As an inspector be aware that a sharp electrician may use Table 220.55 Note 4 to use a single 40 amp br. ckt. and tap connections to the cooktop and wall oven per 210.19(A). Tap rules have been around for a long time. I have inspected several industrial sites with taps and high-bay overhead drops. Please review 240.21(A) and look over part (B) and (C) for future reference.
I thought that tap rule only applied to 50 amp Range/cooktop/oven circuits. I do not think a 40 amp circuit may be tapped for this application. Am I wrong?
(3) Household Ranges and Cooking Appliances. Branchcircuit
conductors supplying household ranges, wallmounted
ovens, counter-mounted cooking units, and other
household cooking appliances shall have an ampacity not
less than the rating of the branch circuit and not less than
ti]83̺he maximum load to be served. For ranges of
[color:#3366FF][0;4[/i[/color]] kW or
more rating, the minimum branch-circuit rating shall be
40 amperes.
Exception No. 1: Conductors tapped from a 50-ampere
branch circuit supplying electric ranges, wall-mounted
electric ovens, and counter-mounted electric cooking units
shall have an ampacity of not less than 20 amperes and
shall be [i]suffı[/i];cient for the load to be served. These tap conductors
include any conductors that are a part of the leads
supplied with the appliance that are smaller than the
branch-circuit conductors. The taps shall not be longer
than necessary for servicing the appliance.