#689 - 09/09/03 09:51 AM
Re: 680.24 j box & Encloser for Trans or GFCI
|
Post-A-Holic Member
  
Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
|
What is the question? Are we talking about Swimming pool junction boxes? Or other enclosures for transformers or GFCI receptacles? Trying to combine the two subjects is like trying to compare apples to oranges. They are both fruit, but different types.
The fixture type in this case is not important. What it important is the type junction box or enclosure used when connected to a conduit that connects directly to a forming shell, or mounting bracket of a no-niche fixture.
That statement applies to 680.24(a)&(B) main paragraph. This forming shell is the niche of a wet-niche or dry-niche fixture, and also applies to the mounting bracket of a no-niche fixture.
But lets talk about the fixtures for a moment. Dry-niche fixture: The reason why the approved seal is NOT required per 680.24(b)(3) is that the forming shell is a dry-niche. In other words, no water can enter the forming shell or the conduit that extends to the enclosure. That is why more than likely the conduit from the dry-niche fixture will run directly to the breaker panel, with no junction box or enclosure between the fixture and panel. IT'S DRY-NICHE That is also why the fixture can't be opened underwater for relamping. You have to tunnel behind the pool wall or floor to open the forming shell from the back to repair or relamp the fixture.
Wet-niche fixture: Yep you guessed it the forming shell fills with water so the conduit that extends from the junction box, or enclosure will circulate air-causing water to siphon.
No-niche Fixture: This type of fixture has no niche. The fixture is surface mount. The mounting bracket is installed on the pool wall and the fixture is connected to the mounting bracket. But it is still a wet fixture, so water can still siphon through the conduit that extends from the junction box, or enclosure.
As I said the fixture type is not important, what is important is the circulation of air that can cause water to siphon. We don't need to worry about this with a swimming pool junction box, (there is nothing in the box) which is why 680.24(a) doesn't require the approved seal. But with 680.24(b)(3) we do need to provide the approved seal in the enclosure of a transformer, or the enclosure of the Intermatic time clock / transformer / breaker panel, or the enclosure of the GFCI receptacle used to protect a 120 volt fixture. ( We would not want water to siphon back into an enclosure with some type of electrical equipment/devices installed ).
With a short note; The approved seal only is required with enclosures that meet the requirements of 680.24(b) and not when installing the swimming pool junction box that meets 680.24(a).
Don't forget that any enclosure directly connected to a conduit that extends to a forming shell, or mounting bracket of a no-niche fixture must be listed for direct connection by an approved testing laboratory.
Hope this helps, sorry for running on. Mike
_________________________
Michael J Timpanaro Inspector/Plans Examiner/CEU Instructor Florida
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#698 - 09/10/03 02:14 PM
Re: 680.24 j box & Encloser for Trans or GFCI
|
Post-A-Holic Member
  
Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
|
Thanks Mike. I too, like debating the issues. I haven't been here lately - kinda busy - due to a personal issue that will hopefully be resolved by the end of this week.
I wish that more people would post, but I think they don't because the forum exposes what one doesn't know. Me, I don't care if I'm wrong because that is how you learn, by asking questions. Most of the time I am shooting from the hip, but your responses and others' responses force me to dig into the issues further and further. Keeps me on my toes. I am waiting for some technical specs on pool light jboxes at this moment because of this conversation. Thanks to all the BRAVE people who use this forum!
I will concede and agree with you that the seal can't be required from 680, but I would like to think that one has the option to require it due to chemical action that could result, using the articles I previously mentioned. I was just trying to help rasmith out of a jam. I agree that the box is corrosion resistant, but the connections?? Also, there is condensation, especially if the pool is heated, that would expose the connections to the chemicals.
300.7 touches on this, even though the intent I believe is for something else. At any rate, I'm still not finished and will look into this further. !!
_________________________
|
|