#6311 - 05/27/09 09:22 AM Rule 9B – 3.047, GFCI Protection
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1600
Loc: City of North Port
According to Rule 9B – 3.047, Section 2705.1 of the FBC and E3304.1 of the FBC-R will be amended to include to language found in Section 680.22(B) of the 2008 NEC which requires GFCI protection of both direct connected (hard-wired) and cord-and-plug connected pool pump motors.



However, there will also be an Exception for one-and two-family dwellings. This exception is NOT found in the NEC.



As indicated in the IAEI Analysis of Changes, Proposal 17-85 was rejected which suggested this rule be placed back into the NEC as it was in the 1999 edition. It was looked at again by CMP-17 after a review of data provided from the Consumer Product Safety Commission, National Injury Information Clearinghouse. (See Comment 17-75 of the 2007 Record of Comments.)



I can and have supported making amendments to the NEC when the code is made stronger and provides better protection to people and property, but can’t understand why or how the Florida Building Commission is in a position to reduce what is established as the minimum provisions by a consensus process.



For example, the requirement for bonding metal studs in buildings and structures enhanced the NEC requirements without creating a significant burden to builders and contractors. This new rule reduces the minimum provisions for safety of a nationally recognized standard with no real substantiation provided for creating the Exception.



I hope you all can take some time to review this matter and forward your comments and opinions to the Florida Building Commission.

_________________________
Bryan P. Holland, MCP

Top
#6312 - 05/27/09 11:32 AM Re: Rule 9B – 3.047, GFCI Protection [Re: Bryan Holland]
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1101
Loc: Ocklawaha FL.
I understand that not all on the commission are in favor of this.

For many years up north it is common to to cord and plug the pool pump motors. As you know this required GFCI protection for the receptacle. There have not been any problems with the GFCI unit to trip. Therefore their idea that GFCI protection for a hard wired pump motor will be a trip problem is unfounded.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#6317 - 05/27/09 08:24 PM Re: Rule 9B – 3.047, GFCI Protection [Re: Mike Timpanaro]
Ruben Rocha Offline

Senior Member
*****

Registered: 05/24/00
Posts: 764
Loc: Lutz,FL
I guess I am not really clear on this change.
Understood that GfCI protection is required. But what is the exception??
Nobody has stated what the exception is.
_________________________
Webmaster
IAEI Florida Chapter

Top
#6318 - 05/28/09 08:52 AM Re: Rule 9B – 3.047, GFCI Protection [Re: Ruben Rocha]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1600
Loc: City of North Port
The exception is for 1&2 family dwellings.

My issue with the whole deal is:

1. This wasn't even an agenda item.
2. This wasn't open for public review.
3. This wasn't sent to the electric TAC for review.
4. There has been no substaniation provided to necessatate the exception.
5. The exception reduces an already established minimum provision.
_________________________
Bryan P. Holland, MCP

Top
#6319 - 05/28/09 12:17 PM Re: Rule 9B – 3.047, GFCI Protection [Re: Bryan Holland]
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1101
Loc: Ocklawaha FL.
I agree with Bryan 100%
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#6322 - 05/28/09 06:16 PM Re: Rule 9B – 3.047, GFCI Protection [Re: Mike Timpanaro]
Ruben Rocha Offline

Senior Member
*****

Registered: 05/24/00
Posts: 764
Loc: Lutz,FL
Still not clear.
The exception is for 1&2 family dwellings excludes the requirement for gfci completely?
So I guess this means it only applies to public/commercial pools I assume or what about the Mom and Pop swimming classes held at their home. I have at least 6 homes in my immediate area that do so.
_________________________
Webmaster
IAEI Florida Chapter

Top
#6323 - 05/29/09 10:03 AM Re: Rule 9B – 3.047, GFCI Protection [Re: Ruben Rocha]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1600
Loc: City of North Port
Almost Ruben.

The 2008 NEC has expanded the gfci protection to hard-wired pool pumps in addition to cord-and-plug connected pumps which were already required to be gfci protected in the 2005 NEC.

