I personally do not accept / approve operational control switches as the means of disconnect. If there is any substantial energized wiring within the appliance on the line side of the switch, then it isn't a disconnect means.
A circuit breaker located in an air handler where the circuit conductors terminate directly at the breaker would, in my mind, could qualify as a unit switch and therefore acceptable as the means of disconnect.
I recently heard a rumor that the next edition of the Canadian Electrical Code is going to remove every requirement for disconnecting means as long as the main service disconenct is readily accessible and this would be proposed for the 2014 NEC as well.