MENU
Florida Chapter Officers
BOD Chairman
Nelson Montgomery
President
Dan Prater
1st Vice President
Ted Licitra
2nd Vice President
Mark Deegan
3rd Vice President
Richard Wheelus
Chaplain
Vince Dellacroce
Secretary
Joe DuPriest
Treasurer
Eric L Wasser
Parliamentarian
Tim Wright
Who's Online
0 registered (), 5 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Newest Members
ampherder, TonyLutziFlaRep, Jeff Sargent, Kerry Leuzinger, myv5pb
505 Registered Users
Top Posters (30 Days)
Bryan Holland 14
Ruben Rocha 3
Paul J Cameron 3
Nick Sasso 3
inspector32513 3
ronwampler 2
Joe L. DuPriest 1
DickWidera 1
SOwings 1
Google Search
Today's Birthdays
No Birthdays
Page 3 of 4 < 1 2 3 4 >
Topic Options
Rate This Topic
#7314 - 05/30/10 10:29 AM Re: 680.10 [Re: Bryan Holland]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1598
Loc: City of North Port
I forgot to mention one other significant difference between system grounding and equipotential bonding.

Equipotential bonding is a LIFE safety matter. There is no risk of fire, equipment damage, or structural damage from a lack of equipotentail bonding at and around a pool. It's only purpose is to protect PEOPLE from shock.

Grounding is a PROPERTY safety matter. Grounding does NOT protect people from shock or electrocution.


Also keep in mind that neither of these systems are absolute. One limits the voltage imposed (grounding), and the other reduces the potential hazard (equipotntial bonding). Neither allows for the operation of overcurrent devices, and neither protect the contents and equipment of the premise wiring system. Remmber, neither of these two systems are a component of the effective fault path.

It is interesting to note that there are likely millions of pools and structures in the US that do not have proper grounding or equipotential bonding. The current that can be present at a pool is so small that many people can feel the sensation. It is frequently called "tingle voltage" and is in the mA range. In other cases in can be fatal, if it causes you to slip and fall, or perhaps gasp for air while under water.

A lack of grounding of the system doesn't mean much either if that external surge event never occurs. Normally operating currents and fault currents do not rely on the grounding system to operate. So, if you are lucky enough to never have a lightning event, line surege, high-voltage cross-over, or some other surging event be imposed on your system, grounding does and means nothing.



_________________________
Bryan P. Holland, MCP

Top
#7316 - 05/30/10 03:08 PM Re: 680.10 [Re: COTInspector]
Ruben Rocha Offline

Senior Member
*****

Registered: 05/24/00
Posts: 762
Loc: Lutz,FL
Originally Posted By: COTInspector
All I asked was if you all were enforcing 680.10 on PVC associated with the pool.
And I think Bryan, Nick, Paul C, and Paul N all say 680.10 applies to other counduts less than 5' outside edge of pool, but we are so off topic I cannot tell.

I guess we just cannot help ourselves.

Yep called topic drift.

But I think it is straight forward.
680.10 states to refer to the 680.10 table if wiring necessary for pool equipment is within the 5' distance.
So for a light niche I would say you need to maintain the 18" depth for pcv until you exceed the 5' distance.
Looks to me you can't infringe on the 5' distance for anything else but pool equipment.


Now have fun with things such as malibu lights and speaker wiring.(Would you call that pool equipment?)
If not it needs to be beyond the 5' distance.

Or another thought would be the required gfi outlet on a existing dwelling that the contractor trys to place it in a planter.In lieu of adding it on say a porch. But the feed runs less than 5' from the pool shell to get there.(is that pool equipment?)
Topic drift again.
But like you said we can't help it.

Is this fun yet?
The FBC was supposed to make a uniform code for us all. But we still have the subjective determination problem in the field.


Edited by Ruben Rocha (05/30/10 03:28 PM)
Edit Reason: Added Comment
_________________________
Webmaster
IAEI Florida Chapter

Top
#7317 - 05/31/10 06:07 PM Re: 680.10 [Re: Ruben Rocha]
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1101
Loc: Ocklawaha FL.
680.10 allows wiring within 5ft of the pool under two conditions.
1. Wiring for pool associated equipment.
(See cover table 300.5 not cover table 680.10).