See section 680.22(B) of the 2008 NEC.

The FBC has come along and added an exception for 1&2 family dwellings. The end result:

Cord connected pumps - gfci protection - Residential and Commercial.

Hard wired pumps - gfci protection - Commercial only.

At least that is the way it appears to be heading...
_________________________
Bryan P. Holland, MCP

Top
#6324 - 05/29/09 01:11 PM Re: Rule 9B – 3.047, GFCI Protection [Re: Bryan Holland]
gfretwell
Unregistered


Has there been a big body count from residential hard wired pool pumps or is this just a "why not do it" issue?

I suspect it has to do with money and the builders have lobbied someone although we are only talking about $50-60 (2 pole 20a GFCI breaker).

Top
#6325 - 05/29/09 01:31 PM Re: Rule 9B – 3.047, GFCI Protection [Re: ]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1600
Loc: City of North Port
If you read the data provided by the CPSC used as the substantiation for the rule, there has been many inujuries and deaths here in the US related to contact with pool pump motors.

The problem appears to be the fact that persons working around / maintaining their pool equipment are coming in contact with the pool pump motor and the timer, other enclosures, etc. and hurting / killing themselves. It only requires a small amount of leakage current, ususally caused by corrosion from the pool water chemicals, to be imposed on the motor housing for someone to be severely shocked. This leakage current is well below the threshold to trip a standard circuit breaker and is not mitigated by the equipotential bonding system. A GFCI device would be sufficient in preventing this hazard from occuring.

So yes, it will cost a little more for GFCI breakers, and perhaps the pump motors will have to be replaced more often, but, the NFPA's nationally recognized consensus process deemed it necessary and prudent for all pool installations.

You know me Greg. I am not a huge fan of manufacturer's lobby and other lobbying interests that have force-fed new code down our throats with no substaniation at all, but there can be no arguement or GFCI protection, especially of outdoor, pool related, wet, and corrossive electrical equipment.

_________________________
Bryan P. Holland, MCP

Top
#6326 - 05/29/09 06:13 PM Re: Rule 9B – 3.047, GFCI Protection [Re: Bryan Holland]
gfretwell
Unregistered


Maybe it is time we went for the equipotential ground plane under this equipment like we have for the artificial bodies of water.
I did it on my pool but it was just because it was easy. The 8ga was already there, I just "bugged" it to the wire mesh when I poured the pad the equipment sits on.

Top
#6327 - 05/29/09 07:56 PM Re: Rule 9B – 3.047, GFCI Protection [Re: ]
Ruben Rocha Offline

Senior Member
*****

Registered: 05/24/00
Posts: 764
Loc: Lutz,FL
Well I don't get it Bryan.
If the hazard is there then something had to change.
Even in the last several code cycles. It was required that the 8AWG wire was connected to the pump. And you were required to a have a grounding conductor to the pump.
So maybe after several years the pump was replaced the #8 wire was not reconnected and the chemicals corroded the grounding conductor connection.
So since most jurisdictions don't monitor pool repair/service companies. How can we determine the problem is not the code but enforcement of say the person that cleans the pool then replaces the pump and does not ensure that the bonding conductor is reconnected and that the grounding conductor is intact.

I will agree that the GFCI will help mitigate the problem.
But it will not correct the cause.
_________________________
Webmaster
IAEI Florida Chapter

Top
#6329 - 05/29/09 10:13 PM Re: Rule 9B – 3.047, GFCI Protection [Re: ]
Nick Sasso Online   content

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1438
Loc: West Palm Beach
I have a really weird freakin' idea. How about all of these regulatory and legislative bodies quit screwing with the NEC?
_________________________

Top
#6331 - 05/31/09 03:44 PM Re: Rule 9B – 3.047, GFCI Protection [Re: Nick Sasso]
John Desjardins Offline
Mechanic Member

Registered: 08/07/03
Posts: 306
Loc: Body=NC, Head & Heart=Florida
They aren't going to be able to get away from this.

