#7601 - 07/28/10 07:11 PM
Re: GEC to footer steel
[Re: Ruben Rocha]
|
Post-A-Holic Member
  
Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
|
So what you are saying is that technically, the connection to the doohickey needs to be at the bottom of the footer, in order to be a true concrete cased electrode.
I never liked the rebar-sticking-out method that was used in Pinellas for years, because as Ruben mentions the rebar is left exposed and corrodes, and so does the connection. Sometimes the rebar was even stubbed below grade. From experience I can say that the connections were frequently loose, and the gardener was somehow magnetically drawn to this connection point, which would get knocked into by his shovel or weedwacker, I never knew which. Or maybe it was the dreaded sprinkler guy (they have some real neat wiring methods, too).
Then others - partially agreeing with this logic - invented a new method - turn up the rebar into an interior wall and make the connection there. Ok fine, but...is that really 20' of rebar near the bottom of a concrete footing? Or is that a splice? Did anyone check the steel twisty-ties to see if they were tight? Is the 90 even connected to the footing? Or did the steel guy just "conveniently" stick it in the right spot, without even splicing it? If there was a splice, did it have proper lap? Did someone even check for lap? Has this method even been tested? (Don't laugh in Poke County to this day, some stick the 90's in after the slab is poured, breaking about every code in the book)
So after a decade or more of reinventing ways to confuse and confound the simple and pure, unadulterated, concrete encased electrode, the truth of the matter is that the connection to the doohickey needs to be at the bottom of the concrete footer, in order to be a true concrete cased electrode.......and sorry John I thought there was a post on this, my mistake.
_________________________
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7606 - 07/29/10 03:54 PM
Re: GEC to footer steel
[Re: psnorthrup]
|
Secretary
   
Registered: 10/05/04
Posts: 1622
Loc: City of North Port
|
Looking at the situation purely from an electrical standpoint, it really doesn't make any real difference. As long as the prescriptive requirements of 250.42(A)(3) are met, the actual orientation of the rebar and where the GEC connects will not functionaly change its performance.
That being said, I agree that the electrode itself should be encased, thus the GEC conection and a portion of the GEC should also be encased. If the rebar leaves its encasement its no longer an electrode and it doesn't qualify as a GEC.
I feel one solution would be to allow a vertical portion of the rebar to serve as the connection point if that rebar is in a poured cell. That way, the prescritive requirements of the section are met by the portion of the rebar in the horizontal footing. The short vertical section also gets encased along with the GEC connection. This is permitted by 250.68(A) Exception No. 2.
Another solution is to make the GEC conenction near the top of the slab/floor where the rebar protrudes up, cut of the rebar, and then form and pour the assembly to re-encase the whole thing.
From a structural stand-point, as long as the rebar is not being used as reinforcement, its really not under the scope of the building code. But, that still doesn't change the fact that it could pose a corrosive hazard to the concrete over time. The effect would be much less if the rebar is stubbed up in an interior wood / metal framed wall rather than an exterior masonry wall.
This is a good topic...
_________________________
Bryan P. Holland, MCP
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7638 - 08/11/10 07:53 AM
Re: GEC to footer steel
[Re: COTInspector]
|
Secretary
   
Registered: 10/05/04
Posts: 1622
Loc: City of North Port
|
I have to ask some dumb questions; Why is Table 250.66 still in the Code Book, maybe we can get Bill Pancake to get it removed if no one uses a fully sized grounding electrode system anymore? Table 250.66 is required to be used "except as permitted in 250.66(A) through (C). So, GEC's bonding metal underground water pipe and metal frame of the building or structure electrodes are sized to the Table. Also keep in mind that other bonding and grounding components are sized to Table 250.66 such as Equipment Bonding Jumpers on Supply Side of Service. When does a grounding electrode as described in 250.52(A) (1) through (A) (7) become present? If the foundation is already poured when the electrical contractor arrives on the site is he now exempt from using the concrete encased electrode as part of the grounding electrode system (not present anymore right)? No. The electrode is present. This is not a code issue but a cooridnation issue. It is the responsibility of the builder to properly schedule his contractors to perform work at the appropriate time. It wouldn't make sense for a builder to install all the drywall in a structure before the electrical wiring has been installed, just as it doesn;t make sense for a builder to pour the footings prior to the CEE being installed. If the electrician has #2 copper wire and a ground rod on his truck when he pulls up on a site, is he now required to install a ground ring and a ground rod (present right)? Of course not. Remember, section 250.50 requires all the electrodes that are present to be BONDED together to form the GES. It is only when they do not exist at the strucutre that you are required to create / install the electrode. If none of the electrodes exist how many of grounding electrodes specified in 250.52(A) (4) through (A) (8) are required to be installed and used, one or more?/[quote]
The section is clear; "ONE or MORE."
[quote]Would it also be ok to ground a 2,000 amp service with one ground rod connected to a #6 copper grounding electrode conductor if there are no other electrodes present? YES! If this GES has greater than 25 ohms resistance, we can just add one additional ground rod tie the 2 rods together with a #6 and call it a properly grounded system? YES! I personally do not believe, especially after re-reading Chapter 6 in the Soares 10th edition several times, that a #4 GEC to a 250.52 (A) (3) electrode for any service above 200 amps, meets the performance requirements stated in 250.4. Then as soon as you become a PE or electrical engineer that is free to design the grounding electrode system on your prjects in any manner you wish, we can only enforce the requirements of the code as they are written. GOOD QUESTIONS !!!
_________________________
Bryan P. Holland, MCP
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7643 - 08/11/10 06:53 PM
Re: GEC to footer steel
[Re: COTInspector]
|
Apprentice Member
Registered: 05/30/07
Posts: 47
Loc: Marathon, Florida
|
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7646 - 08/12/10 07:40 AM
Re: GEC to footer steel
[Re: COTInspector]
|
Secretary
   
