#7032 - 04/01/10 05:24 PM Legally required standby systems
thomas Offline
Apprentice Member

Registered: 04/21/06
Posts: 7
Loc: florida
I am looking for information on a legally required standby system for a fire pump other than art. 701, can anyone help?

Top
#7033 - 04/01/10 09:59 PM Re: Legally required standby systems [Re: thomas]
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Sure, what information are you looking for?
_________________________

Top
#7034 - 04/02/10 01:37 AM Re: Legally required standby systems [Re: Nick Sasso]
thomas Offline
Apprentice Member

Registered: 04/21/06
Posts: 7
Loc: florida
Riser diagram with disconnect locations.

Top
#7035 - 04/02/10 10:27 AM Re: Legally required standby systems [Re: thomas]
Joe L. DuPriest Offline
Apprentice Member
*****

Registered: 07/25/08
Posts: 33
Loc: Orlando Fl.
Have you read through Article 695, and specifialy 695.3 and 695.12?

Top
#7042 - 04/03/10 11:41 PM Re: Legally required standby systems [Re: Joe L. DuPriest]
Dewey Palmer Offline
New Member

Registered: 03/22/10
Posts: 1
Loc: WPB, Florida
NFPA-20 also contains a lot of electrical information for Fire Pumps.
As mentioned above 695 of the NEC will help.

The adopted versions of the NFPA-70 and 20 will depend on the permit application date.

Top
#7043 - 04/04/10 11:51 AM Re: Legally required standby systems [Re: Dewey Palmer]
Bryan Holland Online   shocked

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
I believe both Mike Holt and Tom Henry publish a book on the subject of Fire Pumps. Perform a Google search.

_________________________
Bryan P. Holland, MCP

Top
#7053 - 04/05/10 09:22 AM Re: Legally required standby systems [Re: Bryan Holland]
thomas Offline
Apprentice Member

Registered: 04/21/06
Posts: 7
Loc: florida
Thank you for code articles.

Top
#7054 - 04/05/10 09:56 AM Re: Legally required standby systems [Re: thomas]
psnorthrup Offline
Mechanic Member

Registered: 04/23/07
Posts: 115
Loc: Plant City
also look at NFPA 110, Standard for Emergency and Standby Power Systems

Top
#7057 - 04/05/10 02:29 PM Re: Legally required standby systems [Re: psnorthrup]
Ron Wampler Offline
Apprentice Member

Registered: 08/20/08
Posts: 43
Loc: Florida Keys
Keep in mind that the F.P. service can not be routed thru the building service equipment. It may come off the same outdoor utility xfmr but is routed underground or encased in concrete if routed inside. The F.P. disconnect should be part of a listed S.U.S.E. fire pump controller and the conductors are sized at least 125% of the motor FLA but there is no overload protection just fault protection at about 600% FLA from my recollection. Please study the NFPA stds. mentioned by others for specific details...I am just giving a general overview...and common G.E.C. with building system of course.

Top
#7058 - 04/05/10 02:34 PM Re: Legally required standby systems [Re: Ron Wampler]
Ron Wampler Offline
Apprentice Member

Registered: 08/20/08
Posts: 43
Loc: Florida Keys
Oops...Legally required standby system...I think that there is such a thing as a listed S.U.S.E. F.P. contoller-transfer switch. I recall one a few years ago...

Top



Active Topics
May Meeting Minutes
by Bryan Holland
05/17/12 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
Registered: 03/14/11
Posts: 0
Forum Stats
519 Members
29 Forums
1892 Topics
8569 Posts

Max Online: 53 @ 03/30/12 04:16 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image