#6621 - 09/24/09 05:31 PM feeders
Rob Barbee Offline
Mechanic Member
***

Registered: 06/24/08
Posts: 120
Loc: Pinellas County
Hows about an opinion or two.

120/240 volt 1 phase feeder pulled from gang meter to townhouse.......one 2/0 ungrounded and one 3/0 ungrounded conductor along with the neutral and ground.
Should there be concern for the difference in size and is this a violation.
Not sure which way to take it but something does not seem right. Maybe the same logic stated that parallel conductors shall be the same size?
_________________________
Rob
Electrical Inspector

Top
#6622 - 09/24/09 05:46 PM Re: feeders [Re: Rob Barbee]
Ruben Rocha Offline

Senior Member
*****

Registered: 05/24/00
Posts: 763
Loc: Lutz,FL
That is a odd one.
First thing I would consider is if the 2/0 is ample size for the load and over current protection.
I really don't know why some one would do this except for they needed 2/0 and ran out so ran the other leg with 3/0.

What does the contractor say?
If you start down the road of voltage drop or adjustment correction factors then it does not hold water. Then you also need to consider the neutral and ground size.
_________________________
Webmaster
IAEI Florida Chapter

Top
#6623 - 09/25/09 01:05 AM Re: feeders [Re: Ruben Rocha]
inspector32513 Offline
Lynn Adams

Registered: 10/06/05
Posts: 46
Loc: Pensacola, FL
IF IF IF the 2/0 is big enough. AND AND AND the neutral and ground are big enough (see the calculations and tables and charts) THEN having one wire be bigger is just a plus.

Today- it probably means that they had some 3/0 in the scrap bin and did not want to buy more 2/0. Bigger is better. Bigger is allowed. The "unbalance" does not really exist. What if they used both ungrounded conductors as 3/0? or 4/0? or 500 KCMC? jUST BIGGER.
\

BUT!
_________________________
Lynn Adams
Chief Electrical Inspector, Escambia County
IAEI_Panhandle Division

Top
#6624 - 09/25/09 01:06 AM Re: feeders [Re: inspector32513]
inspector32513 Offline
Lynn Adams

Registered: 10/06/05
Posts: 46
Loc: Pensacola, FL
BUTT!

(still have not mastered the "TAB" key and entry key)

I still bet the bigger wire was on hand and used to save money. I would have!
_________________________
Lynn Adams
Chief Electrical Inspector, Escambia County
IAEI_Panhandle Division

Top
#6625 - 09/25/09 11:34 AM Re: feeders [Re: inspector32513]
Ron Wampler Offline
Apprentice Member

Registered: 08/20/08
Posts: 43
Loc: Florida Keys
I agree with 32513. Assuming the mains or calculated load does not exceed the 2/0. The same would apply to replacing only one RHW leg with THWN as a cheap repair...This is not the same principle as parallel sets but similar in that each set must be identical but not with another leg of the same run...NEC 310.4(B)

Top



Active Topics
Moving site.
by Ruben Rocha
Yesterday at 06:43 PM
2010 FBC - Significant Changes (North Port List)
by Bryan Holland
02/01/12 01:22 PM
February Meeting Announcement
by Bryan Holland
02/01/12 01:21 PM
January Meeting Minutes
by Bryan Holland
02/01/12 01:20 PM
LISTING FOR SAUNA
by Nick Sasso
01/30/12 10:33 AM
February
M Tu W Th F Sa Su
1 2 3 4 5
6 7 8 9 10 11 12
13 14 15 16 17 18 19
20 21 22 23 24 25 26
27 28 29
Featured Member
Registered: 05/03/02
Posts: 0
Forum Stats
506 Members
29 Forums
1861 Topics
8490 Posts

Max Online: 32 @ 12/14/11 08:55 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image

Upcoming events