#8501 - 10/20/11 07:54 PM Hot tub wiring
Dan Wellins Offline
New Member

Registered: 05/04/11
Posts: 4
Loc: Charlotte County
Is it permissable to connect a outdoor hot tub to a subpanel fed with 6/3 romex. Wiring is in the interior of the house, sleeved in conduit to subpanel(surface of exterior), at which point would be in Sch. 40/LFNC to hot tub. Thanks
_________________________
Dan Wellins
President
Dan Wellins Electric
EC13004669

Top
#8502 - 10/20/11 08:47 PM Re: Hot tub wiring [Re: Dan Wellins]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
MAYBE.

If the feeder is existing to the panbelboard at which the branch-circuit will be supplied for the spa, then YES. The exception to section 680.25(A) gives this permission.

Installing a new NM cable feeder to panel to supply a spa or pool equipment would be a code violation.

While 680.42(C) & 680.21(A)(4) permit NM cable to be used for "interior wiring to outdoor installations", these two sections do not apply to a feeder supplying a panelboard used to supply pool & spa equipment. (Unless that feeder is existing as stated above)

Great Question...
_________________________
Bryan P. Holland, MCP

Top
#8504 - 10/23/11 09:51 AM Re: Hot tub wiring [Re: Dan Wellins]
SOwings Offline
CBO, MCP, ER, EN

Registered: 01/22/10
Posts: 50
Loc: Nassau County
Geeze, Brian, for once I disagree with you... As I read 680.21(A)(4), I do not see where this does not allow this wiring method if you go to a subpanel. It would be like going to a pool panel (like they use so often to control the motors and lights and such). I see no difference. When they revised the code to allow this, it was for SFR's to be allowed to have the pool feed run without using an insulated ground. Yet to this day I see so many pool feeds piped to the main panel.
If you read 680.25 literally then the feeder from your service equipment to your main panelboard would have to be in conduit IF it later fed pool wiring. "and on the load side of the service equipment or the source of the seperately derived system", this would be the line from the service to your indoor panel...

Top
#8507 - 10/23/11 07:25 PM Re: Hot tub wiring [Re: Dan Wellins]
Bryan Holland Offline

Secretary
*****

Registered: 10/05/04
Posts: 1622
Loc: City of North Port
We will have to agree to disagree. There would be no purpose for section 680.25 if sections 680.21(A)(4) & 680.42(C) exempted it.

In fact, section 680.25 states, "These provisions shall apply to ANY feeder on the supply side of panelbaords supplying branch circuits for pool equipment covered in Part II of this article..."

The exception covers your example above for an EXISTING feeder to an EXISTING panelboard LATER supplying pool equipment. But a NEW feeder to a NEW panelboard supplying pool equipment must meet 680.25...
_________________________
Bryan P. Holland, MCP

Top
#8510 - 10/23/11 08:16 PM Re: Hot tub wiring [Re: Dan Wellins]
Nick Sasso Offline

Post-A-Holic Member
****

Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
Don't agree to disagree. Florida law requires that the NEC be enforced the same "from jurisdiction to jurisdiction." So make the call.

Is he wrong?

Is he right?

Someone make the call ! shocked


Edited by Nick Sasso (10/23/11 08:16 PM)
_________________________

Top
#8511 - 10/23/11 09:55 PM Re: Hot tub wiring [Re: Dan Wellins]
gfretwell
Unregistered


I see a couple of things here
680.21 seems to be talking about branch circuits, not feeders and when you get to 680.42 it seems to be talking about the same thing.

Quote:
...shall be permitted to be used for the connection to motor, heating, and control loads that are part of a self-contained spa or hot tub or a packaged spa or hot tub equipment assembly.


That throws you back to 680.25 for the feeder.
So that is a vote for Bryan.

I do agree that this is pretty ambiguous in the code and a ruling from NFPA or Tallahassee would be the best answer.

I will say I always see feeders in RNC in new construction


Edited by Ruben Rocha (10/24/11 02:05 PM)
Edit Reason: Fixed quote tag

Top
#8523 - 10/26/11 12:57 PM Re: Hot tub wiring [Re: Dan Wellins]
ronwampler Offline
Apprentice Member

Registered: 05/30/07
Posts: 47
Loc: Marathon, Florida
You didn't indicate 6/3 w/grd.NM cable so the answer is no.

Top



Active Topics
May Meeting Minutes
by Bryan Holland
05/17/12 02:05 PM
May Meeting Announcement
by Bryan Holland
05/08/12 07:58 AM
Visual Alarms
by Nick Sasso
05/02/12 03:55 PM
Nonmetallic Extensions
by Nick Sasso
04/25/12 03:33 PM
Selective Coordination of Circuit Breakers
by Heinz R.
04/24/12 05:03 PM
May
M Tu W Th F Sa Su
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 31
Featured Member
JBD
JBD
Registered: 03/20/10
Posts: 0
Forum Stats
519 Members
29 Forums
1892 Topics
8569 Posts

Max Online: 53 @ 03/30/12 04:16 PM
Uploaded Pictures
Can You Spot The Electrical Violation?
1948 Signalite Fuse
Portable Generator Grounding
2011 Florida Gulf Coast Division - Seminar
Knob and tube in industrial application
1920's Duplex Radio Outlet
Random Gallery Image