R4101.7.2 Installation. Pumps shall be installed in accordance with manufacturer recommendations.

Because the NEC is a National Standard pump manufacturers will require GFCI protection to be inline with the NEC. The Commision can change the Code all they want however they CAN NOT require deviation from the Manufactures installation Instruction.
I've run into this many times. Not just Electrical. If the manufacturers Installation Requirements are greater then the Code they must be installed by the MII.
That is why I ALWAYS require all equipment documentation before any inspections. If you don't you can find yourself behind the 8 ball!

Top
#6332 - 05/31/09 04:12 PM Re: Rule 9B – 3.047, GFCI Protection [Re: John Desjardins]
John Desjardins Offline
Mechanic Member

Registered: 08/07/03
Posts: 306
Loc: Body=NC, Head & Heart=Florida
Case in point.
Does a non seperatly derived generator require a ground rod at the generator? NO

The Manufacturers Installation Instructions for Generac Generators require it.
Does it get installed. You Bet!!

Top
#6334 - 06/01/09 08:30 AM Re: Rule 9B – 3.047, GFCI Protection [Re: John Desjardins]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1600
Loc: City of North Port
Good point John!


...Nick always comes up with the most crazy ideas!...
_________________________
Bryan P. Holland, MCP

Top
#6335 - 06/01/09 10:49 AM Re: Rule 9B – 3.047, GFCI Protection [Re: Bryan Holland]
John Desjardins Offline
Mechanic Member

Registered: 08/07/03
Posts: 306
Loc: Body=NC, Head & Heart=Florida
From Hayward:


WARNING – All electrical wiring MUST be in conformance with all applicable local codes, regulations, and the National Electric Code (NEC).

Tells me GFCI will be required.

Top
#6336 - 06/01/09 11:03 AM Re: Rule 9B – 3.047, GFCI Protection [Re: John Desjardins]
John Desjardins Offline
Mechanic Member

Registered: 08/07/03
Posts: 306
Loc: Body=NC, Head & Heart=Florida
From Sta-rite

Wiring
Pump must be permanently connected to circuit. Table I, below, gives correct
wire and circuit breaker sizes for the pump alone. If other lights or appliances
are also on the same circuit, be sure to add their amp loads to pump amp load
before figuring wire and circuit breaker sizes. (If unsure how to do this or if
this is confusing, consult a licensed electrician.) Use the load circuit breaker
as the master on-off switch.
Install a Ground Fault Circuit Interrupter (GFCI) in circuit; it will sense a shortcircuit
to ground and disconnect power before it becomes dangerous to pool
users. For size of GFCI required and test procedures, see GFCI manufacturer’s
instruction.
In case of power outage, check GFCI for tripping (which will prevent normal
pump operation). Reset if necessary.
NOTICE: If you do not use conduit when wiring motor, be sure to seal wire
opening on end of motor to prevent dirt, bugs, etc., from entering.

Top
#6337 - 06/01/09 11:03 AM Re: Rule 9B – 3.047, GFCI Protection [Re: John Desjardins]
John Desjardins Offline
Mechanic Member

Registered: 08/07/03
Posts: 306
Loc: Body=NC, Head & Heart=Florida
Need I say more!You are so right Nick.

Common sense = GFCI
NEC = GFCI
FBC = No GFCI
Manf. Inst. = GFCI

So once again the FBC makes us go round & round to get to were we were in the first place. The problem is not everyone looks at the Manuf. Inst.

Top
#6343 - 06/03/09 10:38 AM Re: Rule 9B – 3.047, GFCI Protection [Re: Nick Sasso]
John Belew Offline
Electrical Inspector/Plans Examiner

Registered: 06/26/01
Posts: 56
Loc: Milton,FL
AMEN!

