Section: 210.12(B)
Question:
Is it the intent of NEC Article 210.12(B) to require all outlets in a laundry room to be provided with Arc-Fault protected circuits?
Comment:
None.
Answer:
No. NEC Article 210.12(B) requires arc-fault protection in "...family rooms, dining rooms, living rooms, parlors, libraries, dens,
bedrooms, sunrooms, recreation rooms, closets, hallways, or similar rooms or areas." A laundry room is not similar to these
rooms.
Commentary:
The NEC commentary specifically excludes, "...kitchens, bathrooms, unfinished basements, garages and outdoors..." from the
requirement. These rooms are more similar to laundry rooms than those specifically listed in NEC Article 210.12(B).