#7669 - 08/15/10 12:51 PM
Re: LOAD CALCULATIONS FOR RESIDENTIAL HOME
[Re: inspector32513]
|
Secretary
   
Registered: 10/05/04
Posts: 1622
Loc: City of North Port
|
We have had this discussion here a few times before. To start with, I find it "funny" that a permit applicant would be telling the building department what they are or are not required for their submittal documents. That's a bad start...
I find the matter to be cut-and-dry. The building department may not require a load calculation for a particular project. However, if a load calculation IS requested, two licensed professionals are identified by the FBC and F.S. as being qualified to provide those calculations.
Section 105.3.1.2(4)&(5) of the FBC states that only electrical engieers (FS471 Licensed) may prepare electrical documents unless the work is exempt under F.S. 471.003(2)(h). In that section of the F.S., certain work (cost and amperage thresholds) is permitted to be prepared by a FS489 licensed contractor. In most cases, residential work meets the limitations of that statute.
So, if the applicant does not want to employ a PE to perform the requested load calcs, a licensed electrical contractor would be permitted to prepare that calc for submittal.
As Dick noted in his post, I too have performed the calculations myself on submitted permit applications to show reason for rejection the design.,,
_________________________
Bryan P. Holland, MCP
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7670 - 08/15/10 02:04 PM
Re: LOAD CALCULATIONS FOR RESIDENTIAL HOME
[Re: Bryan Holland]
|
Post-A-Holic Member
  
Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
|
HotSparks, If anyone tells you that you cannot require a load calculation, tell them to study the NEC. IT IS THE NEC AND IT IS THE JURISDICTIONS RIGHT TO REQUIRE, YES REQUIRE, A LOAD CALCULATION FOR ANY PROJECT: 215.5 Diagrams of Feeders. If required by the authority having jurisdiction, a diagram showing feeder details shall be provided prior to the installation of the feeders. Such a diagram shall show the area in square feet of the building or other structure supplied by each feeder, the total calculated load before applying demand factors, the demand factors used, the calculated load after applying demand factors, and the size and type of conductors to be used.Sorry - I had to cut and paste from the 2005 but it is the same Article in the 2008 and I believe the wording is the same. It may not be in 220 like everybody thinks it is, but it is for sure in the NEC. "Now get out there and get 'em boys!"
Edited by Nick Sasso (08/15/10 02:05 PM)
_________________________
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#7676 - 08/16/10 01:21 PM
Re: LOAD CALCULATIONS FOR RESIDENTIAL HOME
[Re: Paul J Cameron]
|
Post-A-Holic Member
  
Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
|
A service is also required to comply with a calculated load from article 220. 230.79 Rating of Service Disconnecting Means. The service disconnecting means shall have a rating not less than the calculated load to be carried, determined in accordance with Part III, IV, or V of Article 220, as applicable. In no case shall the rating be lower than specified in 230.79(A), (B), (C), or (D).
230.42 Minimum Size and Rating. (A) General. The ampacity of the service-entrance conductors before the application of any adjustment or correction factors shall not be less than either (A)(1) or (A)(2). Loads shall be determined in accordance with Part III, IV, or V of Article 220, as applicable. Ampacity shall be determined from 310.15. The maximum allowable current of busways shall be that value for which the busway has been listed or labeled. (1) The sum of the noncontinuous loads plus 125 percent of continuous loads (2) The sum of the noncontinuous load plus the continuous load if the service-entrance conductors terminate in an overcurrent device where both the overcurrent device and its assembly are listed for operation at 100 percent of their rating
_________________________
Michael J Timpanaro Inspector/Plans Examiner/CEU Instructor Florida
|
|