#8426 - 10/03/11 03:15 PM Voltage Drop in the codes
SOwings Offline
CBO, MCP, ER, EN

Registered: 01/22/10
Posts: 50
Loc: Nassau County
I had not realized this before but, while the NEC does not specifically give requirements for VD, the Florida Building Code 2007 w/2009 supp does in Chapter 13 (Energy Efficiency); Here is the specific requirements (this is commercial only):

13-413.AB.1 Voltage drop.

13-413.AB.1.1 Feeders and customer-owned service conductors. Feeder and customer-owned service conductors shall be sized for a maximum voltage drop of 2 percent at design load.

13-413.AB.1.2 Branch circuits. Branch circuit conductors shall be sized for a maximum voltage drop of 3 percent at design load.



Edited by SOwings (10/03/11 03:16 PM)

Top
#8428 - 10/03/11 04:33 PM Re: Voltage Drop in the codes [Re: SOwings]
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Yes, it exists and we can use it.

Sometimes when I do plan review I may ask the design professional for a qualifying statement for the codes you cite.

Other times I may ask to see the actual calculation, if I suspect...



Edited by Nick Sasso (10/03/11 04:33 PM)
_________________________

Top
#8429 - 10/03/11 07:24 PM Re: Voltage Drop in the codes [Re: SOwings]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Yep. In fact, this has been in the FBC since the 2004 edition...

While on the subject, I have recently put together a nice PowerPoint on the Electrical Provisions of the 2010 Florida Energy Conservation Code expected to be adopted on March 15, 2012.

I can send a pdf copy to anyone that is interested...
_________________________
Bryan P. Holland, MCP

Top
#8451 - 10/05/11 02:20 PM Re: Voltage Drop in the codes [Re: SOwings]
ronwampler Offline
Apprentice Member

Registered: 05/30/07
Posts: 47
Loc: Marathon, Florida
Some appliances such as A/C condensers include distance /conductor size tables in the installation directions.
Remember that VD is basically heat loss (I^R) and the distance times the resistance/ft. of a long length of conductor that is carrying a decent current load will heat up. This lost heat is voltage drop. Parking lot lighting is infamous for VD and undersized equipt. grounding conductors that are not in compliance with 2008 NEC Sect. 250.122 (B)...

Top
#8452 - 10/06/11 12:59 PM Re: Voltage Drop in the codes [Re: SOwings]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
Also keep in mind that while Section 210.19 & 215.2 can only recommend voltage drop limitations (FPNs), there are two (2) sections of the NEC that REQUIRE voltage drop limitations:

Section 647.4(D) for Sensitive Electronic Equipment & 695.7 for Fire Pumps...
_________________________
Bryan P. Holland, MCP

Top



Active Topics
May Meeting Minutes
by Bryan Holland
05/17/12 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
JBD
JBD
Registered: 03/20/10
Posts: 0
Forum Stats
519 Members
29 Forums
1892 Topics
8569 Posts

Max Online: 53 @ 03/30/12 04:16 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image