#6930 - 03/19/10 09:41 PM
Re: GEC
[Re: Ruben Rocha]
|
Post-A-Holic Member
  
Registered: 11/08/01
Posts: 1438
Loc: West Palm Beach
|
But Ruben, the intent of the code is always to protect the grounding electrode conductor. Not one person has convinced me otherwise thus far. That is the intent of the code - that the GEC remain protected from physical damage. So much so, that in some instances the code mandates that it be run inside pipe or conduit:
Securing and Protection Against Physical Damage. Where exposed, a grounding electrode conductor or its enclosure shall be securely fastened to the surface on which it is carried. A 4 AWG or larger copper or aluminum grounding electrode conductor shall be protected where exposed to physical damage. A 6 AWG grounding electrode conductor that is free from exposure to physical damage shall be permitted to be run along the surface of the building construction without metal covering or protection where it is securely fastened to the construction; otherwise, it shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metallic tubing, or cable armor. Grounding electrode conductors smaller than 6 AWG shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metallic tubing, or cable armor.
Sidebar comments:
Column 4 is only applicable to a 20 amp circuit, GFCI.
The table is the minimum burial depth for conductors.
The purpose of ground ring at 30 inches is not solely for grounding it is also for protection of the conductor.
_________________________
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
|
 |
 |
 |
 |
|
|
|
1
|
2
|
3
|
4
|
5
|
|
6
|
7
|
8
|
9
|
10
|
11
|
12
|
|
13
|
14
|
15
|
16
|
17
|
18
|
19
|
|
20
|
21
|
22
|
23
|
24
|
25
|
26
|
|
27
|
28
|
29
|
|
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
Registered: 06/26/08
Posts: 0
|
|
|
 |
 |
 |
 |
|