I have to ask some dumb questions;
Why is Table 250.66 still in the Code Book, maybe we can get Bill Pancake to get it removed if no one uses a fully sized grounding electrode system anymore?
Table 250.66 is required to be used "except as permitted in 250.66(A) through (C). So, GEC's bonding metal underground water pipe and metal frame of the building or structure electrodes are sized to the Table. Also keep in mind that other bonding and grounding components are sized to Table 250.66 such as Equipment Bonding Jumpers on Supply Side of Service.
When does a grounding electrode as described in 250.52(A) (1) through (A) (7) become present? If the foundation is already poured when the electrical contractor arrives on the site is he now exempt from using the concrete encased electrode as part of the grounding electrode system (not present anymore right)?
No. The electrode is present. This is not a code issue but a cooridnation issue. It is the responsibility of the builder to properly schedule his contractors to perform work at the appropriate time. It wouldn't make sense for a builder to install all the drywall in a structure before the electrical wiring has been installed, just as it doesn;t make sense for a builder to pour the footings prior to the CEE being installed.
If the electrician has #2 copper wire and a ground rod on his truck when he pulls up on a site, is he now required to install a ground ring and a ground rod (present right)?
Of course not. Remember, section 250.50 requires all the electrodes that are present to be BONDED together to form the GES. It is only when they do not exist at the strucutre that you are required to create / install the electrode.
If none of the electrodes exist how many of grounding electrodes specified in 250.52(A) (4) through (A) (8) are required to be installed and used, one or more?/[quote]
The section is clear; "ONE or MORE."
[quote]Would it also be ok to ground a 2,000 amp service with one ground rod connected to a #6 copper grounding electrode conductor if there are no other electrodes present?
YES!
If this GES has greater than 25 ohms resistance, we can just add one additional ground rod tie the 2 rods together with a #6 and call it a properly grounded system?
YES!
I personally do not believe, especially after re-reading Chapter 6 in the Soares 10th edition several times, that a #4 GEC to a 250.52 (A) (3) electrode for any service above 200 amps, meets the performance requirements stated in 250.4.
Then as soon as you become a PE or electrical engineer that is free to design the grounding electrode system on your prjects in any manner you wish, we can only enforce the requirements of the code as they are written.
GOOD QUESTIONS !!!