John,
Seems like the key article for your question is 230.71, which allows up to 6 disconnects for:
each service permitted by 230.2
-or-
each set of service conductors permitted by 230.40 exceptions 1,3,4 or 5. If he is relying on exception #2 to support his stance, then that one is not listed as a possibility in 230.71.
I would normally ask a bunch of question at this point, like how large are these services, why wasn't this caught on electrical plan review if in fact it is a violation, etc., etc.
Edited by Nick Sasso (02/28/08 03:15 PM)