#8368 - 09/16/11 03:57 PM
Transformers and 110.26(A)
|
Apprentice Member
   
Registered: 07/25/08
Posts: 33
Loc: Orlando Fl.
|
"Working Space. Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of 110.26(A)(1), (A)(2), and (A)(3) or as required or permitted elsewhere in this Code" Opines needed. What in a transformer needs examination, adjustment, servicing, or maintenance while energized? If the windings short you can either see the smoke, smell the smoke, or see smoke stains. Adjustments are made in a de-energized state, try to change taps while energized damages equipment fed from the xfmer. What is to serviced and what is to be maintained inside a transformer? If voltage readings are needed, they can be made either at the OCPD upstream or downstream. So, other than the practacality of installation, why would the dimensions in Table 110.26(A)(1) be needed?
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#8382 - 09/21/11 10:16 AM
Re: Transformers and 110.26(A)
[Re: Joe L. DuPriest]
|
Secretary
   
Registered: 10/05/04
Posts: 1622
Loc: City of North Port
|
There is no doubt appliances located in closets, attic spaces, & attics make it extremely difficult for compliance with the NEC requirement for working & dedicated equipment space.
That being said, the installer has several options to come into compliance. If space is not provided for an actual disconnecting means, the a "unit swtich" can be installed. If there are no provisions for a "unit switch", a breaker lock-out device can be installed.
I will admit I have approved disconnecting means located with one or more working space dimensions NOT in full compliance, but where I was readily & easily able to approach, examine, operate, and inspect the equipment without resorting to acrobatics or other unsafe practices.
But those are exceptions to the rule, not the rule...
_________________________
Bryan P. Holland, MCP
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
|
 |
 |
 |
 |
|
|