MENU
Florida Chapter Officers
BOD Chairman
Nelson Montgomery
President
Dan Prater
1st Vice President
Ted Licitra
2nd Vice President
Mark Deegan
3rd Vice President
Richard Wheelus
Chaplain
Vince Dellacroce
Secretary
Joe DuPriest
Treasurer
Eric L Wasser
Parliamentarian
Tim Wright
Who's Online
0 registered (), 0 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Newest Members
onzevil1, beaing, ampherder, TonyLutziFlaRep, Jeff Sargent
507 Registered Users
Top Posters (30 Days)
Bryan Holland 13
Ruben Rocha 5
Nick Sasso 3
inspector32513 3
ronwampler 2
DickWidera 1
Google Search
Today's Birthdays
No Birthdays
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#7717 - 08/28/10 10:56 AM Atticle 400.8(5) Cords in ceilings
SOwings Offline
CBO, PX, BN, ER, EN

Registered: 01/22/10
Posts: 46
Loc: Nassau County
I was talking with My BO the other day and he was involved in a discussion about cords run through ceiling tiles to plug in projectors hung from a suspended ceiling with the receptacle above. This is prohibited by 400.8(2) but as I read further, I stopped at 400.8(5) which seem to prohibit ANY cords above a suspended ceiling. This concerns me since more than once I have had an Air Handler installed above the ceiling and the mechanical contractor has used a cord connected pump to get the condensate out of the building. have had other instances like this on other occasions.
So, while I know of no article that prohibits receptacles above a ceiling, this article seems to prohibit any permanent cord connected devices from being installed above a ceiling.

I would love some imput.

Top
#7718 - 08/30/10 11:57 AM Re: Atticle 400.8(5) Cords in ceilings [Re: SOwings]
Rob Barbee Offline
Mechanic Member
***

Registered: 06/24/08
Posts: 120
Loc: Pinellas County
Your last sentence says it. Receps above susp. ceiling is allowed, you just can't plug anything in!
_________________________
Rob
Electrical Inspector

Top
#7719 - 08/30/10 12:06 PM Re: Atticle 400.8(5) Cords in ceilings [Re: SOwings]
Nick Sasso Online   content

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1438
Loc: West Palm Beach
400.7 may allow the condensate pump - "Appliances where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance and repair, and the appliance is intended or identified for flexible cord connection"


Edited by Nick Sasso (08/30/10 12:07 PM)
_________________________

Top
#7720 - 08/30/10 03:09 PM Re: Atticle 400.8(5) Cords in ceilings [Re: SOwings]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1600
Loc: City of North Port
I agree with the above statements. A receptacle outlet above the ceiling would facilitate temporary cord-and-plug connection for maintenance and repair issues. A good example would be Section 210.63 of the NEC / Section 306.3.1 of the FMC which require a receptacle at an air handler above a drop ceiling.

Flexible cords and cables directly assoicated with the operation of the appliance like condensate pumps, or condensate float switches would be permitted under the 400.7 criteria as mentioned by Nick.

It may seem like a fine line, but the generally accepted practices...





_________________________
Bryan P. Holland, MCP

Top
#7721 - 08/30/10 05:04 PM Re: Atticle 400.8(5) Cords in ceilings [Re: Bryan Holland]
SOwings Offline
CBO, PX, BN, ER, EN

Registered: 01/22/10
Posts: 46
Loc: Nassau County
Yes, I saw 400.7 and in the past that is how I have addressed condensate pumps but I have to wonder that the statement in 400.7 is a general statement and 400.8(5) is specific to a particular location (installation). I was always taught that a specific code overrules a general one.

Top
#7722 - 08/30/10 05:25 PM Re: Atticle 400.8(5) Cords in ceilings [Re: SOwings]
Nick Sasso Online   content

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1438
Loc: West Palm Beach
One or both articles could probably use some tweaking.

One thing to watch for is a plenum ceiling. Then it is a
"no way" for the cord and the pump as well.







Edited by Nick Sasso (08/30/10 05:25 PM)
_________________________

Top
#7724 - 09/01/10 08:03 PM Re: Atticle 400.8(5) Cords in ceilings [Re: SOwings]
SOwings Offline
CBO, PX, BN, ER, EN

Registered: 01/22/10
Posts: 46
Loc: Nassau County
I think the final answer is as someone at the NE Fl. IAEI meeting pointed out, that the beginning of 400.8 says "Unless specifically permitted in 400.7...." which tells me that 400.7(8) would prevail and this, in turn, would allow it if it was an appliance as describe there. Interesting, this would also probably make it allowable for security cameras to have their cords run up through the ceiling...

Top
#7725 - 09/01/10 08:41 PM Re: Atticle 400.8(5) Cords in ceilings [Re: SOwings]
Nick Sasso Online   content

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1438
Loc: West Palm Beach
That would most definitely not be permitted. You can never run a cord through a suspended ceiling.

If I follow the post correctly, your original question had the scenario of a condensate pump (already above the ceiling) being plugged in (above ceiling), and now you are talking about a camera (below ceiling) running the cord through the ceiling tile and plugging it in (above ceiling).

Not permitted. See 400.8.
_________________________

Top
#7727 - 09/01/10 09:02 PM Re: Atticle 400.8(5) Cords in ceilings [Re: SOwings]
Ruben Rocha Offline

Senior Member
*****

Registered: 05/24/00
Posts: 764
Loc: Lutz,FL
Reminds me of last week where the local gas station was running extension cords in the suspended ceiling to power up the new beer neon signs.
I guess that would be okay. Ha Ha
_________________________
Webmaster
IAEI Florida Chapter

Top
#7743 - 09/08/10 05:15 PM Re: Atticle 400.8(5) Cords in ceilings [Re: Ruben Rocha]
SOwings Offline
CBO, PX, BN, ER, EN

Registered: 01/22/10
Posts: 46
Loc: Nassau County
If you read 400.8, you would think that No cords could be run through a ceiling, but since 400.8 excepts ALL of the permitted uses of 400.7, you have to read 400.7(8) which reads
"Appliances where the fastening means and the mechanical connections are specifically designed to permit ready removal for maintenance and repair, and the appliance is intended or identified for flexible cord connection."
You either would have to say that fit this description are exempt from 400.8 or that 400.8 prevails in certain conditions (contrary to the opening sentence of 400.8).
Extension cord are independent of the appliance and so that is not relevant. Did you check to see if the cord was within 20 feet of the pump?


Edited by SOwings (09/08/10 05:17 PM)

Top
Page 1 of 2 1 2 >



Active Topics
Moving site.
by Ruben Rocha
Yesterday at 06:43 PM
2010 FBC - Significant Changes (North Port List)
by Bryan Holland
02/01/12 01:22 PM
February Meeting Announcement
by Bryan Holland
02/01/12 01:21 PM
January Meeting Minutes
by Bryan Holland
02/01/12 01:20 PM
LISTING FOR SAUNA
by Nick Sasso
01/30/12 10:33 AM
February
M Tu W Th F Sa Su
1 2 3 4 5
6 7 8 9 10 11 12
13 14 15 16 17 18 19
20 21 22 23 24 25 26
27 28 29
Featured Member
Registered: 05/10/03
Posts: 0
Forum Stats
506 Members
29 Forums
1861 Topics
8492 Posts

Max Online: 32 @ 12/14/11 08:55 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image

Upcoming events