I bet, back in your younger days, the GES was a metal water piping system that spanned the city.
Now it is likely to be a Ufer at best and could just be a couple of rods that struggle to get 15 or 20 ohms to the sand. It takes a GES with less than 6 ohms to trip a 20a breaker and that won't cook off for a while. I bet a 20a bolted fault into a rod would cook off the water and increase in resistance before the breaker tripped.
Your only hope would be if your rod was in the ground water ... but then it may have corroded away in a few years.
This would be a good study for one of these university engineering departments. Send the students out with real ground performance equipment and evaluate the GES in various buildings around town. Pull some rods that have been in the ground for 10-15 years and see what you have. Inspect the clamps.
I bet, if the FBC really looked at that study we would be doing CadWelds on rods, banning steel core rods and certainly requiring something in addition to a rod or two. I know for a fact that the 15 year old clamp on the rod at this house was not working when I moved in and there was only the one rod.