Please see
http://www.harborfreight.com/lawn-garden/power-tools/2-1-2-half-hp-chipper-shredder-66910.html.This chipper is rated at 15A and provided with a AWG#12 cord with a parallel blade attachment plug cap.
If I understand NEC 430.22 (and the associated Table 430.248)correctly a 2 1/2 HP motor needs to be provided with conductors rated at least 29A (interpolating between the 2 HP and 3 HP values in the Table).
How can the chipper be rated both 15A as well as 2 1/2 HP even for intermittent use? I thought the use of the table was mandatory to determine full load curent.
There is also an another specification for 40A maximum. Presumably, this is the motor start-up maximum and is intended to define the OCPD. But how can a 40A OCPD be used for a general purpose AWG #12 conductor branch circuit with general purpose receptacles?
There are no indications that the product has UL Listing or equivalent.
Am I justified in getting an uncomfortable feeling that this appliance and recommended use does not comply with the NEC?
Thanks for your help.
Heinz R.