MENU
Florida Chapter Officers
BOD Chairman
Nelson Montgomery
President
Dan Prater
1st Vice President
Ted Licitra
2nd Vice President
Mark Deegan
3rd Vice President
Richard Wheelus
Chaplain
Vince Dellacroce
Secretary
Joe DuPriest
Treasurer
Eric L Wasser
Parliamentarian
Tim Wright
Who's Online
0 registered (), 5 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Newest Members
ampherder, TonyLutziFlaRep, Jeff Sargent, Kerry Leuzinger, myv5pb
505 Registered Users
Top Posters (30 Days)
Bryan Holland 14
Ruben Rocha 3
Paul J Cameron 3
Nick Sasso 3
inspector32513 3
ronwampler 2
Joe L. DuPriest 1
DickWidera 1
SOwings 1
Google Search
Today's Birthdays
No Birthdays
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#6986 - 03/28/10 11:34 PM Article 600.5a
Joe Flynn Offline
New Member

Registered: 01/11/10
Posts: 1
I have a commercial building, open to the public. It has no over hang for signs but the customer wants to put two large signs on the side of the building and feed these signs from a wall pack circuit. Their electrical engineer tells me 600.5a only applies to outlets at entrances to a commercial space. My interpretation of the code and experience tells me a dedicated circuit is required. Is there another section of the NEC which permits these signs from sharing a wall pack circuit?

Top
#6994 - 03/30/10 02:47 PM Re: Article 600.5a [Re: Joe Flynn]
Ron Wampler Offline
Apprentice Member

Registered: 08/20/08
Posts: 43
Loc: Florida Keys
Good question. NEC Sect. 90.3 Code Arrangement says that Chapter 6 supplements or modifies Chapters 1 thru 4. Section 600.5 requires sign branch circuits that supply no other load; only sign outlets...I don't think that you need any additional code...

Top
#6999 - 03/30/10 05:55 PM Re: Article 600.5a [Re: Ron Wampler]
Rob Barbee Offline
Mechanic Member
***

Registered: 06/24/08
Posts: 120
Loc: Pinellas County
Or we could look at this differently - if the requirements are met for 600.5 and additional signs to be added, who cares which circuit they are fed from, as long as that circuit is sized to handle load on it. 600.5 says the one required sign circuit may feed no additional loads, it does not specify if other circuits may include signage. IMHO of course! smile
_________________________
Rob
Electrical Inspector

Top
#7000 - 03/30/10 06:43 PM Re: Article 600.5a [Re: Rob Barbee]
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1438
Loc: West Palm Beach
Joe, can you define what you are calling a "wall pack" ?
_________________________

Top
#7003 - 03/31/10 12:06 AM Re: Article 600.5a [Re: Nick Sasso]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1598
Loc: City of North Port
I imagine Joe is refering to one of these:




I really don't see a code violation having a sign or signs supplied from a circuit serving other loads as long as the REQUIRED sign circuit and outlet is provided elsewhere.

_________________________
Bryan P. Holland, MCP

Top
#7008 - 03/31/10 12:53 AM Re: Article 600.5a [Re: Bryan Holland]
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1438
Loc: West Palm Beach
I don't know, sometimes people refer to interior lighting as a "wall pack" even emergency lighting.

_________________________

Top
#7011 - 03/31/10 02:32 PM Re: Article 600.5a [Re: Nick Sasso]
Joe L. DuPriest Offline
Apprentice Member

Registered: 07/25/08
Posts: 31
Loc: Orlando Fl.
Outlet. A point on the wiring system at which current is taken to supply utilization equipment.
600.5 Branch Circuits.
(A) Required Branch Circuit. Each commercial building and each commercial occupancy accessible to pedestrians shall be provided with at least one outlet in an accessible location at each entrance to each tenant space for sign or outline lighting system use. The outlet(s) shall be supplied by a branch circuit rated at least 20 amperes that supplies no other load. Service hallways or corridors shall not be considered accessible to pedestrians.

Refering to the definition of outlet and 600.5(A), I would not allow the connection of the signs to the circuit feeding lighting. 600.5(A) talks about "at least one outlet" and "The outlet(s)...that supply no other load", that to me means if additional signs are installed then they are to be connected to the existing sign circuit or additional sign circuits are to be installed. General lighting circuits would be an "other load".

Top
#7012 - 03/31/10 03:54 PM Re: Article 600.5a [Re: Joe L. DuPriest]
psnorthrup Offline
Mechanic Member

Registered: 04/23/07
Posts: 115
Loc: Plant City
What I see here is an additional signs being installed on the side of the building, 600.5 requires an outlet at each entrance to the building or tennent space, if that outlet is there, then the one on the side doesn't fall under 600.5 and is supplemental and can be fed from elsewhere as long as the total load does not exceed the limits of the overcurrent device


Edited by psnorthrup (03/31/10 04:09 PM)

Top
#7013 - 03/31/10 04:35 PM Re: Article 600.5a [Re: psnorthrup]
John Belew Offline
Electrical Inspector/Plans Examiner

Registered: 06/26/01
Posts: 56
Loc: Milton,FL
The outlets are required to be there even if the sign is not. Branch circuit for sign, no other load. 600.5 Handbook has some good reading. IEAI weekley update. http://www.iaei.org/magazine/?p=4827
_________________________
John Belew
Electrical Inspector/Plans Examiner
Santa Rosa Co.
johnb@santarosa.fl.gov

Top
#7020 - 03/31/10 07:01 PM Re: Article 600.5a [Re: Joe L. DuPriest]
Ron Wampler Offline
Apprentice Member

Registered: 08/20/08
Posts: 43
Loc: Florida Keys
I agree. All sign outlets to be supplied by sign br. ckts. We all know that sign types and loads vary dependent on type and size and changing out of old signs or teneants...

Top
Page 1 of 2 1 2 >



Active Topics
2010 FBC - Significant Changes (North Port List)
by Bryan Holland
02/01/12 02:22 PM
February Meeting Announcement
by Bryan Holland
02/01/12 02:21 PM
January Meeting Minutes
by Bryan Holland
02/01/12 02:20 PM
LISTING FOR SAUNA
by Nick Sasso
01/30/12 11:33 AM
2010 FBC Code Change Questions
by Bryan Holland
01/27/12 12:39 PM
February
M Tu W Th F Sa Su
1 2 3 4 5
6 7 8 9 10 11 12
13 14 15 16 17 18 19
20 21 22 23 24 25 26
27 28 29
Featured Member
Registered: 06/26/08
Posts: 0
Forum Stats
505 Members
29 Forums
1860 Topics
8488 Posts

Max Online: 32 @ 12/14/11 09:55 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image

Upcoming events