#995 - 05/19/04 10:40 AM
Re: Pool junction boxes
|
Post-A-Holic Member
  
Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
|
1. There are longer cords on wet niche fixtures, the manufacturers provide fixtures with cords up to 100 ft. 2. There is no requirement in article 680 that will prohibit one from running the bonding conductor back and connecting it to the grounding electrode system. Although there is no benefit in doing so there is no harm either. Lets face it, dig a big hole, put in a bunch of steel rebar connected together, cover it in concrete, and what do you have? A great big ufer ground! (concrete-encased electrode). 3. As a mater of fact, if a pool is installed within a specific distance to a lightning protection system, NFPA 780 requires the pool shell and equipment be bonded to the lighting protection system ground. The lightning protections system is now required to be bonded to the grounding electrode system at the service.
4. There is no requirement that the bonding conductor be installed continuos (without a splice or joint). That requirement is only for EGC (equipment grounding conductors).
5. The requirement for bonding is to eliminate voltage gradients, not to provide a path for fault current to return to the source to facilitate the operation of the overcurrent protective device. Thats what the EGC's do.
6. When all the metal parts and electrical equipment associated with the pool as prescribed in 680 are bonded together, that eliminates unequal voltage potentials, therefore there is no hazard.
_________________________
Michael J Timpanaro Inspector/Plans Examiner/CEU Instructor Florida
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#997 - 05/19/04 01:44 PM
Re: Pool junction boxes
|
Post-A-Holic Member
  
Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
|
Nick you are correct, and we do agree, if there is a fault on any circuit in the electrical system current flows on all grounding and bonding conductors. Some have thought that current flows on the path of least resistance. That is 100% incorrect.
We bond all metal parts and equipment so there is no potential at all between parts, from a fault that may occur in any circuit, cracked lens in the wet-niche fixture, motor winding going to ground, whatever.
The primary purpose of bonding is to ensure that voltage gradients in the pool area are eliminated. The fine print note explains that the 8 AWG conductor's only function is to eliminate the voltage gradient in the pool area. It is not required to provide a path for fault current that may occur as a result of electrical equipment failure.
If there is no potential difference there is no hazard! 20 volts to ground at the motor, 20 volts at the handrail, 20 volts at the fixture...etc... equal potential, no hazard . That’s just what an equipotential plane does, eliminate voltage gradients just like 680.26(a) says.
_________________________
Michael J Timpanaro Inspector/Plans Examiner/CEU Instructor Florida
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#1000 - 05/20/04 07:50 AM
Re: Pool junction boxes
|
Post-A-Holic Member
  
Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
|
So let me try to understand your point better. What you are saying is that the resistance of the #12 EGC conductor, and its length is a problem? Lets think about it, if that were true, wouldn’t there be too much resistance to allow the current to return to the source and open the breaker in a fault condition? If what you say is correct than no circuit in a fault would ever work because of to much resistance! Lets get back to the point. If the code panel thought it was unsafe to connect the pool bonding grid to a grounding electrode they wouldn’t say that its just not the intent to require it, but rather our code would say that it shall not be connected to any grounding electrode. Again lets go back to quote the code: 680.26(a) “The bonding required by this section shall be installed to eliminate voltage gradients in the pool area as prescribed”. FPN: “This section does not require that the 8 AWG or larger solid copper bonding conductor be extended or attached to any remote panelboard, service equipment, or any electrode". Now here is a quote from the handbook: “The primary purpose of bonding is to ensure that voltage gradients in the pool area are eliminated. The fine print note explains that the 8 AWG conductor's only function is to eliminate the voltage gradient in the pool area. It is not required to provide a path for fault current that may occur as a result of electrical equipment failure". By code if we do that there is no hazard. I agree that if it were a hazard as you believe, than the code should come out a specifically say not to connect it to any electrode. Maybe we do need a code change.
_________________________
Michael J Timpanaro Inspector/Plans Examiner/CEU Instructor Florida
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#1002 - 05/20/04 09:56 AM
Re: Pool junction boxes
|
Post-A-Holic Member
  
Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
|
Lets break it down and deal with one part at a time, and talk about your first paragraph. The short circuit withstand rating of a conductor (how much fault current a conductor can carry) is: For every 42.3% of the circular mill area of a conductor that potion can withstand 1 ampere for 5 sec. Based on I2t (how fast the breaker or fuse will open and clear a fault) the withstand current rating of a #12 copper conductor at ½ cycles (standard circuit breaker operation) is 3,800 amperes. For #8 it is 9,600 amps. If there was a 1/8 cycle overcurrent protective device the withstand rating of that same copper #12 conductor is now 7,600 amps. For a #8 it is 19,200 amps. Since the fault has to return to the source, the amount of fault current (worse case) available is based on the source transformer SCA, and a point–to-point fault current calculation.
The basic purpose of overcurrent protection is to open the circuit before conductors or conductor insulation is damaged when an overcurrent condition occurs. An overcurrent condition can be the result of an overload, a ground fault, or a short circuit and must be eliminated before the conductor insulation damage point is reached. System components include wire, bus structures, switching, protection and disconnect devices, and distribution equipment, all of which have limited short-circuit ratings and would be damaged or destroyed if those short-circuit ratings were exceeded.
Since article 110.9 and 110.10 requires the overcurrent protective devices shall be selected and coordinated to permit the circuit-protective devices used to clear a fault to do so without extensive damage to the electrical components of the circuit.
Every component, conductor, etc..must be able to withstand any fault likely to be imposed upon it .
Maybe its just me but I don’t understand how the size of the conductors, or their resistance comes into the picture, since the code requires that the system be installed to withstand current at all fault levels.
_________________________
Michael J Timpanaro Inspector/Plans Examiner/CEU Instructor Florida
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#1008 - 05/20/04 02:35 PM
Re: Pool junction boxes
|
Post-A-Holic Member
  
Registered: 11/08/01
Posts: 1451
Loc: West Palm Beach
|
The earth shall not be used as an effective ground-fault current path, however this does happen in an emergency. That is why I didn't quote the technical parts and I said that it has to clear a fault. I know, I know, I shouldn't have said it that way. I have seen entire buildings and homes where the neutral has been cut or became unattached where the structure was running entirely on the grounding electrode, and the earth was the return path.
While this is not allowed, if this didn't happen someone could get seriously injured or killed. The electrode provides this safety in the event of an emergency. That's why it's important to have good service grounding.
Consider the situation: A contractor has ran his #8 bare pool bond wire and attached it to the grounding electrode. What happens in the unlikely event that a neutral lug becomes unattached or burns up, and someone is in the pool? Do you know for sure?
Isn't it better to leave bonding alone, and not confuse it with grounding the pool? Why does everyone disagree with me? There is no reason to mix bonding and grounding. None whatsoever. Otherwise rewrite the Code to say "the pool steel shall be effectively GROUNDED." Otherwise leave it alone if no one is willing to change the language.
All that pool bonding does is mechanically bond the associated metal parts of the pool together, so that in the event that some metal part accidentally gets energized, and if someone is in the pool, everything stays at the same potential. That's it in a nutshell. The purpose of pool bonding is not to ground everything.
This issue is becoming more and more confusing as current code language and intent gets ignored time and time again. The intent of the Code is clear. If everyone wants to ground the pool bonding grid, then change the code language to say so.
_________________________
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#1012 - 05/21/04 07:28 AM
Re: Pool junction boxes
|
Post-A-Holic Member
  
Registered: 04/10/01
Posts: 1104
Loc: Ocklawaha FL.
|
Yep that’s correct, but remember, even though the grounding electrode system is not intended to be used as a fault path for current to return to the source, current will flow on all paths. Its just that because earth impedance is so high, more current will take the path of least resistance, to open the breaker, but again current will flow on all paths. And Nick I agree with your statement and I quote: All that pool bonding does is mechanically bond the associated metal parts of the pool together, so that in the event that some metal part accidentally gets energized, and if someone is in the pool, everything stays at the same potential That’s exactly what I've been saying, if there was a problem for example, lets say the water has a potential of 20 volts, we bond all the parts per 680.26, that means the ladder has 20 volts the deck has 20 volts. See with all parts at the same electrical potential there is no shock hazard. But if things were not bonded or bonded properly, if the water was 20 volts, and the handrail was 10 volts, and the deck was 5 volts, now we have a hazard because of the gradient of electrical potential differences between parts. So you see even though personally I wouldn't connect the bonding grid to the electrodes myself, if it were done, and there was a fault, overvoltage, stray voltages, whatever, the bonding grid potential would be raised equal to the potential of the fault or problem. There should be no gradients, all electrical potential should be equal and there should be no hazard.
_________________________
Michael J Timpanaro Inspector/Plans Examiner/CEU Instructor Florida
|
|