I hope to have more details about this by tomorrow.
First report indicates:
the meter socket in question was a 200 amp bypass type. labled with "3 Phase 4 wire"
under the bypass mechanism, not easily visible, the center lugs were from a single phase unit with the center lug tagged to the meter can.
The electrician did not notice it
The inspector did not notice it
The Gulf Power lineman did not notice it
The Gulf power lineman installed a meter and energized the transformer
EVERYone noticed it then!
The contractor was from Mobile, AL
We do not know where the meter socket was purchased
BUT examination of stock at a supply house in Pensacola turned up some units with the same defect.
It may be an isolated case of a few units. It may be a widespread problem.
Lynn
--- On Wed, 7/9/08, Lynn Adams <lhadams@co.escambia.fl.us> wrote:
From: Lynn Adams <lhadams@co.escambia.fl.us>
Subject: Danger Warning.
DANGER
200 amp 3 Phase
Milbank meter sockets with lever bypass.
Some sold in the Pensacola area have had incorrect interiors, with the center phase grounded.
AT least one has been energized and exploded.
Check all stock and installations carefully. More identification to follow
Lynn Adams 595-3462
Attachments


_________________________
John Belew
Electrical Inspector/Plans Examiner
Santa Rosa Co.
johnb@santarosa.fl.gov