#7293 - 05/26/10 09:32 PM
680.10
|
Mechanic Member
   
Registered: 02/14/08
Posts: 129
Loc: Tampa, Florida
|
We are having yet another NEC disagreement in the City of Tampa. I say 680.10 and Table 680.10 are depths for conduits containing wiring not associated with the pool. I first base my opinion on the Handbook statement; “This section allows wiring within 5 ft of the inside walls of the swimming pool under two conditions. The first condition permits wiring to pool-associated equipment such as an underwater luminaire. The second condition permits wiring not associated with the pool within this area where spatial (space) constraints such as property lines preclude the 5-ft minimum separation. Under the second condition, underground wiring located within the 5-ft zone is required to be installed in rigid metal conduit, intermediate metal conduit, or rigid nonmetallic conduit and must be buried to a depth not less than that required by Table 680.10 for these permitted wiring methods. The raceway must be installed as a complete system between points of termination and cannot simply be a sleeve through the 5-ft zone. Beyond the 5-ft zone, the minimum cover requirements of Table 300.5 apply to the underground wiring methods used for circuits rated 600 volts and less.” The commentary specifically says the “under the second condition”, wiring not associated must be buried not less than that required by Table 680.10, pretty cut and dry to me. The Handbook further states; “As indicated by the title of this section (Underground Wiring Location), the focus of 680.10 is to mitigate shock hazards that may occur as a result of a faulty or damaged underground installation that is in close proximity to the swimming pool. Due to water splashing out of the pool and water dripping off those who have been in the pool, the area within 5 ft of the inside walls is generally the wettest location; as a result, electrical leakage from underground installations presents a greater shock hazard in this continuously wet environment.” So is not the interior of the PVC raceway from the pool niche also a continuously wet environment? We install the equipotential bond ring between 18” and 24” from waters edge, would not this #8 equipotential ring dissipate any stray voltage from the underground wiring, especially the 15 volt pool light supply?
Please let me know how you all are looking at the requirements in 680.10.
Thank you, Neal Burdick City of Tampa Construction Inspector II
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7301 - 05/28/10 08:11 AM
Re: 680.10
[Re: COTInspector]
|
Secretary
   
Registered: 10/05/04
Posts: 1599
Loc: City of North Port
|
No, you're still a little off.
The voltage gradients are created by the pool, not by a remote voltage source.
For example, if you install an aluminum frame pool cage on the concrete pool deck that is within 5' of the pool water it needs to be bonded. WHY? Not because it may become energized by stray voltage from an electrical circuit, but due to the fact that a difference in potential can be present between the water and the pool cage. The bonding shorts out this potential.
Stray voltages from a remote source can and will energize the bonded pool parts. The equipotential bonding grid doesn't and can't mitigate that. All the parts bonded together will be energized to that potential until that source is disconnected or the reason for the stray currents is corrected.
Like I stated in my email, think of the pool and its parts like a big battery. All the exposed metal parts that can be touched are like the two electrodes. A voltage potential will be present between these metal parts. A human becomes the circuit connecting the battery, allowing current to flow. Like with a battery, the votlage comes from the battery not from a remote source.
I will be presenting a grounding and bonding class at the July ECF meeting in Tampa. This will not be your typical code based grounding and bonding class.
In this class, I will:
Explain the 3 types of bonding described in the NEC and how they are 3 completely different concepts totaly unrelated.
Explain the 2 ways the term grounding is used in the code that are 2 completely different concpets totaly unrelated.
And most importanly, explain the WHY grounding, bonding, and equipotential bonding is performed.
_________________________
Bryan P. Holland, MCP
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7311 - 05/29/10 02:05 PM
Re: 680.10
[Re: Ruben Rocha]
|
Mechanic Member
   
Registered: 02/14/08
Posts: 129
Loc: Tampa, Florida
|
All I asked was if you all were enforcing 680.10 on PVC associated with the pool. And I think Bryan, Nick, Paul C, and Paul N all say 680.10 applies to other counduts less than 5' outside edge of pool, but we are so off topic I cannot tell.
I guess we just cannot help ourselves. Bryan, would not a #2 "ground ring" installed as part of the grounding electrode system be the same as the #8 around a pool(which is required by the code, but no one enforces)? There is also big difference between Equipotential Bonding in 680 and the Equipotential Plane required in 547. I agree that a bond ring is required at items covered by 680 whether or not it has electric service. From Article 680 in the 2008 Handbook "The installations covered by this article can be indoors or outdoors, permanent or storable, and may or may not be directly supplied by electrical circuits of any nature". But Article 547 differs; The Equipotential Plane is only required in confinement areas with concrete floors where metallic equipment is located that may become energized and is accessible to livestock. This plane is only required where metallic equipment may become energized, so I would say it would have to have electrical service to become energized. This #8 must be connected to the electrical grounding system (which differs from 680)to prevent a difference in voltage from developing within the plane. So I have to ask if voltage is developed in the Equipotential Plane installed under 547 where would the voltage go?
IMHO Neal Burdick City of Tampa Construction Inspector II
Edited by COTInspector (05/29/10 02:16 PM)
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7313 - 05/29/10 10:54 PM
Re: 680.10
[Re: COTInspector]
|
Secretary
   
