Nick your 100% correct. Stray voltage is a problem. The utility uses the earth as a return path and this has created a stray voltage problem for pool decks that do not have rebar/wire mesh. Now when you use pavers as you say there is a gradient potential difference with the deck, and other parts of the pool, and equipment associated with the pool.
I had thought there was a proposal to require mesh under pavers so the mesh could be bonded to eliminate the very problem you describe. I haven’t kept up with that, but I'll check the draft and see if there were changes on that.
You know with a deck made of materials that are not or can't be bonded, or just bare ground around the pool I would in fact make them remove the bonding grid from the electrode system. Now as you said you do have a problem with voltage gradients that can't be corrected by bonding, and that is exactly the hazard you have been talking about.
Great point, I had forgotten all about that.
_________________________
Michael J Timpanaro
Inspector/Plans Examiner/CEU Instructor
Florida