I recently ran across small PV panels (maybe 250 watt) installed on light poles, and red-tagged the job for violation of 690.4(B).
However I am being told that since only AC wiring (not DC) runs through the light pole (along with the other conductors), that it is not considered to be a "PV output circuit" and that all the conductors can be in the light pole, mixed together. The contractor claims that it is not a violation of 690.4.
Am I wrong?
The only other places that I have ever seen PV panels installed on light poles, are at utilities, which we all know are not subject to the regulations of NEC therefore it is OK.
Appreciate any input.