#7037 - 04/02/10 12:55 PM
338.10 (B) (4)
|
Mechanic Member
   
Registered: 02/14/08
Posts: 132
Loc: Tampa, Florida
|
With the change to section 338.10 (B) (4) in the 2008 NEC, 1) Is a 4/0 Aluminum SER sill allowed to serve an interior MLO panel installed in a one or two family dwelling that is protected by an exterior 200 amp main breaker. 2) Are two 4/0 Aluminum SER’s allowed to server two MOL interior panels that are protected by two 200 amp main breakers. (400 amp service) 3) Are two 2/0 Aluminum SER’s allowed to server two MOL interior panels that are protected by two 150 amp main breakers. (300 amp service)
I feel #1 would still be permitted due to the following, 1)From NEC 2008 ROP 7-88 Log #2639 NEC-P07 (338.10(B)(4)(a)Substantiation: When Type SE conductors are used for interior wiring, as a replacement for Type NM cable, the ampacity of the conductors should be the same as permitted for NM cable since the insulations used are the same both NM and SE conductors. This SER cable is not being installed as a replacement for type NM cable in this application.
2) 310.15 (B) (6) would still apply being the more specific requirement for this installation. “For individual dwelling units of one-family, two-family, and multifamily dwellings, conductors, as listed in Table 310.15(B)(6), shall be permitted as 120/240-volt, 3-wire, single-phase service-entrance conductors, service-lateral conductors, and feeder conductors that serve as the main power feeder to each dwelling unit and are installed in raceway or cable with or without an equipment grounding conductor. For application of this section, the main power feeder shall be the feeder between the main disconnect and the panelboard that supplies, either by branch circuits or by feeders, or both, all loads that are part or associated with the dwelling unit.” SER cable installed under this provision would be the “main power feeder”, not an interior feeder or branch circuit that 338.10(B)(4) is referring to.
I am not sure about #2 and #3 but I feel this installation is not allowed due to the following, 1) Each SER cable is not carrying the entire load associated with the dwelling unit. From the 2008 NEC Handbook “Section 310.15(B) (6) permits the main feeder to a dwelling unit to be sized according to the conductor sizes in Table 310.15(B) (6). For the 2008 Code, the panel clarified that this permission to use this table applies only to conductors carrying 100 percent of the dwelling unit's diversified load.” So since each SER is only carrying around 50% of the dwellings load, 310.15 (B) (6) and the Table 310.15 (B) (6) would not be allowed to be used to size each SER cable. I’m curious how other inspectors are looking at these changes.
Neal Burdick City of Tampa Construction Inspector
|
|