If there is attic space and or crawl space, then smoke detectors must be installed as a new dwelling would require.
We have been accepting stand alone battery smoke detector in the remote areas if access is not available for interconnection.
I would like to see the building code require "wireless" smoke detectors to the unaccessible areas of the dwellind.
At least the detectors would all signal an alarm together.
"R313.2.1 Alterations, repairs and additions. When alterations, repairs or additions requiring a permit occur, or when one or more sleeping rooms are added or created in existing dwellings, the individual dwelling unit shall be equipped with smoke alarms located as required for new dwellings; the smoke alarms shall be interconnected and hard wired.
Exceptions:
1. Interconnection and hard-wiring of smoke alarms in existing areas shall not be required where the alterations or repairs do not result in the removal of interior wall or ceiling finishes exposing the structure, unless there is an attic, crawl space or basement available which could provide access for hard wiring and interconnection without the removal of interior finishes.
2. Work involving the exterior surfaces of dwellings, such as the replacement of roofing or siding, or the addition or replacement of windows or doors, or the addition of a porch or deck, are exempt from the requirements of this section."
I don't beleive there were any changes to this requirement in all the rewrites of the 2007 FBC
IMHO
Neal Burdick
City of Tampa
Construction Inspector