Just another thought. Take a look at 300.4(e):From the NEC;
(E) Cables and Raceways Installed in Shallow Grooves. Cable- or raceway-type wiring methods installed in a groove, to be covered by wallboard, siding, paneling, carpeting, or similar finish, shall be protected by 1.6 mm (1/16 in.) thick steel plate, sleeve, or equivalent or by not less than 32 mm (11/4 in.) free space for the full length of the groove in which the cable or raceway is installed
Exception: Steel plates, sleeves, or the equivalent shall not be required to protect rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, or electrical metallic tubing.
Now I understand that it says "shallow groove", but the idea is when the cable is installed in a wall where the 1 1/4" measurement can't be maintained than a steel plate must be installed for the full length of the groove. So than, what is the difference between a shallow groove, that does not have the 1 1/4", and a wall that does not have the 1 1/4" because of the size of the furring strip? Really isn't it the same thing, I mean if the code requires protection for the cable for a groove, why would not the cables in the whole wall require the same protection?
Doesn't that put a kink in your belt!
So if a contractor installed some sections of furring strip to staple the cable, would it comply with 300.4(e)?
_________________________
Michael J Timpanaro Inspector/Plans Examiner/CEU Instructor Florida
|
|