3428 - 01/17/07 02:24 PM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
I guess the difference is who you work for and what their affiliations are. My BO hangs his hat on Building Officials Association of Florida interpretations. They are the only recognized organization contracted by the DCA to give non-bonding interpretations of the FBC, including electric related questions. Unless the NFPA comes out with a TIA or Formal Interpretation, the Building Officials Association of Florida document is what we (my BO) are going with.

I have also personally discussed this issue with both Don Jhonson of CMP 17, Doug Harvey who released the final draft version of the Building Officials Association of Florida interpretation, and it was discussed at the IAEI Florida Chapter Meeting this past weekend.

I am not making the decision myself nor establishing my personal opinion on the matter. I am simply posting the information as I have received it for the forum to consider.

Please don't assume I have degraded the sanctity of the NEC or my personal integrity based on this specific issue alone.
_________________________
Bryan P. Holland, MCP

Top
#3429 - 01/17/07 02:59 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
The Building Officials Association of Florida "informal" interpretation is non-binding and non-legal. The 2005 NEC is an adopted legal document and part of the FBC.

You said it yourself - the difference is who you work for and who your affiliations are. I work for the end-user of that pool. Until an NFPA interpretation comes out that says otherwise, they deserve a code-compliant installation that corresponds to the wording in the NEC,and nothing less.
_________________________

Top
#3430 - 01/17/07 11:17 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
APSP Files Request for “Formal Interpretation” of the NEC Equipotential Bonding Grid

Alexandria VA (February 23, 2005) -- The Association of Pool & Spa Professionals (APSP) Technical Committee has reviewed the history, wording, and subsequent interpretations of Article 680.26(c) Equipotential Bonding, as published in the 2005 National Electric Code (NEC). The APSP has learned that there are significant differences in the actual code wording versus the interpretations found in the NEC handbook and additional private industry publications. The APSP Technical Committee Chair, Lee West, sits on the NEC Panel (17) that drafted the new code and is clear on the original intent of the new language.

The specific conflict of interpretation pertains to the apparent requirement for an equipotential bonding grid to "cover the contour of the pool and the pool deck." Based upon certain interpretations by Building Code Officials, there have been reports of "Red Tagged" vinyl-lined pools, fiberglass composite pools, and spas. The original intent of the new code language was to provide for a grounding plane extending horizontally three feet out from the pool perimeter. This would be typically accomplished with bonded conductive rebar found in the pool deck. In pool decks that use fiber mesh, pavers, stone, or other non-conductive material, several alternatives are offered to achieve this 3-foot-perimeter grounding plane.

As a result, the APSP has submitted a request for a Formal Interpretation (FI) from the NEC. The APSP recommends that Building Code Officials and Pool Builders obtain and follow the actual code Article 680.26(c) and disregard the confusing interpretations until the FI is published. The APSP understands the urgency of the situation and will communicate the FI results immediately upon completion.


Association of Pool and Spa Professionals
_________________________

Top
#3431 - 01/18/07 01:25 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I don't think the tie wires contribute much to the conductivity of the matrix, whether this is a Ufer or a pool deck. They never really get tied that tight. We are really depending on the conductivity of the concrete. Normal lap of mesh is one "square". I am not sure of how other AHJs deal with chairs but the Lee County guys are pretty strict that they must be there and be affective. I know a lot could happen between the time it is inspected and when it is poured but this should be up in the concrete. If it is laying in the dirt, I see little difference in whether it is 6 over wire or #3 rebar. As an aside, I know a lot of contractors will tie #3 to the mesh, just so it will lay flat. If they did have a couple #3s would that make Nick happy? It wouldn't be a 12x12 but it would be a double ring in addition to the 6 over mesh. That might be the best of both worlds.

Top
#3432 - 01/20/07 03:19 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
Im going to a seminar on the 25th in Miami held by the IAEI and the speaker whos name I cant remember now is going to speak. Hes someone on the code making panel so Ill bring up these questions at the seminar.