Originally Posted By: Nick Sasso
I have a really weird freakin' idea. How about all of these regulatory and legislative bodies quit screwing with the NEC?
_________________________
John Belew
Electrical Inspector/Plans Examiner
Santa Rosa Co.
johnb@santarosa.fl.gov

Top
#6358 - 06/11/09 04:57 PM Re: Rule 9B – 3.047, GFCI Protection [Re: John Belew]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1600
Loc: City of North Port
It appears the rule has gone thru thus effective July 1st 2009, the 2008 NEC is adopted with one amendment. Section 680.22(B) will not apply to 1&2 family dwellings.
_________________________
Bryan P. Holland, MCP

Top
#6359 - 06/11/09 05:34 PM Re: Rule 9B – 3.047, GFCI Protection [Re: John Desjardins]
Ruben Rocha Offline

Senior Member
*****

Registered: 05/24/00
Posts: 764
Loc: Lutz,FL
Originally Posted By: John Desjardins
They aren't going to be able to get away from this.

R4101.7.2 Installation. Pumps shall be installed in accordance with manufacturer recommendations.

Because the NEC is a National Standard pump manufacturers will require GFCI protection to be inline with the NEC. The Commision can change the Code all they want however they CAN NOT require deviation from the Manufactures installation Instruction.
I've run into this many times. Not just Electrical. If the manufacturers Installation Requirements are greater then the Code they must be installed by the MII.
That is why I ALWAYS require all equipment documentation before any inspections. If you don't you can find yourself behind the 8 ball!

John, I think you hit the nail on the head with this statement.
Since most jurisdictions require listed equipment, and the installation guideline is part of the listing. How can someone get around the GFCI protection if it is part of the listing, regardless if there is an exception in Florida and it was never added in 2008.
What would you do if we were under the 1996 NEC and the install sheet required gfci protection?
I guess it will become a call from the building official.
_________________________
Webmaster
IAEI Florida Chapter

Top
#6360 - 06/11/09 11:06 PM Re: Rule 9B – 3.047, GFCI Protection [Re: Ruben Rocha]
Nick Sasso Online   content

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1438
Loc: West Palm Beach
Hey guys, the Florida Building Commission makes total sense on this issue, because everyone knows that the electrical for a commercial pool is far more dangerous than the electrical for a residence. WAY TO GO 'FELLAS!

They should keep screwing with the electrical code until there is an accident. Then after the accident, they can go retroactive and abolish the amendment, and adopt the NEC as written. Until then, the prority is to coddle the pool contractors. "Waaaaaaaaahhh. Waaaaaaaaaaahh. We don't wanna do it............."

I'm sure this is the result of some very smart "engineers" on the commission and not the electrical tac. The tac voted to adopt as written. This is probably the result of a civil engineer, or several, or a building official with no electrical experience, applying their superior intelect and knowledge. If an electrical engineer voted for this amendment then I will eat my pouch.

If the manufacturer's instructions require it and it's not there you can be sure I'm writing a RED TAG. If my building official says they don't need it then he can PUT IT IN WRITING. If I ever get the chance to act as an expert in a law suit where there was no GFCI protection, than rest assured I will make mincemeat out of that contractor (your liability insurance rates will triple) and the jurisdiction as well. I should be so lucky.

And no, it's not a call from the building official - to violate 110.3(b) on purpose because the commission is not smart enough to know the difference.

ns


Edited by Nick Sasso (06/11/09 11:11 PM)
_________________________

Top
#6361 - 06/12/09 08:35 AM Re: Rule 9B – 3.047, GFCI Protection [Re: Nick Sasso]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1600
Loc: City of North Port
NICK SASSO FOR PRESIDENT !!!!


The good news is that pool owners can no longer get their hair, fingers, and bodies stuck on and in water inlet covers. Flows and suction has been reduced to help prevent drowning. Baby barriers / alarms must be installed and the pool must be empty at final electrical inspections to protect the homeowner..... BUT.....

We are going to allow them to be electrocuted when as little as 6mA of leakage current flows on the frame of the pool pump.

What's wrong with this picture???



