A good time was had by all at the grounding seminar on Saturday. I want to thank Dick Widera, who while still suffering from food poisoning still got everything going and did an excellent job. I approached John Minnick before the course started with the question relating to using Table 300.5 with the related table to enforce the protection of the GEC. John's answer was that nothing in 250.64 references that but he see's nothing that would stop you either. The main point was that 250.64 (B) states A 4 AWG or larger copper or aluminum grounding electrode conductor shall be protected where exposed to physical damage.So this leaves the method up to the AHJ. He saw nothing wrong with using 300.5 but would not use the 24 inch depth. He went on to say this discussion has never come in code panel 5 all the years he has been there, but it is a worthy for future consideration. Paul, did I forget anything?