Top
#3433 - 01/22/07 05:54 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
His name is DON JHONSON and he is the chairman of CMP 17.
_________________________
Bryan P. Holland, MCP

Top
#3434 - 01/22/07 10:11 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Bryan, I will see you there, I am also going
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3435 - 01/22/07 01:42 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
Yes thats it. Thanks See you there.

Top
#3436 - 01/25/07 02:44 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
I heard from a reliable source that the CMP guy JHonnson said that "rods" means rods, mesh is not acceptable, and then he told everyone to "just use the 2008 code" and then he said use 90.4.

Very unimpressed if this is true, and I have no reason to believe that my source isn't providing me with accurate information.
_________________________

Top
#3437 - 01/26/07 05:41 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Hey Nick. That is pretty much what I am hearing as well. That was basically what Mr. Jhonson expressed to me on the phone a few weeks back before I contacted you about the matter.

I have presented all the comments posted here and from other various sources to my chain of command for their final word.

At this point, I am only comfortable enforcing the exact wording of the 2005 NEC until further notice from the NFPA is provided as either a TIA or Formal Interp.

The rumor around some at the IAEI is that Florida may not adopt the 2008 and opt to skip to the 2011 edition at the adoption of the 2010 FBC.

(P.S. I didin't make it to the meeting in Miami but we had a rep. present from the Gulf Coast Div.)
_________________________
Bryan P. Holland, MCP

Top
#3438 - 01/26/07 05:51 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Maybe there is a way to repeal (or "unadopt") that section of 680 in the 2005 NEC.
_________________________

Top
#3439 - 01/26/07 07:49 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Lessons learned in Miami.
1)If using steel it must be the equivalent of the steel used in the pool structure, in other words Rod means rod not mesh.
2)If using the alternative copper grid, it must be attached to the pool every 12 inches, with a #8 bonding jumper.
3) If using a free floating steel rod grid under the paved walking surface, it to must be attached every 12 inches with bonding jumpers.
4) NEC 2008 will change all of this to a #8 copper encircling the pool in a ring attached at 4 places.
5) In May when this is ratified, you can use Art. 90.4 and allow this.
The 2008, which I am sure everyone has read, has taken out the verbage Paved walking surfaces to just surfaces which would include grass, rock etc.
All of the above were intrepretations of Don Jhonson of which I wasn't to impressed by.
I had a feeling from the room that we are all going off in different directions and thus and I don't think this is fair to the pool companies.
I agree with Bryan and Nick and will enforce the 2005 until such time directed otherwise.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3440 - 01/26/07 07:54 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Don't forget this also applies to outdoor installations of spas and hot tubs, which means if a person installs a new hot tub out on his patio he must chop up the concrete to install the equipotential grid. Also fountains that have water common to the pool. This is going to be beautiful.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3441 - 01/26/07 09:35 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
"I had a feeling from the room that we are all going off in different directions and thus and I don't think this is fair to the pool companies."

You've got that right! I got the same impression at the IAEI state meeting a few weeks back. frown
_________________________
Bryan P. Holland, MCP

Top
#3442 - 01/26/07 09:50 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
That's why I don't go to the meetings anymore....it's the same old thing everytime.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3443 - 01/26/07 10:40 AM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I would not be surprised if a lot of AHJs are deleting this requirement. The general idea is OK but the comments on implimentation are absurd. Why would a COPPER grid need to be connected every 12" when the whole pool shell only gets connected to the rest of the equipment and metal objects once?
Where is the body count to support this? You would think people are dropping like flies from energized pool decks.
NFPA is out of control.

Top
#3444 - 01/26/07 11:06 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Just look at the CMP lists in the front of the NEC and see how many members represent a manufacturing interest. Everything from whole house afci's, tamper resistant receptacles, receptacles listed for wet locations, and even roughed box protective coverings are soon to be code requirements and have all been proposed by manufacturer's or their representatives.