Registered: 10/05/04
Posts: 1622
Loc: City of North Port
|
The "performance" of the grounding electrode system is all in the bonding aspects of the system. The actual grounding component does not have all that much signifigance. In order for a hazard to be present during a 250.4(A)(1) event, there must be an imposed voltage. If all the non-current carrying metal parts of the system(s), the grounded service conductor, the system EGC's, the service equipment enclousres, and the earth are all bonded together per code, there will be no voltage potential between those parts thus no current will flow for the duration of the event.
So why it is important that the earth be a component of this protection system, it is not the essential or critical aspect. The overall circuit impedance of the earthing connection are really not all that important. Clearly, a single #6 AWG conductor terminating at a single 8' ground rod is all that is really needed to perform effective grounding of the system. However, it is essential that you BOND any other electrode that is present to ensure no potential is created between the different grounded elements.
So in essence, the pupose of 250.50 is NOT an attempt to create as many grounding connections as possible, but rather to ensure that all present grounding connections are bonded together.
GET IT?
_________________________
Bryan P. Holland, MCP
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7651 - 08/12/10 01:49 PM
Re: GEC to footer steel
[Re: Bryan Holland]
|
gfretwell
Unregistered
|
Neal, the visqueen should not be extended under the footer, only to the edge of the floor. Bryan, I will throw more gas on the fire. How much neutral current do you figure the earth is carrying? I know on my street where we have wye distribution there is current on all of the transformer grounding electrode conductors going down the pole and I have a couple of amps on the drop neutral coming into the house with the main breaker off. I talked to my FPL lineman neighbor about it and he didn't even grasp the concept that all of the current was not going to go down that aluminum/steel 2 gauge strand they bond to and he assumed that ground wire would assure zero volts because a foot or so of the #6 was coiled and stapled to the bottom of a pole 6-8 feet in the ground. When I started talking about voltage drop his eyes glazed over. This particular string of 20 transformers is about a 3/4 mile long. How many volts do you figure they drop along that strand? How much do you figure the earth tries to make that up? This does take some of the mystery out of where "stray voltage" can come from. The street behind my house is fed from another phase on the distribution and I have always wondered what the voltage difference would be between his ground electrode and mine. I certainly would not want to string a LAN cable between our houses. 
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7656 - 08/12/10 10:38 PM
Re: GEC to footer steel
[Re: ]
|
Mechanic Member
   
