It is a problem. Where they do not bury it to minimum depth, the conductor is subject to damage, and also when the landscaper knocks into it, it pulls and creates tension on the clamp. How many loose ground clamps have we all seen? Like a gazillion?
Mike I do not agree with your premise that "since proposals were rejected" the code therefore does not require it. The proposals just like the law, can be rejected (or not adopted) for a million other reasons, like lousy wording. They only need to add the last sentence like I just wrote yesterday. In fact if someone would like to copy and paste my wording and submit it, go ahead. The reasoning is that the ground ring, which is an electrode (but yet still a conductor) must be buried 30 inches.
So what gives? There is obviously confusion in the code at this point, and that needs clarification. But that does not mean the GE conductor does not need to be buried to the minimal depth. Table 300.5 is all inclusive. It is not just for some conductors. It applies to all conductors.