There is a lot of money to be made from code changes that mandate the use of a product!!!
_________________________
Bryan P. Holland, MCP

Top
#3445 - 01/27/07 05:29 PM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
The body count I heard at the meeting was 3, Two in a hottub and one from an energized pump motor (wasnt grounded). One of the reasons that prompted the change in the 2008 was Australia had conducted numerous tests and found the single # 8 copper encircling the pool reduced volatge gradients just as well as the 3 foot grid. I knew and inspector who wanted to bond the pools this way quite a while ago, wished I had let him. Did any one notice one of the members on panel 17?? Seems to me He would have quite an interest in copper!!!
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3446 - 01/29/07 05:22 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
EXTRA EXTRA READ ALL ABOUT IT!



_________________________

Top
#3447 - 01/29/07 09:28 AM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I like that he "is happy" not to give you a formal intrepretation, nor to even really answer the question.

Top
#3448 - 01/29/07 09:40 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
1. NFPA Regulation will not permit a formal interpretation since the code language is specific. There is nothing to interpretate.

2. He also did in fact provide the answer:
Quote:
"The welded wire mesh that you have described is not recognized in this section of the code".
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3449 - 01/29/07 10:15 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
To all that were at the meeting, do you subcribe to the tieing the grid every 12 inches with jumpers to the pool steel? Do we really need to bond to the grid every 12" and why or why not?
Im not sure I believe this to be nessesary. I could be wrong thats ok. I just think bonding the grid with #8 for jumpers from pool steel to grid would be sufficient. One to start. One to bond grid to grid together and one from the end back to pool steel.
What say you?

Top
#3450 - 01/30/07 05:57 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Whether I agree or not this was the stated way by Mr. Jhonson. The intent is for the grid (12x12) to extend up onto the deck and under the paved walking surface for 3 feet. But if a test was done to show a ground ring around the pool is suffecient and is ratified in May will everyone be willing to accept that?
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3451 - 01/30/07 06:03 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


Electricman brought up spas. Since "portable spa" is not addressed in the NEC (just indoor and outdoor)does that mean that if they drop a home depot packaged spa on the lanai they need to rip it up and install the grid?

Top
#3452 - 01/30/07 06:52 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
Quote:
Originally posted by electricman:
Whether I agree or not this was the stated way by Mr. Jhonson. The intent is for the grid (12x12) to extend up onto the deck and under the paved walking surface for 3 feet. But if a test was done to show a ground ring around the pool is suffecient and is ratified in May will everyone be willing to accept that?
Im not sure I agree or understand is more like it, but I want to. I was thinking this morning along those same lines about the 12"x 12" up and around the pool to the deck also. It make sense I think?

I brought up minimum size of structual steel also and taking my answer to the BO, hes still leaning toward welded wire mess. Why did he send me down there if what I bring back isnt well you know.

Top
#3453 - 01/30/07 10:10 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
No matter how you slice it, wire mesh is NOT recognized by the Code, or NFPA for that matter.

If any particular group,......... or B.O. wants to say something else, then they are out there flappin' in the breeze. I will tell you why: In the event of a customer problem, shock, or God forbid an electrocution, any jurisdiction who used a "wire mesh" material substitute is just open season for the legal community.


material substitute


:p
_________________________

Top
#3454 - 01/30/07 10:37 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I ask again, is there a documented case of someone being killed or injured because of a potential difference between the deck and the pool shell? If anything I would think this would be a worse problem with vinyl or fiberglass pools since you don't have the "Ufer" effect.

Top
#3455 - 01/31/07 07:49 AM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
I agree Nick. How about the connection from the pool shell to the grid? Anybody?

Top
#3456 - 01/31/07 08:41 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I agree the language for the steel mesh being OK is simply not there. I think bonding it to the pool every 12' is overkill though, If you have 8ga copper mesh around the pool a few connections is plenty (2008 may say four), and then only for redundency in case one fails to a yellow boot during the construction.

Top
#3457 - 02/01/07 06:09 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Again, with #8 bonding jumpers every 12 inches as explained by Don Jhonson.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3458 - 02/01/07 06:10 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
I am not saying I don't agree with you but can we legally be safe with any other method?
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3459 - 02/01/07 07:44 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Do you see the problem? When you deviate from the code and permit something else you make for all kinds of different problems and interpretations.