Registered: 02/14/08
Posts: 132
Loc: Tampa, Florida
|
I really need to be studying for my P1 exam rather then discussing something that has been some of the most unclear and poorly written code sections for over 75 years, but here I go again.
And by the way I do “Get It” as I have designed and installed many approved grounding electrode systems that are still performing as required by the NEC for over 25 years,as well as having inspected a 1,000 or so GES in the last five years.
Part of the problem here is not understanding what word “system” means. “System (noun) a group or combination of interrelated, interdependent, or interacting elements forming a collective entity; a methodical or coordinated assemblage of parts, facts, concepts.”
“250.50 Grounding Electrode System (there is that word). All (not just one electrode but all) grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present (only (A)(1), (2), (3), or (8) would be present during normal construction all other electrodes are only present if you bring them, why do they include (A)(4) – (A)(7)????) at each building or structure served shall be bonded together to form the grounding electrode system (there is that word again). Where none of these grounding electrodes exist, one or more (I choose more) of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.
Even the NEC handbook encourages the formation of a system of electrodes, which adds reliability and ensures performance.
“Section 250.50 introduces the important concept of a “grounding electrode system,” in which all electrodes are bonded together. Rather than total reliance on a single grounding electrode to perform its function over the life of the electrical installation, the NEC encourages the formation of a system of electrodes “that are present at each building or structure served.” No doubt, building a system of electrodes adds a level of reliability and helps ensure system performance over a long period of time.”
In the City of Tampa on a non-reviewed new construction services we encourage and get a concrete encased electrode, and two ground rods. The electrode to the CCE is sized to table 250.66 based on the service entrance conductors. For a service upgrade on an existing structure we require two ground rods, and a water connection if still metallic pipe, once again sized according to 250.66. This has been the practice in Tampa longer than the 5 years I have been there, and I believe the systems installed are meeting the “intent” of the code for the GES.
In my opinion if an electrical contractor, electrical engineer, plans examiner, electrical inspector, installed, designed, approved the plans, approved an inspection on a grounding electrode system that only had a #4 copper wire connected to a concrete encased electrode on a service with larger than 3/0 copper service conductors, rhey should look for a new career.
Well I need to go study plumbing, I’m done with this one thanks for reading.
Neal Burdick
My Opinions and Mine alone
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7657 - 08/13/10 08:06 AM
Re: GEC to footer steel
[Re: COTInspector]
|
Secretary
   
Registered: 10/05/04
Posts: 1622
Loc: City of North Port
|
And by the way I do “Get It” as I have designed and installed many approved grounding electrode systems that are still performing as required by the NEC for over 25 years,as well as having inspected a 1,000 or so GES in the last five years. I don't think anyone here is questioning what you know Neal, certainly not me. I've seen the CMP-5 members themselves argue over the meaning of a section. If they can't figure it out, no wonder we have these discussions out in the real world. Part of the problem here is not understanding what word “system” means. “System (noun) a group or combination of interrelated, interdependent, or interacting elements forming a collective entity; a methodical or coordinated assemblage of parts, facts, concepts.” “250.50 Grounding Electrode System (there is that word).All (not just one electrode but all) grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present (only (A)(1), (2), (3), or (8) would be present during normal construction all other electrodes are only present if you bring them, why do they include (A)(4) – (A)(7)????) at each building or structure served shall be bonded together to form the grounding electrode system (there is that word again). Where none of these grounding electrodes exist, one or more (I choose more) of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used. The grounding electrode system is more than just the electrodes. The system is the electrodes, the GEC, the fittings and connectors, etc. The reason 250.50 requires ALL the electrodes that are present to be bonded is to prevent an electrode that is present from not be bonded. So, if someone were to drive a ground rod, required or not, it is now present and must be bonded to the grounding electrode system. Again, a designer can include as many electrodes as they wish, however the code stipulates they must all be bonded. Even the NEC handbook encourages the formation of a system of electrodes, which adds reliability and ensures performance.“Section 250.50 introduces the important concept of a “grounding electrode system,” in which all electrodes are bonded together. Rather than total reliance on a single grounding electrode to perform its function over the life of the electrical installation, the NEC encourages the formation of a system of electrodes “that are present at each building or structure served.” No doubt, building a system of electrodes adds a level of reliability and helps ensure system performance over a long period of time.” That's great, but not enforceable. The code is a minimum and the minimum is all that is required.Why not require two or more of everything required by the code? That would certainly be better. Instead of just one required lighting outlet per room, lets make it two just in case one doesn't work. Instead of just one receptacle within 3' of a bathroom sink, let's make it two just because redundancy is better. You can quickly see how this can get out-of-hand. In the City of Tampa on a non-reviewed new construction services we encourage and get a concrete encased electrode, and two ground rods. The electrode to the CCE is sized to table 250.66 based on the service entrance conductors. For a service upgrade on an existing structure we require two ground rods, and a water connection if still metallic pipe, once again sized according to 250.66. This has been the practice in Tampa longer than the 5 years I have been there, and I believe the systems installed are meeting the “intent” of the code for the GES. I think this is an incorrect interpretation of the code. If the city of Tampa believes this is the appropriate method of grounding for their jurisidiction, they should submit a proposal to the NFPA or the Florida Building Commission to have the rule changed. Until then, the city really has no legal basis for requiring anything more than the code.