Bryan, would not a #2 "ground ring" installed as part of the grounding electrode system be the same as the #8 around a pool(which is required by the code, but no one enforces)?
No. The purpose and function of the grounding electrode system is completely different than the purpose of the equipotential bonding grid.
The purpose of "grounding" is identified in section 250.4(A)(1), wheras the purpose of the equipotential bond is identified in Section 680.26(A). So you may be asking, what is the difference?
Grounding is to limit the voltage imposed on the premise wiring system from an EXTERNAL SOURCE, with lightning being the primary contributor. Euipotential bonding is to limit the voltage at and around the pool from an INTERNAL SOURCE, the pool parts and materials themselves.
Like with equipotential bonding, grounding doesn't dissipate anything. Until the source is removed or de-energized, the possibility of a difference in potential is created, thus resulting in surge currents on parts NOT INTENDED TO CARRY CURRENT.
The ground ring was developed to allow for several lightning down conductors to be attached to the earth and provide a means for establishing a counterpoise at a building or structure. The perimeter bonding ring was established to allow for the 4-point connection from the conductive pool shell and to provide equipoential bonding of the perimeter surfaces fully around the pool, 3 feet out.
So I have to ask if voltage is developed in the Equipotential Plane installed under 547 where would the voltage go?
You have to go back to your theory days to remember that voltage is only the pressure or potential that is present between two or more objects. The only way to ensure no potential is present between two objects is to electrically bond them together. This way, no current can flow between those two objects using a humnan, or in this case, cattle as the circuit.
I guess this is good time to point out that we are indeed talking about THEORY and not LAW or FACT. We could all be wrong...