If you stick with the code its a done deal.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3460 - 02/01/07 07:58 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
I agree Mike, 100 per cent
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3461 - 02/01/07 07:46 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


The problem is I don't see the "bond to the pool shell every 12" with 8ga copper" in the code. A single 8ga copper seems to be all you need to bond everything else in the grid.
If this does get recognized I imagine the real answer is they will just continue the pool steel up and over the bond beam in one continuous piece that gets tied into the pool shell. (for a concrete deck)
That still would not explain why a copper ground grid under pavers would need that much bonding to the pool shell. We will let them bond a 1000 square foot pool cage with a single #8.

Top
#3462 - 02/02/07 08:14 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
There is no requirement in the code section to require the deck bonding grid to be attached to the shell every 12" with a #8 bonding conductor.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3463 - 02/03/07 10:30 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
Quote:
Originally posted by Mike Timpanaro:
There is no requirement in the code section to require the deck bonding grid to be attached to the shell every 12" with a #8 bonding conductor.
I see that also. I can also see the intent of it coming in the 12 x 12 pattern over and to the dek. The trouble about bending the steel over and keeping the pool steel as you might say one piece is that a crack could very well travel along the deck and into the pool and create a leak.

Top
#3464 - 02/03/07 11:44 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


When they do this they do not pour the deck with the pool shell. One is shot and the other poured or pumped after the plumbing and this will be a cold joint in the concrete. It is just the steel that sticks out. The deck crack should stop at the pool bond beam interface. They usually only have a rod every 3-4 feet. I have some pictures if you want to see one.

Top
#3465 - 02/05/07 09:00 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Did everyone who attended the Miami meeting hear Don Jhonson say the deck if separate had to be attached every 12 inches?
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3466 - 02/05/07 10:04 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
Quote:
Originally posted by electricman:
Did everyone who attended the Miami meeting hear Don Jhonson say the deck if separate had to be attached every 12 inches?
I just remebering him say that the connection had to be every 12".

Top
#3467 - 02/06/07 05:56 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Again where is that wording in the code section?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3468 - 02/06/07 06:13 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Mike, the phrase equipotential bonding "Grid" with Grid being the key word is the best I can figure for the intent of every 12 inches. "The bonding "Grid" shall extend under paved walking surfaces for 3 foot horizontally beyond the inside walls of the pool...".So to continue the grid to the deck you would need bonding jumpers every 12 inches. Does this make sense?
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3469 - 02/06/07 06:35 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Nope. In the 2002 one of the options for the common bonding grid was a #8 copper conductor run around the pool.

With a fiberglass pool there is no connection to the pool shell....no rebar.

There is no definition as to how the grid is to be constructed when using rebar, only when the field-fabricated grid is constructed with #8 copper conductors.

The bonding conductor only needs to be connected to the grid in 1 location. In the 2008 code it is to be attached in 4 locations.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3470 - 02/06/07 01:44 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
Ill take I can see both sides of this for 100 Alex = )

Top
#3471 - 02/08/07 03:50 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
The Building Officials Association of Florida FTC( Building Official Association of the Treasure Coast) is having a meeting on Thurs of this coming week and Dave Harvey (I believe his name is) will be discussing this subject. If anybody is interested I will post more detailed information ( place, time, date).This should be interesting = /

Top
#3472 - 02/08/07 11:59 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Name is Doug Harvey, and I will run into him in about 2 weeks. I'm not really interested, but please do let us know what he says. I think he was part of the Building Officials Association of Florida opinion, but don't quote me on that. The Building Officials Association of Florida made an informal opinion of convenience. NFPA admits that wire mesh isn't recognized. I can't believe the Building Officials Association of Florida isn't embarassed by the informal opinion they put out.

I have been using this informal opinion:

Pool Equipotential Bonding


:p


PS - It would not be complete unless I said this: There are many jurisdictions that don't feel comfortable inventing their own code, and they are going by the wording in the NEC. No matter what anyone "thinks" or what anyone's "opinion" is, these jurisdictions are going by the letter of the code. My hat is off to them.
_________________________

Top
#3473 - 02/09/07 06:01 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Just so the record is clear, I had no part in the writing or wording of the Building Officials Association of Florida informal interpretation #4856 and I too believe Mr. Harvey was the final editor of the document.

