#8465 - 10/10/11 10:21 PM Location of Gasoline Station Seal-offs
inspector32513 Offline
Lynn Adams

Registered: 10/06/05
Posts: 46
Loc: Pensacola, FL
Location of gasoline station seal-offs.

Prefabricated modular service station. Gasoline despencers out front. Ridgid conduit from dispenser, under store, up out of poured concrete on rear of building, seal-off, entry into proper equipemnt.

BUT: Once the large foundations piles were set, no dirt was backfilled. The conduit enters an open void under the building.

If the conduit was in free air all the way, the seal off could be at the 20' boundry of the Class 1 Division 2 around the dispenser. If it was in burried all the way, the seal off could be 'the first fitting as the conduit emerges from grade'

In this situation, is there not a danger of vapor traveling down the conduit, accumulating in the unventilated void under the building, and creating a hazard? And it does not have a seal-off 'where it emerges from grade' ? comments?

Lynn Adams
_________________________
Lynn Adams
Chief Electrical Inspector, Escambia County
IAEI_Panhandle Division

Top
#8466 - 10/12/11 01:46 PM Re: Location of Gasoline Station Seal-offs [Re: inspector32513]
ronwampler Offline
Apprentice Member

Registered: 05/30/07
Posts: 47
Loc: Marathon, Florida
Hmmm...I would ask for the riser and sealoffs to be on the modular side before going underneath the unit if that were 20ft. or more from the dispensers. I would ask for a w.p. wireway above 18" at that point and appropriate Class I bonding at that wireway. They could then route under or thru the modular as necessary. Propane and gasoline vapors settle at the low points. The void beneath the modular should not be approved. I would speak with the jurisdiction Fire Marshal.

Top
#8468 - 10/12/11 02:17 PM Re: Location of Gasoline Station Seal-offs [Re: inspector32513]
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Originally Posted By: inspector32513
In this situation, is there not a danger of vapor traveling down the conduit, accumulating in the unventilated void under the building, and creating a hazard? And it does not have a seal-off 'where it emerges from grade' ? comments?

Lynn Adams


I'd agree with Ron and ask the fire marshal to help investigate further. Perhaps there is a fire code to prevent this.



Edited by Nick Sasso (10/12/11 02:17 PM)
_________________________

Top
#8478 - 10/12/11 08:40 PM Re: Location of Gasoline Station Seal-offs [Re: Nick Sasso]
inspector32513 Offline
Lynn Adams

Registered: 10/06/05
Posts: 46
Loc: Pensacola, FL
A little more information (I have been 500 miles away due to a family medical situation) There is a 20 minunite timer activated ventilation fan for the sump area. BUT it is only for activation and min. 20 minute ventalation of the area before entry into 'confined space'.

That solves the entry into question. But if the whole station and convienicence store is lifted into the air, will we have cameras operating so we can send it to U-Tube?

L A
_________________________
Lynn Adams
Chief Electrical Inspector, Escambia County
IAEI_Panhandle Division

Top



Active Topics
May Meeting Minutes
by Bryan Holland
05/17/12 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
JBD
JBD
Registered: 03/20/10
Posts: 0
Forum Stats
519 Members
29 Forums
1892 Topics
8569 Posts

Max Online: 53 @ 03/30/12 04:16 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image