#7293 - 05/26/10 09:32 PM
680.10
|
Mechanic Member
   
Registered: 02/14/08
Posts: 129
Loc: Tampa, Florida
|
We are having yet another NEC disagreement in the City of Tampa. I say 680.10 and Table 680.10 are depths for conduits containing wiring not associated with the pool. I first base my opinion on the Handbook statement; “This section allows wiring within 5 ft of the inside walls of the swimming pool under two conditions. The first condition permits wiring to pool-associated equipment such as an underwater luminaire. The second condition permits wiring not associated with the pool within this area where spatial (space) constraints such as property lines preclude the 5-ft minimum separation. Under the second condition, underground wiring located within the 5-ft zone is required to be installed in rigid metal conduit, intermediate metal conduit, or rigid nonmetallic conduit and must be buried to a depth not less than that required by Table 680.10 for these permitted wiring methods. The raceway must be installed as a complete system between points of termination and cannot simply be a sleeve through the 5-ft zone. Beyond the 5-ft zone, the minimum cover requirements of Table 300.5 apply to the underground wiring methods used for circuits rated 600 volts and less.” The commentary specifically says the “under the second condition”, wiring not associated must be buried not less than that required by Table 680.10, pretty cut and dry to me. The Handbook further states; “As indicated by the title of this section (Underground Wiring Location), the focus of 680.10 is to mitigate shock hazards that may occur as a result of a faulty or damaged underground installation that is in close proximity to the swimming pool. Due to water splashing out of the pool and water dripping off those who have been in the pool, the area within 5 ft of the inside walls is generally the wettest location; as a result, electrical leakage from underground installations presents a greater shock hazard in this continuously wet environment.” So is not the interior of the PVC raceway from the pool niche also a continuously wet environment? We install the equipotential bond ring between 18” and 24” from waters edge, would not this #8 equipotential ring dissipate any stray voltage from the underground wiring, especially the 15 volt pool light supply?
Please let me know how you all are looking at the requirements in 680.10.
Thank you, Neal Burdick City of Tampa Construction Inspector II
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7301 - 05/28/10 08:11 AM
Re: 680.10
[Re: COTInspector]
|
Secretary
   
Registered: 10/05/04
Posts: 1599
Loc: City of North Port
|
No, you're still a little off.
The voltage gradients are created by the pool, not by a remote voltage source.
For example, if you install an aluminum frame pool cage on the concrete pool deck that is within 5' of the pool water it needs to be bonded. WHY? Not because it may become energized by stray voltage from an electrical circuit, but due to the fact that a difference in potential can be present between the water and the pool cage. The bonding shorts out this potential.
Stray voltages from a remote source can and will energize the bonded pool parts. The equipotential bonding grid doesn't and can't mitigate that. All the parts bonded together will be energized to that potential until that source is disconnected or the reason for the stray currents is corrected.
Like I stated in my email, think of the pool and its parts like a big battery. All the exposed metal parts that can be touched are like the two electrodes. A voltage potential will be present between these metal parts. A human becomes the circuit connecting the battery, allowing current to flow. Like with a battery, the votlage comes from the battery not from a remote source.
I will be presenting a grounding and bonding class at the July ECF meeting in Tampa. This will not be your typical code based grounding and bonding class.
In this class, I will:
Explain the 3 types of bonding described in the NEC and how they are 3 completely different concepts totaly unrelated.
Explain the 2 ways the term grounding is used in the code that are 2 completely different concpets totaly unrelated.
And most importanly, explain the WHY grounding, bonding, and equipotential bonding is performed.
_________________________
Bryan P. Holland, MCP
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
|
 |
 |
 |
 |
|
|
|