I have received notices from several surrounding jurisdictions with their intended enforcement of this issue. Most appear to be accepting what the 2008 NEC section is likely to permit/require as an alternative to "structural reinforcing steel". The issue will be discussed for hopefully the last time at our IAEI Division Meeting next Wednesday in hopes to get everyone on the same page in this region of Florida.
_________________________
Bryan P. Holland, MCP

Top
#3474 - 02/09/07 12:00 PM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
#1. I don't think that is a good option since the 2008 isn't in print yet....don't know what it will read.

#2. It isn't a legal adopted code for Florida and I hear there is talk we may not adopt the 2008 at all and go right to the 2011.

Lets see what Nick thinks:
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3475 - 02/09/07 12:04 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
I think the best option and the safest option for everyone involved in this debacle is to stick to the wording in the code.


PS - rasmith, if you can, ask Doug about the procedure on how they pick the committee that makes the informal opinions.
_________________________

Top
#3476 - 02/09/07 01:49 PM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Nick,

The typical manner in which Building Officials Association of Florida selects members of this or any committee is by request from the individual wanting to participate. All one most do is contact either Donald Fuchs or Doug Harvey and indicate interest. Once they determine the individual has a special knowledge or expertise of a particular code or segment of the construction industry, those persons will be given opportunity to review informal requests by submitters and make responses to those requests if they so wish. Once a sufficient number of responses are received, I understand a committee at Building Officials Association of Florida goes over each question and the committee responses, and then form the final response.

When it comes to the group that specifically looks at electrical questions submitted, all are fine and upstanding members of the IAEI. I do not have any knowledge of those that specifically contributed to the #4856 response.
_________________________
Bryan P. Holland, MCP

Top
#3477 - 02/09/07 04:05 PM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
I agree with Nick and Mike
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3478 - 02/12/07 03:55 PM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
This pool company called me about a month ago asking what we wanted to enforce the equipotential bonding grid, I explained and he didn't argue or put up a fight like a lot of them did and here are the results.






[img]http://i153.photobucket.com/albums/s201/inspector830/Picture003.jpg[/img]
[img]http://i153.photobucket.com/albums/s201/inspector830/Picture002.jpg[/img]
[img]http://i153.photobucket.com/albums/s201/inspector830/Picture001.jpg[/img]
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3479 - 02/12/07 03:56 PM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Amazing what they can do if they put their minds to it.He also said it only cost about 200.00 more to do it this way and wasn't that difficult.
Almost right out of the handbook.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3480 - 02/12/07 04:00 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
IMAGINE THAT! IT CAN BE DONE! What about all the whinin' and gaggin' and moanin'? Looks like they complied and even though it was a substantial change, it wasn't impossible. GREAT JOB PAUL! Keep up the good enforcement!
_________________________

Top
#3481 - 02/12/07 04:33 PM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
What will make the problem worse than it would be is that there will not be uniform enforcement of the code section since Building Officials Association of Florida put out an INCORRECT informal interpretation of the code section, and half the state will go with that and make it hard for the guys that will do it according to NFPA.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3482 - 02/12/07 04:41 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Yes, you are correct. There seems to be more trouble in Florida now with Chief Inspectors and Building Officials enforcing the eq. bonding plane code, rather than the contractors - who PREFER THE UNIFORM ENFORCEMENT!
_________________________

Top
#3483 - 02/12/07 04:50 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
When this code first hit I made a post on another website to give fair warning. The reaction wasn't "What can we do to enforce this" but rather "What can we do to NOT enforce this".
_________________________

Top
#3484 - 02/12/07 05:13 PM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
I'll tell you what they can do to NOT enforce the code section.

Follow proper procedure. Go to NFPA and CHANGE IT!
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3485 - 02/12/07 06:58 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


My only problem with this method is structural. Since the deck becomes the edge of the pool 4" deep a crack in the deck can be a leak in the pool.
They stubbed out rebar on my pool too but it stubbed out of the tie beam which was shot as part of the shell. Then trhe deck was poured later so there was a natural place for a deck crack to stop before it got to the pool.
I suppose if they really did a good job backfilling the pool the deck wouldn't crack but that seldom happens. Sinkholes in the backfill is the main reason production builders like pavers.

