1. What is the definition of a field-assembled spa? 2. Is a field-assembled spa really a self-contained manufactured spa delivered to the site in pieces that requires assembly? 3. Is a field-assembled spa, component pieces motor, blower, heater, etc. (located next to the house)with a spa vessel (in the yard) build by the pool contractor....just like a pool...but its a spa?
I need to know if #3 is the definition of field-assembled and requires GFCI portection per 680.44.
_________________________
Michael J Timpanaro Inspector/Plans Examiner/CEU Instructor Florida
Registered: 10/05/04
Posts: 1622
Loc: City of North Port
I think both #2 and #3 can be considered field-assembled spas.
Thus, gfci protection would be required. Only when the spa, which is built like a pool, is commonly bonded with the pool as identified in Part (C) of the section, would gfci protection be exempt.
On the other hand, adding a heat pump to a pool doens't nake it a spa nor mandates the gfci protection.
I think this needs to be a judgment call based on the specifics of the installation on a case by case basis. I would tend towards the conservative.
I think this is a case where we need a definition in the code as to what field-assembled is.
Here in Sumter County in the Villages we have pool contractors building spa's, and swim spas in the back yard..it's built just like a pool but it is a spa, with component heaters, motors, blowers and a remote vessel. I think that they require GFCI protection for the equipment sometimes needing as many as 4 GFCI breakers, but I am getting alot of friction. That is why the definition of field-assembled is so important.
_________________________
Michael J Timpanaro Inspector/Plans Examiner/CEU Instructor Florida
#4777 - 03/13/0801:28 AMRe: 680.44 GFCI Protection
[Re: Nick Sasso]
gfretwell
Unregistered
I am looking at the 2002 (I don't have my 5 handy) but the changed the wording such that all spas need GFCI unless they are part of the pool, commonly grounded or they are 3 phase or more than 250v or they have heaters bigger than 50a.
Quote:
Except as otherwise provided in this section, the outlet(s) that supplies a self-contained spa or hot tub, a packaged spa or hot tub equipment assembly, or a field-assembled spa or hot tub shall be protected by a ground-fault circuit interrupter.
Nick Sasso
Post-A-Holic Member
Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
I would hate to think that something constructed in the field which resembles a spa would not have GFCI protection, especially if there is a failure with the heater or blower component.
Yes Nick this spa is installed in-ground and is constructed exactly like an in-ground swimming pool.....but it's a spa!!!
I wonder if this falls under what would be defined as field-assembled, and require GFCI protection. Remember that because there are component pieces more than one GFCI is required to protect all the equipment wired to the outside remote panelboard.
_________________________
Michael J Timpanaro Inspector/Plans Examiner/CEU Instructor Florida
GREAT....GREAT....job Nick!!! That UL guide is exactly what I needed. The definition of a field-constructed spa is just what they are doing out there and provides me with what I need to apply 680.44 GFCI protection.
_________________________
Michael J Timpanaro Inspector/Plans Examiner/CEU Instructor Florida
Nick Sasso
Post-A-Holic Member
Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Now keep in mind that the UL doc I posted is 2004, there may be an updated version. At any rate, I don't think they would change too much of the wording about what they call a "field constructed spa."
I don't think the NEC would actually need to have this definition as it is like saying - what is the definition of a site-built home? It is a home that is built "on site." I think it is pretty self explanatory. The UL information just backs up what we already know to be true.