Edited by Bryan Holland (06/12/09 09:22 AM)
_________________________
Bryan P. Holland, MCP

Top
#6362 - 06/12/09 09:35 AM Re: Rule 9B – 3.047, GFCI Protection [Re: Bryan Holland]
John Desjardins Offline
Mechanic Member

Registered: 08/07/03
Posts: 306
Loc: Body=NC, Head & Heart=Florida
Bryan,
Do you not agree with what I said about the manufactures Installation Instructions?

Top
#6365 - 06/12/09 01:51 PM Re: Rule 9B – 3.047, GFCI Protection [Re: John Desjardins]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1600
Loc: City of North Port
Yes John. I completely agree with your postings.
_________________________
Bryan P. Holland, MCP

Top
#6378 - 06/15/09 02:52 AM Re: Rule 9B – 3.047, GFCI Protection [Re: Bryan Holland]
gfretwell
Unregistered


"Pool has to be empty on the final electrical" ???

How do you do that? They will pop out of the ground if they don't have water in them around here.
It is either going to be brown water or blue water.
You also need to fill the pool immediately after plastering it to keep the plaster from cracking and you can't install the underwater lights, ladders, rails etc until it is plastered.

Something sounds wrong with that sequence.

The "final electric" is the pool final here, or at least it was in 2004 when I did mine. The electrical inspector does it all. They wanted the pool blue before they came out.

Top
#6379 - 06/15/09 07:58 AM Re: Rule 9B – 3.047, GFCI Protection [Re: ]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1600
Loc: City of North Port
Here is one commentary on the issue I was able to find online:

Quote:
FBC adopts 2008 NEC, exempting GFCI requirement on residential pools

FSPA President Alan Cooper, "This epitomizes what our government relations program is all about. Further, it is an excellent example of the importance of having a swimming pool contractor on the FBC."

On Tuesday the Florida Building Commission (FBC) held a final rule hearing on glitch rule 9B-3.047, which encompassed a number of proposed changes to the 2007 Florida Building Code (the code). Most important to the pool industry was the 2008 NEC discussion.

In April the FBC voted to adopt the 2008 NEC, but exempt the GFCI requirement on residential pools. However, the National Electrical Manufacturers Association (NEMA) and others received word of this action and were in attendance on Tuesday. Testimony from a NEMA representative and an electrical contractor asked the FBC to reverse their original decision and adopt the 2008 NEC in total. Representatives from FSPA and other groups provided testimony to rebut the NEMA claims and encourage the FBC to stand by their original decision.

Larry Brown, FSPA Central Florida member and electrical contractor for Mid Florida Pools, did a superb job rebutting the NEMA testimony. In addition, comments were made to the FBC by UPSA members. To sum up the discussion, Commissioner Ken Gregory spoke to his fellow Commissioners asking them to vote down a motion to adopt the 2008 NEC in its entirety. The FBC agreed with him and the testimony the pool industry provided, ultimately voting down the motion 16-6. The original decision to adopt the 2008 NEC except for the GFCI requirement on residential pools withstood.

Also note that the FBC voted to incorporate into the glitch rule the 64E-9, F.A.C., public pool code revisions.

Read this story in its entirety in the July issue of Florida Pool Pro (sm).


_________________________
Bryan P. Holland, MCP

Top
Page 1 of 3 1 2 3 >



Active Topics
Moving site.
by Ruben Rocha
Yesterday at 06:43 PM
2010 FBC - Significant Changes (North Port List)
by Bryan Holland
02/01/12 01:22 PM
February Meeting Announcement
by Bryan Holland
02/01/12 01:21 PM
January Meeting Minutes
by Bryan Holland
02/01/12 01:20 PM
LISTING FOR SAUNA
by Nick Sasso
01/30/12 10:33 AM
February
M Tu W Th F Sa Su
1 2 3 4 5
6 7 8 9 10 11 12
13 14 15 16 17 18 19
20 21 22 23 24 25 26
27 28 29
Featured Member
Registered: 05/10/03
Posts: 0
Forum Stats
506 Members
29 Forums
1861 Topics
8492 Posts

Max Online: 32 @ 12/14/11 08:55 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image

Upcoming events