Top
#3486 - 02/12/07 07:16 PM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
My neighbors pool had a sinkhole under it and cracked the pool but not the deck- go figure. I give them both options, free float the grid on the deck and bond it to the shell, or the way shown in the pictures. (concrete pools). I'm not an engineer but looking at the photos, the shell is poured first and then the deck next, like one sitting on the other. I can't see where a deck crack would carry through to the pool.Any takers?
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3487 - 02/12/07 07:17 PM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
WE might get up to 20 pages on this discussion, Amazing.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3488 - 02/13/07 05:58 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Great Pics! Thanks!
_________________________
Bryan P. Holland, MCP

Top
#3489 - 02/13/07 07:52 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


In those pictures it looks like the white "rim" you see around the pool is actually just the form for the concrete and it will actually be the top 4" of the pool wall.
I suppose if the water line is >4" below the deck it isn't a problem if it cracks.

Top
#3490 - 02/13/07 07:58 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


BTW I know you guys always say you don't care what happens the day after the CO but how many think that ugly [censored] #8 going up to the window frames in picture 2 will last a week before wifey cuts it? That is some nasty work and putting a couple rusty straps on the wire is not going to make it look any better.

Top
#3491 - 02/20/07 05:20 PM Re: 680.26 Bonding Methods
rasmith Offline
Journeyman Member

Registered: 03/27/03
Posts: 72
Loc: vero beach
Well its official in my juresdiction welded wire mesh has been approved. I didnt go to the BOAFTC meeting, beause I was on vacation but I got the official informal interpetation from Building Officials Association of Florida and my boss.Once I heard that Doug Harvey was going to speak and that he was the one that drafted the informal interpitation there was a fat chance that anything I said or brought up was going to change anyones mind. Doug is a smart man and more versed in the electrical field then I. Im not taking that away from him. Im just in agreement with others on this site that the code is very clear on what its asking for and welded wire mesh isnt one of them. So my inspection results will now read if in code compliance,"approved as per IRC Bld official". wink

Top
#3492 - 02/21/07 05:43 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
You are 100% correct. I think that Building Officials Association of Florida has done a great injustice and have failed in that they put out an opinion that was popular but NOT CODE . Since that is the case we now have a division of how the code will be enforced instead of being uniform. This is a great disservice for contractors and inspectors.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3493 - 03/02/07 09:28 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Quote:
Originally posted by gfretwell:
Electricman brought up spas. Since "portable spa" is not addressed in the NEC (just indoor and outdoor)does that mean that if they drop a home depot packaged spa on the lanai they need to rip it up and install the grid?
Nobody answered this, How about it?
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3494 - 03/02/07 10:13 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
There is a difference between "portable spa" and "packaged spa". See definitions 680.2.

A portable spa is one that is intended to be used once, drained and put away. I would not require the equipotential bonding grid for that since it is the same type application as a storable pool like in 680 Part III.

A packaged spa is a factory-fabricated unit consisting of the water-circulating and control equipment etc..mounted on a common base but does not include the spa or hot tub vessel. This type of set-up is intended to be used with a remote tub vessel. I would require the equiopotential bonding grid located in the deck around the tub vessel for outside installations.

A self-contained spa is a factory-fabricated unit consisting of a spa or hot tub vessel including all the water-circulating, control equipment etc..integral to the unit. I would require the equiopotential bonding grid located in the deck around the tub vessel for outside installations.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3495 - 03/02/07 10:39 AM Re: 680.26 Bonding Methods
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
I agree with Mike.

I asked this very question to Don Jhonson and his reply was basically,

1. They can break up the concrete and reinstall it with a grid,

2. They can pour another pad on top of the existing with the grid.

3. They can permanently cover the surface with a non-conductive material. (wood deck)
_________________________
Bryan P. Holland, MCP

Top
#3496 - 03/02/07 10:50 AM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Rasmith, that is a very well-thought out and diplomatic way to handle the situation.

