#7244 - 05/13/10 06:27 PM 310.15.(B)(2)(c)
gfretwell
Unregistered


This showed up on the ECN BB (George Little Inspector in Michigan) and I thought it might be interesting to discuss here.

"How is Article 310.15.(B)(2)(c) applied in your area?"

My question
Is there a particular guideline you use or do you just accept the EC/Engineer's calculation?

Top
#7245 - 05/14/10 07:51 AM Re: 310.15.(B)(2)(c) [Re: ]
Bryan Holland Online   shocked

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
I am using the guidelines established by the CDA. As indicated in the FPN, the CDA guidelines utilize the average of the 2% ASHRAE design temperatures for each region and major city in the state.

The guildelines and sliding scale card can be obtained FREE from www.copper.org
_________________________
Bryan P. Holland, MCP

Top
#7246 - 05/14/10 01:09 PM Re: 310.15.(B)(2)(c) [Re: Bryan Holland]
gfretwell
Unregistered


Thanks That is exactly what George was looking for. I will pass it on.

Top
#7247 - 05/14/10 05:29 PM Re: 310.15.(B)(2)(c) [Re: ]
COTInspector Offline
Mechanic Member
*****

Registered: 02/14/08
Posts: 132
Loc: Tampa, Florida
Bryan,
Could you narrow the link down a little, I cant locate the temps on the web page.
I have been using 34 C for the Tampa area, I got that # from a PV publication, am I close?

Neal Burdick
COT Construction Inspector II

Top
#7248 - 05/14/10 05:50 PM Re: 310.15.(B)(2)(c) [Re: COTInspector]
Ruben Rocha Offline
Senior Member
*****

Registered: 05/24/00
Posts: 767
Yea I had to hunt a little and HERE is a page.

Top
#7249 - 05/14/10 05:59 PM Re: 310.15.(B)(2)(c) [Re: ]
ronwampler Offline
Apprentice Member

Registered: 05/30/07
Posts: 47
Loc: Marathon, Florida
Assuming ambient temperature is surrounding air temperature. Rooftop air at 113*F. = 45*C. Add 22*C. for rooftops with sunlight...you get 67*C. which is an correction factor of 0.58 so #12 THWN-2 @ 90*C. is rated 30amps. x 0.58 = 17.4amps...could still be on a 20amp ckt. bkr...only 3 current carrying conductors plus maybe a balanced neutral and E.G...I still think that linear expansion and contraction is a bigger issue on long rooftop runs...

Top
#7250 - 05/14/10 07:58 PM Re: 310.15.(B)(2)(c) [Re: ronwampler]
Ruben Rocha Offline
Senior Member
*****

Registered: 05/24/00
Posts: 767
Quote:
I still think that linear expansion and contraction is a bigger issue on long rooftop runs...

You bet.
I have seen even supposedly properly placed expansion fittings come apart due to excessively long runs.
Which leaves exposed conductors that are subject to uv deterioration.

Top
#7251 - 05/14/10 10:19 PM Re: 310.15.(B)(2)(c) [Re: Ruben Rocha]
Bryan Holland Online   shocked

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Expansion Fittings for Rigid NonMetallic Conduit

Rigid NonMetallic Conduit, commonly referred to as PVC, will expand and contract over its length as the ambient temperature around the installation fluctuates. RNC has thermal expansion characteristics three times that of aluminum and six times higher than steel.

The requirement for expansion fittings can be found in Section 352.44 of the National Electrical Code. It’s accompanying Table identifies the change in conduit length based on the maximum temperature change expected during the life of the installation. If this change in length exceeds ¼ in or greater, an expansion fitting is required.

A good rule of thumb is that any straight conduit run exceeding 25 feet and where the temperature change exceeds 25°F, an expansion fitting is probably needed. The temperature change is based on the maximum and minimum temperature expected to occur. Another consideration is exposure to direct sunlight. Most fittings have directions indicating an increase of 30°F to be added to the maximum temperature for proper installation.

For example, assume a 50' run of RNC in direct sunlight with a maximum expected temperature of 95°F and minimum likely temperature of 25°F:

95°F + 30°F – 25F° = 100°F temperature change. Per Table 352.44(A), this would produce a change in conduit length of 4.06 in / 2 = 2.03 in. (The Table is based on in./100ft.)

The best installation practice is to install the expansion fitting in a horizontal position. If the fitting must be installed in a vertical position, proper arrangement must be assured to prevent the entrance of rain water. Care must also be taken to ensure the initial position of the piston within the barrel takes in account the current temperature conditions to allow the full range of expansion and contraction.

Without the use and proper installation of RNC expansion fittings, the conduit system and its supporting structure could be significantly damaged. This may expose the concealed conductors or energized parts. Be sure to read all installation instructions and follow any UL listing requirements.
_________________________
Bryan P. Holland, MCP

Top
#7252 - 05/14/10 10:51 PM Re: 310.15.(B)(2)(c) [Re: Bryan Holland]
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Way back in my childhood when I did electrical inspections at Clearwater/St. Pete airport and there were long runs of PVC they always used them, and they were always on the plans. Of course, there is vibration to consider as well in that type of construction. But they were used, allright.
_________________________

Top
#7253 - 05/15/10 06:12 PM Re: 310.15.(B)(2)(c) [Re: Nick Sasso]
Ruben Rocha Offline
Senior Member
*****

Registered: 05/24/00
Posts: 767
Bryan you need to give that info to the DOT.
I can't tell you haw many bad joints on a bridge I have seen.

Top



Active Topics
May Meeting Minutes
by Bryan Holland
05/17/12 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
Registered: 05/11/05
Posts: 0
Forum Stats
519 Members
29 Forums
1892 Topics
8569 Posts

Max Online: 53 @ 03/30/12 04:16 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image