#8290 - 08/03/11 03:28 PM Service Conductors in Parallel
Nova Offline
Apprentice Member

Registered: 11/03/10
Posts: 7
Loc: St. Lucie
I am inspecting a new service that consist of 600amp meter can with service conductors in parallel, that leads into a gutter and taps out to 4 main disconnects. The contractor bonded the metal gutter using only 1 of the grounded conductors in parallel (continous). So instead of coming out of the polaris tap that contains the grounded conductor in parallel and bonding the gutter, he landed it as mentioned above, would it be required that he land both the neutrals to the gutter since he used this method. I am thinking about 310.4B "be terminated in the same manner".

Top
#8291 - 08/03/11 05:46 PM Re: Service Conductors in Parallel [Re: Nova]
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
From your description I picture that the contractor skinned part of one of the grounding conductors and fed it through a lug (wire uncut) that was attached to the inside of the trough. I like your thinking, and I think I understand what you are asking. After looking through Articles 200, 230, and 250, I can find no code to accomplish what you seek.

Looking at 310 like you say, specific to parallel conductors, I am leaning toward agreeing with you. I think the intent of the code is that all parallel conductors be treated in exactly the same manner. That being said, bonding only one of them to the gutter (trough) may have some sort of weird effect given a fault condition -- although I don't know what. I also believe we are not all-knowing and there is no way we could know that.

So yes, you can use that code to have the contractor treat all the parallel service conductors in exactly the same manner. I don't necessarily believe that the conductor is being "terminated" at the trough, but it is being bonded to the trough, and thus grounding the trough itself. So the contractor should treat all of the parallel conductors in the same manner. Or -- run a single tail from the polaris tap and be done with it.

Good question. It is not everyday that someone makes me think. Anyone else agree or disagree? Please chime in.





Edited by Nick Sasso (08/03/11 05:48 PM)
_________________________

Top
#8292 - 08/04/11 07:37 AM Re: Service Conductors in Parallel [Re: Nova]
psnorthrup Offline
Mechanic Member

Registered: 04/23/07
Posts: 115
Loc: Plant City
Nick; I have to agree with you, both parallel conductors should be treated exactly the same

Top
#8293 - 08/04/11 01:07 PM Re: Service Conductors in Parallel [Re: psnorthrup]
John Belew Offline
Electrical Inspector/Plans Examiner

Registered: 06/26/01
Posts: 56
Loc: Milton,FL
Agree
_________________________
John Belew
Electrical Inspector/Plans Examiner
Santa Rosa Co.
johnb@santarosa.fl.gov

Top
#8294 - 08/05/11 10:10 AM Re: Service Conductors in Parallel [Re: Nova]
ronwampler Offline
Apprentice Member

Registered: 05/30/07
Posts: 47
Loc: Marathon, Florida
Maybe... Assuming the grounded conductor is superior in size to the minimum from table 250.66 for bonding, wouldn't a single bonding jumper be permitted? Assuming the parallelled grounded conductors are joined together within the meter base and in the trough I would think that any fault current would be safely transferred to the grounded conductors especially if the parallelled sets are within one raceway.
This is a lot of assumung and not a substitute for actually seeing the installation and making a judgement decision.

Top
#8295 - 08/05/11 12:10 PM Re: Service Conductors in Parallel [Re: Nova]
DAEngelhart Offline
David A Engelhart

Registered: 12/29/10
Posts: 26
Loc: Collier County, Fla
Agreed
_________________________
David A Engelhart
Electrical Inspector and Plans Examiner
Fire Safety Inspector & Plans Examiner

Top
#8297 - 08/08/11 08:52 AM Re: Service Conductors in Parallel [Re: Nova]
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
I too agree with Ron. 250.92(b)(1) would permit the raceway or gutter to be bonded to the service neutral conductor, as long as it is sized per table 250.66 as Ron noted.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#8301 - 08/09/11 09:14 AM Re: Service Conductors in Parallel [Re: Nova]
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
The problem here is not that the bonding jumper is of the right size, which it should be,using one conductor of the parallel Run, but is the termination of the parallel conductors on the polaris tap and to that point I would have to agree with Nick and Nova. Even though one conductor is terminated at the trough, it has bee extended in length also violating 310.4 (B)(1) and (5).I also agree with Ron in that it would not create any ground or fault current problems.
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
#8302 - 08/09/11 02:58 PM Re: Service Conductors in Parallel [Re: Nova]
Mike Timpanaro Offline

Post-A-Holic Member
****

Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
I don't understand how it is extended in length so it violates that code section?
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida




Top
#8303 - 08/09/11 03:23 PM Re: Service Conductors in Parallel [Re: Nova]
Paul J Cameron Offline
Mechanic Member
***

Registered: 11/04/03
Posts: 412
Loc: Pasco County Florida
By extending one conductor of the parallel set through the polaris to the ground lug makes it longer, does it not or are you considering it completed at the polaris as all other neutrals will tap off of there the length doesnt really matter. Either way its no big deal, I would have jumped off the polaris with the correct size bonding jumper but I guess he ran out of space. In some way or other this application seems to be in violatioin of 310.4 does it not??
_________________________
Paul Cameron
Chief Electrical Inspector
Pasco County
Past President IAEI Suncoast



Top
Page 1 of 3 1 2 3 >



Active Topics
May Meeting Minutes
by Bryan Holland
05/17/12 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
JBD
JBD
Registered: 03/20/10
Posts: 0
Forum Stats
519 Members
29 Forums
1892 Topics
8569 Posts

Max Online: 53 @ 03/30/12 04:16 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image