I ran into Doug Harvey a week ago. I will say this about him: Doug is a nice guy. He is polite, he is respectful, he understands laws and rules, and he takes the time to read them. He is good in front of an audience. He is genuinely a pleasure to deal with. I just think in this case about this particular subject -- he erred. I think all things considered he would probably agree with us that mesh is not acceptable. But I did not get into this discussion with him because I didn't want to hash it out again. He knows where we stand, I can assure you of that.

Spas?

Spas?

I guess if it was a new installation I would make them put in the grid. If it was an existing patio what code section would you cite to make them bust up the patio cement?


?
_________________________

Top
#3497 - 03/02/07 11:15 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Mike, I dont see it in the code about a portable spa and have never seen one. The only spas I have seen are large enough to qualify for the statement in definition for spa or hot tub that says "Generally a spa or hot tub is not designed or intended to have its contents drained or discharged after each use. So many contractors think the huge cedar enclosed spas that they plop down on a deck are portable.
Bryan you are 100 percent correct, Dan Jhonsen stated that exactly at the Miami meeting.
and even added notching the concrete to accomodate a #8 around the spa.
But as Nick asks and so do I how do you make someone rip up there deck or patio? I can see whats going to happen here, We won't see any more spas, believe me.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3498 - 03/02/07 11:37 AM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
You are correct there is no definition of portable spa but they do have them. They have all plastic walls, are round, and designed to move from on location to another.
The links below should help:

http://www.spadepot.com/warehouse/smartub.htm

http://www.thermospas.com/benefits/fiscal.aspx?source=PG0038&gclid=CKDZ35LS1ooCFQgTWAodHVy2fg


Nick I agree with you but we can use the same idea as the one for the (ufer) concrete-encased electrode..you know I got that from NFPA that we should chop up the footing if it's missed...Ha! Ha! Remember??

Oh...this is a joke!
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3499 - 03/02/07 02:33 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
I know, and I made that same joke when I was talking with the electricman just the other day!


Maybe for the spas we can make them put a non-conductive rubber surface under the spa that encircles the spa and goes 3' out on every side. Damn! I promised I wasn't going to do this anymore! That's what the CMP is for!~


I wonder what Mr. Jhhonsohn would say?
_________________________

Top
#3500 - 03/02/07 02:36 PM Re: 680.26 Bonding Methods
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
How did you like the link?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#3501 - 03/04/07 07:37 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I suspect if you really started enforcing the "deck bonding" on spas, the manufacturers would quickly respond with a wood deck kit that matched the spa walls. I suppose if you slam it in the corner of the screen cage you would really only have to deck the two sides that were inside the cage. You would also have to bond the cage.

Top
#3502 - 03/05/07 07:55 AM Re: 680.26 Bonding Methods
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
Mike, excellent, I have never seen one of those spas, and I agree with your statement this is a joke. I guess the wooden decks under the spas on existing patios or lanais is looking pretty good.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#3503 - 03/07/07 01:26 PM Re: 680.26 Bonding Methods
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
What if you have to run an electrical line? This part of the add is a joke:


No Building Permits Necessary
Our portable hot tubs do not require any permanent connection to your home’s plumbing. You simply fill your portable hot tub with water from a garden hose! Since our hot tubs are legally categorized as portable home appliances, they do not require building permits in most locations (the only time a permit would be necessary is if you permanently fix it into a setting, such as submerging it into a deck).
_________________________

Top
#3504 - 03/07/07 11:10 PM Re: 680.26 Bonding Methods
Anonymous
Unregistered


I bet the salesman tells them to have a new receptacle installed before the spa is delivered as a general purpose GFCI outlet.
I imagine there will also be some connected with orange cords. A lot of people will have problems finding a spare 16a or so on any circuit they can get to if they don't run an individual circuit.

Top
Page 1 of 20 1 2 3 ... 19 20 >



Active Topics
May Meeting Minutes
by Bryan Holland
Yesterday at 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
Registered: 02/02/07
Posts: 0
Forum Stats
518 Members
29 Forums
1892 Topics
8569 Posts

Max Online: 53 @ 03/30/12 04:16 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image