2. Wiring not associated with the pool where the property lines do not permit the 5ft separation.
(Table 680.10 Minimum Cover Depths).
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#7318 - 05/31/10 08:08 PM Re: 680.10 [Re: Mike Timpanaro]
Ruben Rocha Offline

Senior Member
*****

Registered: 05/24/00
Posts: 762
Loc: Lutz,FL
I agree Mike but now, how do we determine what actually is pool equipment.
I don't see a definition!
Is a pool lite considered pool equipment? In my mind it does not.
It is a light fixture not equipment.

Also is the required gfi outlet pool equipment?
Looks to me like a outlet not equipment.

This was my feeble attempt to make a point of the dilemma in my prior post.
I guess I might have missed the point on a few statements but still where is some guide line on what pool equipment is. We can probably all agree a pool pump is equipment. But then what else is?


Edited by Ruben Rocha (05/31/10 08:36 PM)
_________________________
Webmaster
IAEI Florida Chapter

Top
#7321 - 06/01/10 09:57 AM Re: 680.10 [Re: Ruben Rocha]
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1101
Loc: Ocklawaha FL.
I would say that it's anything associated with the pool per article 680.

Pool lighting, pumps, heaters, pool cover motors, receptacles, etc. 680.10 comes into play when a shed (for example) in the back yard needs electric and the property line will not permit routing the wiring method beyond the 5ft.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#7326 - 06/02/10 11:43 AM Re: 680.10 [Re: Mike Timpanaro]
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 410
Loc: Pasco County Florida
Quote:
Section 90.3 states that Chapters 1 through 4 apply generally, while Chapters 5, 6, and 7 can supplement or modify the requirements in Chapters 1 through 4. I misunderstood your question earlier. The burial depth for nonmetallic conduit in both Table 300.5 and 680.10 is 18 inches, unless one is in a trench below 2 inches of concrete, then nonmetallic conduit can be installed at 12 inches deep per Table 300.5. However, Section 680.10 and Table 680.10 requires nonmetallic conduit to be installed 18 inches deep without exception so the nonmetallic conduit must be 18 inches deep, not 12 inches as stated in Table 300.5.

From Mark Ode regarding depths of pvc.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#7327 - 06/02/10 12:08 PM Re: 680.10 [Re: Paul J Cameron]
John Belew Offline
Electrical Inspector/Plans Examiner

Registered: 06/26/01
Posts: 56
Loc: Milton,FL
Definition of equipment includes luminaires. ART 100
_________________________
John Belew
Electrical Inspector/Plans Examiner
Santa Rosa Co.
johnb@santarosa.fl.gov

Top
#7328 - 06/02/10 05:46 PM Re: 680.10 [Re: John Belew]
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1101
Loc: Ocklawaha FL.
Paul to what does your comment apply to? Wiring methods as part of pool equipment, or other?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#7329 - 06/02/10 06:08 PM Re: 680.10 [Re: Mike Timpanaro]
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1438
Loc: West Palm Beach
Pool light PVC.





_________________________

Top
#7331 - 06/03/10 01:36 PM Re: 680.10 [Re: Bryan Holland]
Mike Doyle Offline
New Member

Registered: 04/17/09
Posts: 3
Loc: Hillsborough County, Fl
Ruben,
When you refer to the "Red Barron" you really date yourself. LOL

Top
Page 3 of 4 < 1 2 3 4 >



Active Topics
2010 FBC - Significant Changes (North Port List)
by Bryan Holland
02/01/12 02:22 PM
February Meeting Announcement
by Bryan Holland
02/01/12 02:21 PM
January Meeting Minutes
by Bryan Holland
02/01/12 02:20 PM
LISTING FOR SAUNA
by Nick Sasso
01/30/12 11:33 AM
2010 FBC Code Change Questions
by Bryan Holland
01/27/12 12:39 PM
February
M Tu W Th F Sa Su
1 2 3 4 5
6 7 8 9 10 11 12
13 14 15 16 17 18 19
20 21 22 23 24 25 26
27 28 29
Featured Member
Registered: 06/26/08
Posts: 0
Forum Stats
505 Members
29 Forums
1860 Topics
8488 Posts

Max Online: 32 @ 12/14/11 09:55 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image

Upcoming events