#7942 - 01/07/11 10:49 AM NM installed under a house
COTInspector Offline
Mechanic Member
*****

Registered: 02/14/08
Posts: 132
Loc: Tampa, Florida
We have someone challenging that the crawl space under a SFD is not a damp location.
Our supervision says that the NEC definition is to vague to make a ruling on the location.
They are saying that if the crawl space is open or properly ventilated that it would not be considered a damp location by the Florida Building Code.
We did bring up the fact that if mechanical duct work is installed under a house it must be rated for the damp environment encountered.
There are other inspection agencies in our area still allowing NM cable in these areas.
How are you guys looking at this type of installation?

Neal Burdick
City of Tampa
Construction Inspector II

Top
#7943 - 01/07/11 11:05 AM Re: NM installed under a house [Re: COTInspector]
TerryR Offline
Apprentice Member

Registered: 03/31/05
Posts: 19
Loc: Key West Florida
NM cable has always been allowed under residences here,however since 2005 we have not allowed it below the flood plane.
_________________________
Terence N Richardson
City of Key West
Electrical/Mechanical
Inspector/Plan Examiner
(305)809-3961

Top
#7944 - 01/07/11 12:38 PM Re: NM installed under a house [Re: TerryR]
COTInspector Offline
Mechanic Member
*****

Registered: 02/14/08
Posts: 132
Loc: Tampa, Florida
We allowed it also until the 2008 NEC change in 334.12(B)(4).
When we asked our "Buiding" inspectors what type of location (wet, damp, dry) was the crawl space area, they told us that it was considered a damp location. So with the 2008 NEC change NM or NMS could no longer be installed under a house in the crawl space area. Now our supervisor is saying that it is not a damp location, so my question is, do you and your departments consider this a damp location.

Thank you,
Neal Burdick
COT Construction Inspector II

Top
#7945 - 01/07/11 12:54 PM Re: NM installed under a house [Re: COTInspector]
psnorthrup Offline
Mechanic Member

Registered: 04/23/07
Posts: 115
Loc: Plant City
Hey Neal; We allow it in existing buildings only for repair. New circuits or complete rewire to be done IAW 2008 NEC, under the house is as we see it a damp location

Top
#7946 - 01/07/11 12:56 PM Re: NM installed under a house [Re: COTInspector]
gfretwell
Unregistered


If your crawlspace is damp enough to saturate the paper packing in RX (the best explanation of the hazard I have heard), I would be more worried about mold and rotting of the structural floor.

Top
#7947 - 01/07/11 02:26 PM Re: NM installed under a house [Re: COTInspector]
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
See editor's note for question 60 below (I have underlined it). Apparently it is just "one of those things," and I would tend to agree with your supervisor - unless rain can blow into this area easily. I also agree with the previous comments on flood plane.

International Association of Electrical Inspectors
75th Anniversary Diamond Jubilee Meeting
Coronado Springs Resort – Lake Buena Vista, Florida
September 7-13, 2003

Code Questions

The answers to the code questions are given as they were submitted by the Code Panelist. They do not necessarily reflect the official position or interpretation of the IAEI nor should they be considered as an official interpretation of the Code. An “Editor’s Note” shown in brackets has been provided when additional clarification was necessary, which also is not an official interpretation. An interpretation is only official when expressed from the applicable Authority Having Jurisdiction (AHJ).

60. Is the crawl space of a pier-and-beam dwelling unit considered to be a damp or dry location? If this is a damp location, can Type NM cable be used in this crawl space?

Answer:

The CEC defines “damp location”. Table 19 of the CEC permits use of NMD90 exposed wiring in damp locations. NMWU is allowed to be used for exposed wiring in wet locations

[ Editor’s Note: The determination of whether a specific location is to be considered wet, damp, or dry for the purposes of applying the NEC is the responsibility of the authority having jurisdiction (AHJ). The NEC defines a “damp” location as locations protected from weather and not subject to saturation with water but subject to
moderate degrees of moisture. “Dry” locations are defined as those locations not normally subject to dampness or wetness. There are many crawl spaces under dwelling units considered by the AHJ as a dry location and the use of Type NM cable is permitted by the NEC. Typically the Type NM cable is secured to the underside of the floor joist and not subject to direct contact to the ground under
the dwelling in the event of some unforeseen moisture entering the crawl space.
]

--Dave Clements
_________________________

Top
#7949 - 01/10/11 05:40 AM Re: NM installed under a house [Re: COTInspector]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
I believe that per definition if, "some basements, some barns, and some cold-storage warehouses" may be considered a damp location, then SOME crawspaces would be too.

For the sake of consistent and uniform enforcement, it might be wise to simply consider and declare ALL crawspaces as either a damp location or as a dry location and apply the applicable rules.

I feel this is more of a product use issue rather than a life or property safety matter.
_________________________
Bryan P. Holland, MCP

Top
#7951 - 01/10/11 12:11 PM Re: NM installed under a house [Re: Nick Sasso]
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
The Canadian Electrical Code gives us the answer??
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#7955 - 01/10/11 02:57 PM Re: NM installed under a house [Re: COTInspector]
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
I would tend to agree with Bryan.
Quote:
Location, Damp. Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. Examples of such locations include partially protected locations under canopies, marquees, roofed open porches, and like locations, and interior locations subject to moderate degrees of moisture, such as some basements, some barns, and some cold-storage warehouses.


Due to temp changes under the home in the crawl space, I feel that that location would be subject to moisture. My ruling would be that it is a damp location. Even 550.15(H) addresses under-chassis wiring:
Quote:
(H) Under-Chassis Wiring (Exposed to Weather). Where outdoor or under-chassis line-voltage (120 volts, nominal, or higher) wiring is exposed to moisture or physical damage, it shall be protected by rigid metal conduit or intermediate metal conduit. The conductors shall be suitable for wet locations.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#7957 - 01/10/11 04:54 PM Re: NM installed under a house [Re: Nick Sasso]
COTInspector Offline
Mechanic Member
*****

Registered: 02/14/08
Posts: 132
Loc: Tampa, Florida
Nick,
What is NMD90 and NMWU?
I have only seen NM and NMB being used in our area.
I agree with Bryan and Mike, and feel it is a damp location in most situations.
I also feel we cannot enforce a specific code requirement on a case by case basis.

Neal Burdick
COT Inspector II


Top
Page 1 of 2 1 2 >



Active Topics
May Meeting Minutes
by Bryan Holland
05/17/12 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
JBD
JBD
Registered: 03/20/10
Posts: 0
Forum Stats
519 Members
29 Forums
1892 Topics
8569 Posts

Max Online: 53 @ 03/30/12 04:16 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image