Registered: 10/05/04
Posts: 1599
Loc: City of North Port
|
Bryan, would not a #2 "ground ring" installed as part of the grounding electrode system be the same as the #8 around a pool(which is required by the code, but no one enforces)?
No. The purpose and function of the grounding electrode system is completely different than the purpose of the equipotential bonding grid. The purpose of "grounding" is identified in section 250.4(A)(1), wheras the purpose of the equipotential bond is identified in Section 680.26(A). So you may be asking, what is the difference? Grounding is to limit the voltage imposed on the premise wiring system from an EXTERNAL SOURCE, with lightning being the primary contributor. Euipotential bonding is to limit the voltage at and around the pool from an INTERNAL SOURCE, the pool parts and materials themselves. Like with equipotential bonding, grounding doesn't dissipate anything. Until the source is removed or de-energized, the possibility of a difference in potential is created, thus resulting in surge currents on parts NOT INTENDED TO CARRY CURRENT. The ground ring was developed to allow for several lightning down conductors to be attached to the earth and provide a means for establishing a counterpoise at a building or structure. The perimeter bonding ring was established to allow for the 4-point connection from the conductive pool shell and to provide equipoential bonding of the perimeter surfaces fully around the pool, 3 feet out. So I have to ask if voltage is developed in the Equipotential Plane installed under 547 where would the voltage go? You have to go back to your theory days to remember that voltage is only the pressure or potential that is present between two or more objects. The only way to ensure no potential is present between two objects is to electrically bond them together. This way, no current can flow between those two objects using a humnan, or in this case, cattle as the circuit. I guess this is good time to point out that we are indeed talking about THEORY and not LAW or FACT. We could all be wrong...
Edited by Bryan Holland (05/30/10 09:15 AM)
_________________________
Bryan P. Holland, MCP
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7314 - 05/30/10 09:29 AM
Re: 680.10
[Re: Bryan Holland]
|
Secretary
   
Registered: 10/05/04
Posts: 1599
Loc: City of North Port
|
I forgot to mention one other significant difference between system grounding and equipotential bonding.
Equipotential bonding is a LIFE safety matter. There is no risk of fire, equipment damage, or structural damage from a lack of equipotentail bonding at and around a pool. It's only purpose is to protect PEOPLE from shock.
Grounding is a PROPERTY safety matter. Grounding does NOT protect people from shock or electrocution.
Also keep in mind that neither of these systems are absolute. One limits the voltage imposed (grounding), and the other reduces the potential hazard (equipotntial bonding). Neither allows for the operation of overcurrent devices, and neither protect the contents and equipment of the premise wiring system. Remmber, neither of these two systems are a component of the effective fault path.
It is interesting to note that there are likely millions of pools and structures in the US that do not have proper grounding or equipotential bonding. The current that can be present at a pool is so small that many people can feel the sensation. It is frequently called "tingle voltage" and is in the mA range. In other cases in can be fatal, if it causes you to slip and fall, or perhaps gasp for air while under water.
A lack of grounding of the system doesn't mean much either if that external surge event never occurs. Normally operating currents and fault currents do not rely on the grounding system to operate. So, if you are lucky enough to never have a lightning event, line surege, high-voltage cross-over, or some other surging event be imposed on your system, grounding does and means nothing.
_________________________
Bryan P. Holland, MCP
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7316 - 05/30/10 02:08 PM
Re: 680.10
[Re: COTInspector]
|
Senior Member
   
Registered: 05/24/00
Posts: 763
Loc: Lutz,FL
|
All I asked was if you all were enforcing 680.10 on PVC associated with the pool. And I think Bryan, Nick, Paul C, and Paul N all say 680.10 applies to other counduts less than 5' outside edge of pool, but we are so off topic I cannot tell.
I guess we just cannot help ourselves. Yep called topic drift. But I think it is straight forward. 680.10 states to refer to the 680.10 table if wiring necessary for pool equipment is within the 5' distance. So for a light niche I would say you need to maintain the 18" depth for pcv until you exceed the 5' distance. Looks to me you can't infringe on the 5' distance for anything else but pool equipment. Now have fun with things such as malibu lights and speaker wiring.(Would you call that pool equipment?) If not it needs to be beyond the 5' distance. Or another thought would be the required gfi outlet on a existing dwelling that the contractor trys to place it in a planter.In lieu of adding it on say a porch. But the feed runs less than 5' from the pool shell to get there.(is that pool equipment?) Topic drift again. But like you said we can't help it. Is this fun yet? The FBC was supposed to make a uniform code for us all. But we still have the subjective determination problem in the field.
Edited by Ruben Rocha (05/30/10 02:28 PM) Edit Reason: Added Comment
_________________________
Webmaster IAEI Florida Chapter
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
|
 |
 |
 |
 |
|
|
|