#6612 - 09/21/09 03:10 PM Maximum number of disconnects
gfretwell
Unregistered


2008 eliminated "lighting and appliance" panelboard classification so the "2 disconnect" rule is gone with it. Does that mean you can install a 6 breaker sub panel in a detached building that complies with 225.33 (assuming the load side breaker in the main panel adequately protects the remote panel per 408.36)

Top
#6613 - 09/21/09 03:31 PM Re: Maximum number of disconnects [Re: ]
John Belew Offline
Electrical Inspector/Plans Examiner

Registered: 06/26/01
Posts: 56
Loc: Milton,FL
If 6 breakers were all that could be installed in that panel then 225.33 would allow it.
_________________________
John Belew
Electrical Inspector/Plans Examiner
Santa Rosa Co.
johnb@santarosa.fl.gov

Top
#6615 - 09/21/09 07:45 PM Re: Maximum number of disconnects [Re: John Belew]
Ruben Rocha Offline
Senior Member
*****

Registered: 05/24/00
Posts: 767
I guess I need to break down and buy a 2008 NFPA 70.
I can't keep up with this type of stuff. grin

Top
#6616 - 09/21/09 08:14 PM Re: Maximum number of disconnects [Re: Ruben Rocha]
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
Yes.

The size and spaces of the panelboard has nothing to do with using the 6 handle rule.

408.36 exception would not apply to your installation.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#6619 - 09/22/09 09:31 AM Re: Maximum number of disconnects [Re: Mike Timpanaro]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
You still need to take into consideration the markings and label on the panelboard itself. Until the panelboard labels are updated to include the new allowances in the 2008 NEC, the old rules will still apply.

_________________________
Bryan P. Holland, MCP

Top
#6627 - 09/26/09 03:33 PM Re: Maximum number of disconnects [Re: Bryan Holland]
COTInspector Offline
Mechanic Member
*****

Registered: 02/14/08
Posts: 132
Loc: Tampa, Florida
I agree with Bryan, I have asked several manufactures to provide me a listing for the new larger panels and none have been able to show a properly listed panel.

Neal Burdick
City of Tampa
Construction Inspector

Top
#6628 - 09/26/09 08:21 PM Re: Maximum number of disconnects [Re: COTInspector]
gfretwell
Unregistered


Sounds like a good question for Jim Pauley the next time someone sees him.

Top
#6630 - 09/28/09 02:11 PM Re: Maximum number of disconnects [Re: ]
Ron Wampler Offline
Apprentice Member

Registered: 08/20/08
Posts: 43
Loc: Florida Keys
What a great question! I like this revision. Who doesn't remember the hazards associated with overloaded 'split-bus panels'?? Remember the ITE 'Bulldog' panelboards with 2 mains?? Detached bldgs. under 225.33 and 225.36 allows the 'six disc.' rule for S.U.S.E. pnlbds. and has allowed this for some time. OCP is permitted to be at the main building per 408.36 Exception No. 1. Please recall that these rules coincide with the original 'tap rules' back in 240.21...

Top
#6631 - 09/28/09 06:04 PM Re: Maximum number of disconnects [Re: Ron Wampler]
Ruben Rocha Offline
Senior Member
*****

Registered: 05/24/00
Posts: 767
Okay I will bite!!
What is S.U.S.E?

Top
#6632 - 09/28/09 06:18 PM Re: Maximum number of disconnects [Re: Ruben Rocha]
Ron Wampler Offline
Apprentice Member

Registered: 08/20/08
Posts: 43
Loc: Florida Keys
Old school...S.U.S.E....Suitable for Use as Service Equipment...A requirement that was inadvertantly dropped from Article 230 back in maybe '87 and then revised back in...Any UL listed piece of equipment even Transfer Switches and Contol Cabinets that are used as service equipment must bear this term on their label. Excuse me...'listing agencies'. Even primary service switchgear.

Top
Page 1 of 2 1 2 >



Active Topics
May Meeting Minutes
by Bryan Holland
05/17/12 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
123
123
Registered: 08/08/11
Posts: 0
Forum Stats
519 Members
29 Forums
1892 Topics