I know its not a big deal, but I really wish the editors of the NECdigest would do more to edit out errors or at least clarify comments and statements made in the magazine articles.

The case in point in the recent issue is the "Checking Ground Electrode Impedance" by, Frank Healy (Page 33)

Statement #1,


Quote:

Current will always find and travel the least-resistant path back to its source.



Critique by me: Doesn't current also flow through high-resistant paths such as humans????

Statement #2,


Quote:

The NEC specifies 25 ohms as an acceptable limit for electrode impedance.



Critique by me: 1. Impedance? Section 250.56 refers to resistance. There is a difference.

2. We all know 25 ohms is not a limit nor a requirement. 25 ohms has NO significance.

3. All electrodes? This section only refers to Rod, Pipe, and Plate Electrodes. There is nothing in the code that would prevent any of the other electrodes specified in 250.52 to have resistances above 25 ohms.

There are probably more, but I honestly stopped reading the article after that. We shouldn't be getting bad information or at least poorly written information from the NFPA, especially on NEC issues. I am also not sure I like articles in an NFPA publication written by a manufacturer of a product...
_________________________
Bryan P. Holland, MCP