To answer Paul - Yes, it is a violation. The code clearly states that the outlet(s) on that specific circuit are to supply laundry only, as Mike points out.
If someone plugs in a radio after the inspector leaves, then that person should receive 20 lashes with a wet noodle, and then slowly be lowered into a large vat of cold, wet noodles. I have caught up with these people from time to time. Now I am hearing rumors that I may be prosecuted for noodle-boarding.
If someone permanently mounts an irrigation timer next to the laundry outlet upon final inspection - yes I would red tag the final - because the general purpose outlet for the sprinkler has not yet been installed. It would require a general purpose (or perhaps dedicated) 120V receptacle as stated by the manufacturers instructions for the timer. Listed or labeled equipment must be used in accordance with any instructions included in the listing or labeling:
110.3(B)
It cannot be on the laundry circuit:
210.11(C)(2)
Next time, builder [his electrical sub] should run a 3-wire to this location (which probably is not far from the panel). The remedy is quite basic. Problem solved.